How to Repair a Partial Core Stator Generator

01/28/2009 2:59 AM

Dear All

My NAme is Rita Triani. I have a problem in hydro generator. the capacity is 37.5 MVA. the problem is the core is fault like burning in core that make me have to repair partial it. The question is:

1. How to repair the generator core partially? could you explain the prosedure it?

2. How about the material?

3. what is the testing thar i must conduct except elcid test.

Thank for your aids

Regards

Rita

Photo enclosure

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#1

Re: How to Repair a Partial Core Stator Generator

01/28/2009 4:40 PM

By looking at the picture I would say that this generator is beyond repair. The cost of removing it and having it redone would be more than the purchase of a new one. The length of time to repair and return to service would be longer than the purchase of a replacement.

The problem with this type of fault is that it goes through the whole device and if you miss just one little thing your back to below start. Time and money wasted. Have a factory rep. visit and give an estimate new vs repair c/w with time factors.

Good Luck

__________________
Could be worse, it could be me. :)
Register to Reply
Active Contributor
Engineering Fields - Power Engineering - New Member

Join Date: Jan 2009
Posts: 21
#2
In reply to #1

Re: How to Repair a Partial Core Stator Generator

01/28/2009 8:42 PM

thank you myt2u for your advice.

I will try to describe and clarify the detail explanation of the stator core lamination failure before. The diameter of stator generator is 2.5 m and the height is just about 2 meter. it has 243 slot. The defective core is only one segment that consist on nine teeth . photo enclosure. So if i replace with the new one, does the cost is higher than repair it? do you have experience to repair it? and how many time to repair?

Regards

Rita

Regards

Register to Reply Off Topic (Score 5)
4
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#3

Re: How to Repair a Partial Core Stator Generator

01/28/2009 9:24 PM

Dear Rita

CORE REPAIR AND TEST

Its not so simple to answer, because its need depth experiences to repair this part, however the damaged core as in the figure is still possible to repair.

Following step may can helping you to repair:

  1. Remove the stator coil and surge ring support
  2. Remove the compression bolts and finger plate from frame
  3. Remove the damaged stator core (if need to replace)
  4. Clean out by dry air
  5. Cut the damaged stator teeth core
  6. Grinding the damaged stator surface core, do careful and avoid the metal dust fill in side
  7. Clean up by using clean cloth and by dry air
  8. Separated the damaged core lamination by using thin knife (round 1 mil thick)
  9. Sprayed by insulation varnish onto separated lamination sheet
  10. Dry out
  11. Pull back the lamination onto its position
  12. Applied the epoxy / resin or RTV onto these lamination
  13. Repair all damaged finger plate or replaced
  14. Re assy the compression bolt acc to the torque required.
  15. Test the core looseness after compression bolts has been tighten, found loose on the lamination is indicate loose on compression bolts
  16. Test and analysis the core repair result with EL CID or Loop
  17. Any unsatisfactory result must be repaired.
  18. Clean up and spray paint coating
  19. Core ready to refitting coils

Following is figures as references.

Compression bolts

The failure to tightened of core ay result in core damage, as well as damage to the insulation of the core-compression bolts.

Following is a simple method of calculating the torque required on the core compression bolts of many poles machine. If manufacturer data not available.

calculate the net area of core:

Net area [ in2 ] = 0.7854 x [ OD2 – ID2 ] – [ No. of slot x width of slot x depth of slot ]

è All dimension in inches

Total Force in core [ lb ] = Net area [ in2] x 150 lb/in2

150 lb / in2 is a typical value, the specified value for machine can be obtained from the manufacturer

Force / bolt [ lb ] = [ total force in core x OD/ID ] / [ No. of bolts ]

The required torque per bolt is:

T [ ft-lb ] = Force per bolt / bolt torque constant

The bolt torque constant is a number that depends on the type of bolt and bolt size è see ASTM Std A – 193-B7

In 2-4 poles machine the compression bolts travel through the core lamination. In this case the force per bolt is approximately equal to the total force in core

Total force per bolt ≈ Force in core [ lb ] = Net area [ in2] x 150 lb/in2

Ref : Inspection of Large Synchronous Machine. IEEE Power Engineering Series

INSPECTION AND TESTING

  1. Core Looseness

Core looseness usually will occur at the inside diameter near the ends of the core. However, it is possible for looseness to be general and/or exist on the core outside diameter.

If looseness is suspected, degree of looseness can be evaluated by carefully inserting a knife blade between punchings at several locations. If a 10-mil (1 mil = 0.0254 mm) blade penetrates more than round a quarter of an inch (6mm), the core may be not sufficiently tight.

EXTREAME CARE SHOULD BE TAKEN NOT TO BREAK THE BLADE, LEAVING A PIECE IN THE LAMINATIONS !

Looseness may be accompanied by dust generation, punching and spacer movement, or small pieces of punchings flaking or cracking off.

  1. Digital ELCID

Electromagnetic Core Imperfection Detection (EL CID) is used to check the integrity of inter-lamination insulation for stator cores of generators and motors. A fault current occurring within the laminated stator core results in a hot spot and can cause a catastrophic failure of a generator and motor

  1. Loop Test

Loop is also to test the interlamination core, but its require high current power supply and voltage (normally 220 – 380 V), its very dangerous, special attention for electrical shock must be care.

Loop test is required Ampere Turn looping entire stator core,

Ilustration,

How many turns of cable is depend on the stator core dimensions, such as:

Core Outside diameter, core inside diameter, slot depth, core length. Following formulae to determine of cable turn and cable dimension required.

T = (E x 105) / (4.44 x f x Qt)

Qt = BC x Ace

Bc = 8 x 104

Ace = Le He

Le = .93 [L – (n x wd)]

DM = ID + 2S + He

Lm = π x Dm

Wl = 1.6 watt / lb

Wb = Ace x LM x 0.2764

AT = 12 x LM

IM = AT / T

Iw =( we x wb )/ 50

Dia. cable = 500 x Im (circ.mills)

1 Mill = 1/ 1000 inch

Le : Effective L core

Ace : Effective area of space duct

Lm : Magnetic Length of core

Qt : Total Flux

Bc : Flux Density

Wb : Bore weight

He : Slot height

ID : Inner diameter of core

AT : Amper turn

IM : magnetizing current

Iw : Web current

n : no of space duct / air duct

Instruments and equipment / tools required:

  1. Thermo vision
  2. Cables
  3. Regulator Power supply
  4. Clamp ampmeter
  5. Cable support

Standard req. taken from VDE 0530

PART OF MACHINE

A

E

B

F

H

A.C. Winding of turbine type generator with rated output of 5000 kVA or more607080100125
A.C. Winding of salient pole and induction machine with rated out put of 5000 kVA or more, or having core length of 1 M or more607080100125
If by way of an exception the embedded temperature detector method be used on machines under 5000 kVA, the limit of temperature rise given in this item shall apply607080100125
A.AC. Winding of machine with rated output smaller than in item 1. Field winding of a.c. and d.c. machine with d.c. excitation exception machine in items 3 and 4. Winding of armature of a.c. and d.c. machine with commutator607580100125
Field winding of cylindrical rotor with d.c. excitation658090110125
Multi layer field winding of low resistance and compensating winding607580100125
Single layer winding with exposed bare surfaces658090110125
Permanently short-circuited insulated windings607580100125
Permanently short-circuited uninsolation windings
Iron core and other parts not in contact with the windings

Iron core and other parts in contact with the windings 4)

60

75

80

100

125

Commutator and Slipring, open or enclosed 5)6070808080
Journal bearing and rolling bearings5050505050
Rolling bearings using special grease6060606060
1). A correction is necessary for a.c. winding for rated voltage above 11 kV
2). The temperature rise of parts of machines rated at 5 MVA and above or having core length of 1 M or more, which are insulated with class F or class H materials, shall not exceed the limit of temperature rise for class B materials
3). Where the thermometer method is used, the limit of the temperature rise is that given for the resistance methd less 10 deg.C in the case of classes A, E. B. 15 deg.C with class F and 20 deg.C with class H materials
4). The limit of temperature rise is detrmined by the class of the insulating material of the embedded winding
5). If no marked thermal interaction between the commutator, or the sliprings, and the winding connected thereto is to expected, the limit of temperature rise applicable to these parts are those assigned to their respective insulation classes
6). In the case of commutator and slipring the limit of temperature rise may be exceeded by 10 degC with class F, and by 20 deg.C class H materials.

Core analysis by using loop test for big machine is very dificult, its require big power supply, cables, too many man power. imperfection lamination underneath of core teeth can not detected, ELCID is the best to analysis your stator core.

Pls be careful, and GOODLUCK......

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Good Answer (Score 4)
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#7
In reply to #3

Re: How to Repair a Partial Core Stator Generator

01/30/2009 5:11 AM

Good guidance and excellent explanation.

It appears that you have been involved in this sort of repair procedure.

Lets hope it'll help Rita to weigh the situation and act accordingly.

__________________
Making mistake is part of learning.
Register to Reply
Participant

Join Date: Jan 2011
Posts: 3
#10
In reply to #3

Re: How to Repair a Partial Core Stator Generator

01/30/2011 1:36 PM

Dear Mr. Siswanto,

It was great going through your post regarding "How to repair a partial core stator generator" threaded by Rita.

Well i am having same trouble but in my case a aluminium block(part of rotor) got dislodged and trapped between rotor and stator during machine's mechanical spinning at its rated speed(375rmp). Almost 2kg of aluminium were rubbed off and particles got deposited between stator laminations(2-3mm inside) and few core laminations were also dented. Almost 40mm height of stator throughout peripherially, core laminations are shorted to each other because of this deposition.

We megger test on the windings and found that it is intact. Now we have to remove these aluminium deposits, re-insulate damaged and aluminium deposited laminations and repair the dented core without overhauling the entire rotor. Currently we have removed one pole and started with cleaning and chipping of these depositions and repairing of these dents. But, trouble is, it is very difficult to remove these deposition and repair the dents without loosening the core. We dont want to overhaul the rotor or stator or even loosen the core because it will take lot of time. Our machine supplier are saying that EL CID test is not required for such damage because the machine is only 6 years old. But i am bit worried.

As it seems that you have experience regarding core repairing, can you suggest me how to go about with our work. Moreover, is it necessary to perform the EL CID test in our case? Any special insulation paint that can go inside the laminations by itself by just applying on the core tooth?

Our generators' info:

170MW-hydrogenr, stator dia:5000mm, air gap:29mm, 16 nos. salient poles, Core height: 3000mm, 252slots, wave winding, core packets:60no laminations, 0.5mm thick laminations.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#12
In reply to #10

Re: How to Repair a Partial Core Stator Generator

01/31/2011 5:23 AM

Mr sonam_wangdi

Pls visit my blog: www.sispowergeneration.blogspot.com

Home

http://www.sispowergeneration.blogspot.com/

Preliminary

http://sispowergeneration.blogspot.com/p/detail-inspection-for-high-reverse.html

Rotor

http://sispowergeneration.blogspot.com/p/detail-inspection-for-high-reverse_22.html

Stator

http://sispowergeneration.blogspot.com/p/stator-detail-inspection-for-high.html

Rotor Thermal Sensitivity

http://sispowergeneration.blogspot.com/p/rotor-thermal-sensitivity-phenomena-on.html

Welcome to CR4 Forum and thank you to contacting me

Its little bit difficult to removing the Aluminum when rubbing in the air gap, but it will very difficult to remove it from core surface when foreign material was melted.

Core damaged can occurring on the surface only and or inside of interlamination of core.

Pencil grinding can employ to remove the metal melting on the core surface but not inside or side of wall.

Fig1. Foreign material melt on the stator bore


Fig 2: close up foreign material melting on the core surface

Fig.3 after grinding

Fig.4 Stator core damaged due to rotor touching to stator core

Repair:

Fig, 1,2,3,. Stator core surface can be repaired with grinding to remove foreign material and separate the interlamination core with thin stainless plate and finishing with insulation coating.

Fig 4, Core damaged due to high friction between rotor to stator core, separation of interlamination core to repair of interlamination short.

When damaged of core at inside or side of wall is very difficult to remove without loosening core or re stacking.

Fig.5 Foreign material deposit on side wall

Fig.6 Your generator core


Fig 7. Rotor V Block

Repair:

Fig 5, repair core can be done with re stacking ,to remove the foreign material

Fig 6, repair can be done with combine grinding and separation of core lamination (see fig, 4), when separate the interlaminations, do with extra carefully since the stator winding still in place.

Inspection,

Core should be inspected by using core analysis, such as ELCID or Ring Flux, it mean to identify core short interlamination.

Visual inspection is not possible to identify the core short, ring flux can identify short interlamination with represent of "heat / temperature" but it can not to identify where is the problems location, ELCID can analysis the actual location and more accurate the threshold.

ELCID or Ring Flux should be repeated by several time, before repair and after.


Fig 8. ELCID Visualization.

Do spraying entire core with insulation painting, if you found broken or heavy dent on the teeth of core, apply RTV on this parts to avoid vibration and touching between interlamination during machine in operation.

Your quote: Our machine supplier are saying that EL CID test is not required for such damage because the machine is only 6 years old. But i am bit worried.

"Yes ELCID is normal to analysis of core when machine more than 10 years old (for normal operation / no accident was occurred)", your machine was touching to rotor with foreign material involving, and may some of those foreign materials was also melt and entry to the interlamination, and may also your interlamination was damaged due to high friction, such as dent / broken, etc.

Core inspection ( by ELCID or Ring Flux, depend on the site requirement and budgeting) should be done, since we can't detect the short interlamination by visual.

Remove rotor from stator bore to inspect the core in detail, you can save more time and much more efficient comparing to total time consumption when you are repairing improper way and finally you need more time to shutdown for repairing.

Good Luck

My Best Regards

Siswanto

Specialist Engineer

Power Generation

Emails: sis_cahya@yahoo.com

siscahyabhuwana@gmail.com

Blog : www.sispowergeneration.blpgspot.com

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Participant

Join Date: Jan 2011
Posts: 3
#13
In reply to #12

Re: How to Repair a Partial Core Stator Generator

02/04/2011 12:11 AM

Dear Mr. Siswanto,
Thank you for your advice and suggestions. It was of great help for us. And thank you very much for offering your service. I will discuss with my superiors.
And you are right that the aluminum thing is our V block. What we think what happend was that the stud holding the V block got sheared and both broken stud and V block came between stator and rotor.

Currently we have been chipping out these aluminum deposits and separating the blocked air ducts. It is observed that these deposits have formed layers on the surface and got few millimeters inside the laminations. From 100% deposits we are able to remove only 80-90%. After each exercise we cleaned the core with white spirit (ethanol) and for your information, we have observed oil inside the laminations.
While checking the continuity for these laminations, we have noticed that all the core laminations are shorted to each other and to ground, even the healthy laminations. To confirm further we even tested the continuity between core laminations in other healthy generators and found the same result. Well, what i had in my mind was that all the laminations should be insulated from each other and even from ground, so, these findings were quite alarming. So, can you help me to understand how this is possible? If these laminations are shorted through some means then i feel it should not be a problem with some aluminum deposits at surface of core. Or is it really necessary to have all the laminations insulated from each other (100%)?, is there any tolerances?
After cleaning these core packets, we are planning to apply varnish over it and then carry out the test run. As we have only 4 nos of RTDs to monitor the whole Core tooth, do you suggest any idea on how to maximize our stator core temperature monitoring system? or is there any means to measure temporarily ?
As i know, our main concern is that there should not be any hotspot in the cores, so, is this hotspot instantaneous or gradual process because during test run we will be loading the machine in steps till110% load and monitor the temperature from above RTDS. For your information, we have also got RTDs for stator windings/slots. IF incase there should be any development of hotspots, will it be instantaneous? And i hope it won't melt the winding?

And still we haven't thought anything about the core analysis. Our generator expert still thinks that core analysis is not required. Moreover we don't have ELCID test or flux test equipments.
i will be Looking forward for your suggestions,
thank you

Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#14
In reply to #13

Re: How to Repair a Partial Core Stator Generator

02/04/2011 3:12 PM

Dear Mr Sonam

1. While checking the continuity for these laminations, we have noticed that all the core laminations are shorted to each other and to ground, even the healthy laminations.

2. what i had in my mind was that all the laminations should be insulated from each other and even from ground

3. If these laminations are shorted through some means then i feel it should not be a problem with some aluminum deposits at surface of core

ð Its tested by megger or DC resistance ?

ð Core lamination has been laminated by micro film insulation coating (in micron thickness), and at core back-off to be shorted together (some of them using by welding) and clamping to body support, found problem shorted areas will resulting over fluxing.

This is SIEMENS Generator 16 poles, rotor was touching to the stator core, damaged core was found on the surface only, we test by Ring Flux, with 50% flux from the nominal total flux required was induced on this core, before repair at 1 minute, temperature at the core was reached 125 degrees Celsius, after repair, in 2 hours, temperature was come down to 45 degrees, with ambient temperature 32 degrees Celsius.

When found short interlamination on the coils area (slot) and tooth core, its will resulting high circulating current in the slot and or surface depend where is the short location.

4. As i know, our main concern is that there should not be any hotspot in the cores

Hot spot is caused by short inter lamination due to insulation fail on the magnetic flux areas (slot area and surface).

To identify the hot spot should using ELCID test instrument or ring flux, when using ring flux will be used, its should capable induced current in the core at least 60 – 70% from total number of rating flux required for stator. When using ELCID its need only 4% from the total flux required.

Visual inspection is not possible to identify the hot spot..!!!

When hot spot is not to solved, its will resulting over heating on the coil winding and insulation breakdown can occurred prematurely, finally replace of coil with new and repair the core should be planned..!

My recommendation.

Never operate this generator without any inspection for the hot spot with proper test and method.

- When using ELCID 100 mA is maximum threshold for the hot spot on the core

- When test by ring flux, if your stator is class F, maximum temperature on the core is 100 degrees Celsius, and different temperature at the adjacent core should not 10 degrees Celsius, and test must be done up to temperature reached equilibrium (may between 8 – 12 hrs) depend on the stator size and supply of current test.

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Participant

Join Date: Jan 2011
Posts: 3
#11
In reply to #3

Re: How to Repair a Partial Core Stator Generator

01/30/2011 1:56 PM

Dear Mr. Siswanto,

these are some of the photos of our affacted core:

Register to Reply
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#4

Re: How to Repair a Partial Core Stator Generator

01/28/2009 10:14 PM

Rita check out this wed site is has lots of information on generators, good read.

http://www.gepower.com/prod_serv/products/tech_docs/en/downloads/ger4212.pdf

I don't think that repairs are possible as it will put the rotor in an out of balance situation.

Cheers Robert

__________________
Could be worse, it could be me. :)
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#6
In reply to #4

Re: How to Repair a Partial Core Stator Generator

01/30/2009 5:05 AM

It's a bleak explanation to her concern.

__________________
Making mistake is part of learning.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#5

Re: How to Repair a Partial Core Stator Generator

01/29/2009 4:03 AM

Dear mayt2u and Rita

Yes you right mayt, the best choice is replace the damaged core even partially.

The website as provide is to analysis of rotor or field, yes of course improper repair on the rotor winding will impact to the balance and vibration., we are also using this paper as reference when we are performing rewinding rotor GE 237.5 MVA / 3000 RPM

Based on our experiences the core (based on the photo) is still possible to repair, in my opinion its will take round 3 months including replace of damaged stator coil. The best choice is replace the damaged core lamination.

If you need to repair this core you must have good experiences and equipments, never do it if you do not have experience or not supported by the expert.

The core damage may caused by entry of foreign material inside when machine in operation, or loose of finger plate, because the old design of hydro generator, the finger plate is not welded.

Note:

Its just talking about our experiences,,,,,,

Rgds

Siswanto

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Active Contributor
Engineering Fields - Power Engineering - New Member

Join Date: Jan 2009
Posts: 21
#8
In reply to #5

Re: How to Repair a Partial Core Stator Generator

02/01/2009 8:42 PM

Dear Siswanto,Mayt2U, Isti 80

I have seen about your explanation and the procedure about how to repair the core interlaminar partially as detailed. as mention before how about to repair stator coil partially too? do we need replace all of the insulation along the bar coil? Could you please give us the procedure to repair it? thank for your help.

Regards

Rita

Register to Reply Off Topic (Score 5)
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#9
In reply to #8

Re: How to Repair a Partial Core Stator Generator

02/02/2009 5:44 AM

Dear Mbak Rita..

As I seen that the coils stator winding has partially damage, normally as you know that our customer here need rush and less of cost…(including PLN WILYAH.... its in INDONESIAN language..)

Yes of course, if you need re insulation on these coil bars, the all insulation on the coil bar, must be removed and cleap -up . do not remain it on the copper bar......

Here based on our experiences, its normally they need reinsulated only, its very simple (as the fig. the coil dimensions is not so big, may round 6 - 8 strand of copper wire. Its not difficult because in my opinion the coil structure is not "RUBBEL"

Following is highlight procedure to re insulate and test for the coils.

A. Testing and repair for healthy coils

- Inspect the healthy coil by using borroscope to identified PD activity, its a option.

- Insulation resistance and PI

- Winding Resistance

- Off line partial discharge ( stage 1 ), when the damaged coil was removed, ( you can test by PD probe or C-coupler), I suggest to test by probe, its simple but very useful, because its can identified to each coils even top and bottom, if you found high level PD at coil you can repaired alone

- Test Insulation Tan Delta (stage 1), at this stage if required. The best choice is performing when all the coil has been finished re fitted and connection

- Repair all semi conductive coating on the stator coil (healthy coil)

- Repair all end winding and applied stress grading as per specification

- Prepare the new stator wedges (all). If possible, provide by radial spring, use Class F NEMA G11 materials

Note :

Before performed these test, ensure that the healthy stator coils has finished clean up and dried, especial when you will conduct PD test, IR / PI must pass in acc to minimum value recommendation, see IEEE std 43.

Hipot you can also performed, but its very dangerous, I recommended its no….. except the client accept to repair all stator coils.

Applied heater in the stator bore when the repaired coil still in process repair, and switch off when repaired coils ready to re assy.

B. Re insulation process step and Test for re insulated coils

- Prepare the baking oven to accommodate the length of stator coils

- Prepare press heaters

- Prepare the coils press tools

- Clean up old insulation winding, do careful and avoid damage or crack or scratch on the coil bars

- Applied insulation tape and resin on the copper bars coil, do and processed at clean area, use double B-stage nomex 410 tape, if you are using this materials resin is not require

- Applied the semiconductive coating ( you can applied by paint or tape) on the outside wall insulation and applied stress grading on the end winding with overlap 1" with the semiconductive layer

Attention :

- during in re insulation process, avoid dust and other contaminant involve.

- Minimize void in the winding insulation layer as much as you can

- Putt in the press tools and heat

Testing :

- Test IR for each coil when the coil still in the metal press tools ( do copper to ground / metal shield)

- Test PD for each coils, by using PD prob

- Test Hi Pot for each coil minimum 2Un + 3000 V ac. For voltage rang 6000 < Un ≤ 17000. If you need using DC voltage its must be multiplied by 1.7, no flash, no puncture, no breakdown is "test pass" parameter

Note : all test items must pass, found fail during test you must make a repair the insulation as per above step.

C. Test after all winding has been complete re fitting.

When repaired coils finished re assy, and complete reconnection, following test must be performed.

- IR / PI, refer to IEEE 43

- Winding resistance, the test result must be corrected and referred to the factory measurement, if its not available , Rdc deviation between phase +/- 5 %, refer to NEMA MG1

- Winding Surge comparison test ( if available) as I know that we (in INDONESIA) do not have surge comparison test for big capacity machine, we have two, but its only cover 10 MW.

- Test Insulation Tan Delta

- Test off line PD, if during re insulation process step the PD test is good, but during this test if found unsatisfactory result on the repaired coils, its may cause damaged on the semic conductive coating or the coil dimension is smaller the original ( loose in the slot), re-repaired the coils is required

Note:

Before re fitting the coils you must perform repair and test the stator core, its must 100% satisfactory.

Be careful and good luck…."SEMOGA SUKSES"

We perform unit #3……for Singkarak.. keep close communication

Rgds / SALAM

Sis

Following fig are references only......

Stator coil Alstom 87.5 MVA / 11.5 KV

18 top bars was removed to re insulate, see the black color on the wall insulation coil bar is "semiconductive coating" damaged this coating causing PD activity on the slot.

PD test by probe, use temporary cable as coil replacement when the damaged coil was removed

Stator coils burnt due to PD activities

Repair of semiconductive coating on the healthy coil

Tan Delta test when all stator coil has been connected

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Off Topic (Score 5)
Register to Reply 14 comments