Full Load Current

02/03/2009 4:59 AM

how to calculate full load current for 500 kw motor if this load is fed from 33/6.9 transformer.?

Register to Reply
Pathfinder Tags: full load current
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: full load calculation

02/03/2009 7:16 AM

Power= √3VI CosΦ

You know P, V, powerfactor, you have to calculate I

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#2
In reply to #1

Re: full load calculation

02/03/2009 8:20 AM

Your response is perfect for such a question. A GA from my side.

__________________
Atlas Shrugged - JGD
Register to Reply
Participant

Join Date: Jul 2008
Posts: 3
#3

Re: Full Load Current

02/04/2009 1:53 AM

my question to you my friend is, what voltage(x) is being fed to the motor?

500kw / 6.9v = Full Load Amps or 72.463a

then make the adjustment for the power factor

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4
In reply to #3

Re: Full Load Current

02/04/2009 3:02 AM

You are right, never mentioned it is a 3Φ motor, just assumed by the rating - but can be anything -

Any way doesn't really matters,your answer is correct but it is

500Kw/6.9Kv

Ks do matter (especially if they remove from my pay packet as it usually happens when they recover taxes in the end of year)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 12
#5

Re: Full Load Current

02/04/2009 3:31 AM

then can you tell me the value of breaker needed for this purpose?

Register to Reply
Participant

Join Date: Jul 2008
Posts: 3
#6
In reply to #5

Re: Full Load Current

02/04/2009 11:58 AM

Well my friend thank god for this web site! If im correct this motor is connected to a motor starter right. Then your overload protection will be 90A my friend, and the circuit breaker will be 110A CB.

I need work!!! LOL!

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#7
In reply to #6

Re: Full Load Current

02/04/2009 12:24 PM

just a bit correction, 500KW motor is likely to be 3Φ and then the currents change

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 12
#8
In reply to #7

Re: Full Load Current

02/05/2009 3:59 AM

Full load as told by my friend is 72.3 Amps. So the overload protection must be less or equal to 72.3 Amps.

It must be 70 % of the total full load current.????

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#9
In reply to #8

Re: Full Load Current

02/05/2009 5:05 AM

So that the motor trips as soon as it starts ?

It is clear that unfortunately so, you are getting your homework done by us.

Please go back and study back the basics of fault protection systems and do your work yourself.

Please as yould be engineers do not get your basics from the net. Get clarifications certainly, that also when you have some serious doubts.

As on now what ever you and your classmate ( a guess) have written are part of pre-final engineering syllabus if not earlier.

I could give you the solution but I don't feel I should. After the previous post - you have confirmed, despite several posts, that it is a single phase 500KW Motor.

This total thread smells of a collapsing projectwork

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 12
#10
In reply to #9

Re: Full Load Current

02/05/2009 7:38 AM

no its not project work. Its a small qu`estion in my mind. But thanks 4 all the assistance

Register to Reply Off Topic (Score 5)
Anonymous Poster
#12
In reply to #8

Re: Full Load Current

02/06/2009 6:15 PM

your wrong>

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#11

Re: Full Load Current

02/05/2009 8:03 AM

Assuming you are right, and not one of the subject, the overload setting of the Motor is between 115 to 125% of the rated current. This (115 or 125) depends upon the duty factor etc

You can google it and a few sites that are quite useful are

www.mikeholt.com/mojonewsarchive/EC-HTML/HTML/Motor_Calculations_-_Part_1~20030303.htm

or you can refer to NFPA

www.nfpa.org/assets/files//PDF/necdigest/CodeIssues071305.pdf

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Current Maarey (1); hersona (2); pratyasha5 (3); sb (5)

Previous in Forum: Belt scale operation   Next in Forum: 380 VAC Induction Motor

Advertisement