Difference between Leakage,Earth and Residual current

02/06/2009 5:53 PM

Hello,

Could somebody please explain the difference between the 1)Leakage 2)Earth and Residual current??? Are there any relationship with these currents?? If possible with examples.

Why and when would we consider each of these currents??

Thanks in advance!!

mrelay

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Difference between Leakage,Earth and Residual current

02/06/2009 6:41 PM

This is beginning to sound like homework.

I shudder to think of the alternative.

Are you, perhaps, designing a HV transmission line?

Reply Score 1 for Off Topic
Participant

Join Date: Feb 2009
Posts: 3
#2
In reply to #1

Re: Difference between Leakage,Earth and Residual current

02/06/2009 7:03 PM

This is not homework.

I am new to the protection world, i am more of a metering engineer(energy and power).

Hence the question. I am confused by the term leakage current, earth current and residual currents Io, what i understand is that the relays measure or calculate these currents and depending on the rated value send the tripping command to the CB to open during a fault.

I have searched google but did not find any good answer related to the HV/MV Protection world.

Thanks

Reply
2
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#4
In reply to #2

Re: Difference between Leakage,Earth and Residual current

02/07/2009 9:08 PM

In considering for electrical protection all the three currents are mentioned in different situation and concepts considering type of faults.

A fault is termed Earth Fault when there is total or partial insulation failure causing large fault current to earth from the system which can cause total damage to system if the breaker is not tripped in time. For this purpose earth fault relays are incorporated in distribution panels.

An insulation deterioration due to ageing of regular insulation of equipments or wiring can cause low value regular leakage current of the range of milliamps to few amps which cannot be detected by over current relay or earth fault relay. But these currents can cause fatal accidents resulting to burning to loss of life to people working around and also results in regular energy loss.

These leakage current can be detected by residual current devices which provide earth leakage protection. These relays sense differential current or residual current and when it reach above a predefined value trips off the system. The current that operate these protection relays are termed residual current devises . In other words it is the difference between the input and output currents at the location of the relay. They are also called ELCB .

.

Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #4

Re: Difference between Leakage,Earth and Residual current

02/08/2009 12:32 AM

Good and Precise answer.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Off Topic (Score 5)
Participant
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: goa
Posts: 1
#3

Re: Difference between Leakage,Earth and Residual current

02/07/2009 12:52 AM

hai congrats,

this is my suggest,when the insulation get failure,current will take another easy way that is leakage current,and when the balance system getting unbalance that unbalance current will go on earth that is residual current. we have to measure everyone for our system and our protection

__________________
gopisusi
Reply
Reply to Forum Thread 5 comments