Lockout Relay - ANSI 86

02/18/2009 4:30 PM

Could you please explain what the lockout relay (ANSI device 86) actually means? I am working for the feeder protection system and using the Multilin SR 750 relay. I need to use the lockout for 51 and 50 protections. What I need to use for this lockout?

I noticed that the output relays (3 to 7) of SR 750 have the 'Latched' capability (page 5-27 of SR 750/60 catalog) that means once it is operated, it provides lockout function and need to push the RESET key to release the relay. If I program the relay for this functionality, does it serve my purpose of lockout (86)?

I appreciate your expertise in this regards,

Thanks,

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Lockout Relay - ANSI 86

02/19/2009 2:33 AM

Yes,

You are right. The Relay provides lockout function and needs to be reset manually or through one of the inputs poinsts of SR750 to enable closing of breaker once again.

However, please be careful when you use the SR750 contacts directly to trip the breaker since repeated use of this contact for breaking the trip coil may lead to deterioriation of the contact due to high inductive property of the breaking coil. Your design needs to address this particular issue.

Regards,

Balaji - www.protecsol.in

Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#2

Re: Lockout Relay - ANSI 86

02/19/2009 4:33 AM

86 relay can be :

1. One of Functions in Multilin (Digital Protection relay),

2. A conventional relay (coil relay), that have form like selector switch (we can rotate the handle).

this relay works like other relay, if coil energized, NO contact become NC and vise versa. But once it energized, we must rotate the handle to reset it.

Sometimes, in some plant. to increase the safety of the system, it uses 2(two) 86 relay, installed seriesly. one 86 relay of Multilin & one 86 Conventional relay.

86 conventional relay is used to guarantee if Multilin has a problem.

Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#3
In reply to #2

Re: Lockout Relay - ANSI 86

02/19/2009 8:36 AM

In most designs , you will use a separate lockout relay (86) to do all trip lockouts.

Depending on the Multilin or other electronic relay to do the lockout is a bit risky.

Lockout relays 86) usually have a trip coil and a reset handle giving positive lockout and needing a definite manual turning of the reset handle to reset.

The contacts on the lockout relays can usually handle up to 30 amps easily and also has lots of spare contacts for sending indications to lamps and control systems ,SCADA etc.

__________________
Learn more, Do more , Be more
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Lockout Relay - ANSI 86

02/19/2009 6:06 PM

Thanks so much. All replies are so helpful. Now I know what I have to do.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); djacob (1); elect-ok (1); msamad (1)

Previous in Forum: Maintaining pressure in HT cables   Next in Forum: KVAR Meter in of two generator

Advertisement