Previous in Forum: back pressure tubo generator   Next in Forum: calculate no load current
30 comments
Good Answers: 244
How to Calculate Motor Full Load Current
03/04/2009 9:42 AM
Should we consider the efficiency to calculate the motor full load current?
For example:
If we have the motor of the following specifications:
25 HP, 60 Hz, 480 V, 3 Phase, 0.8 p.f, 89% efficiency at full load
Which of the below formula should we use to calculate the Full Load Current?
Motor Full Load Current = (0.746 x 25 x 1000) / (1.732 x 460 x 0.8)
OR
Motor Full Load Current = (0.746 x 25 x 1000) / (1.732 x 460 x 0.8 x 0.89)
Good Answers: 53
Re: Motor Full Load Current calculation
03/04/2009 10:45 AM
Depends on what the 25HP is? formula 1 if 25HP is input power and formula 2 if its output power.
03/06/2009 3:27 PM
See, the original post is telling that readings are based on name plate specifications. If that is so, then it is illlogical to ask whether 25 HP is input or output.
All the name plates are giving motor output powers only.
Hence FLA = KW / 1.732 x V x pf X effi. (if motor is 3 phase motor)
Good Answers: 53
03/07/2009 2:18 AM
Where is the word name plate in original post?
And name plate is not a science it just describes certain data that is the requirements of certain standard and regimes.That does not mean there is no such thing like input power.
What if tomorrow world over convention changes and they start writing input power consumption on name plate.are you going to change your post?
Standard is a set of document that is made for our convenience but that doesn't means its the science.also its not necessary that standards are always logical. if that would be the case there would be no amendments in due course.
03/24/2009 6:36 PM
Hai You I think you no need to get so anguish on name plate details/specs and why yu are further worrying about tomorrow's world conventions?
Pls refer the specifications for making name plates. They have a set of procedures. And the directions are not only for motors but also pumps, tvs, mobiles, computers, cables, pipes, stoves, shooes, etc. It is not like that any one can write any thing.
Good Answers: 103
Re: How to Calculate Motor Full Load Current
03/04/2009 11:22 AM
Best is to check the motor rating plate and don't calculate.
calculate only if it is a homework/project work.
Good Answers: 804
03/04/2009 3:45 PM
Motor nameplate data is mechanical power. Electrical power takes efficiency and power factor into consideration. So the electrical power formula would be the one with both factored in, the second one in your post. The other one is essentially meaningless when determining current.
Your formula is a bit redundant however. No need to use .746 and then multiply by 1000, just use 746 W/ HP, so 25 x 746 / 1.732 x 460 x .8 x .89
But the Power Factor numer will vary my loading, so keep that in mind. In other words, if you want to know amps at any given amount of mechancial load on the motor, you will need to know the pf at that point, which gets worse as the load decreases. In your case here you were looking for Full Load current, so your formula is valid, I'm just pointing out that for determinig true load power consumption, you need a bit more than standard nameplate data.
Good Answers: 103
03/04/2009 8:59 PM
At our part of globe , motor name plate data do provide FLA in both Y and Δ
Alsorequired as per IEC adn NEC
http://ecmweb.com/mag/electric_understanding_induction_motor/
http://tristate.apogee.net/mnd/mfnrovr.asp
Hence I was surprised the OP is asking this question.
03/05/2009 4:12 AM
dear sir
i'm agree with you, as the data on motor name plate considering the output mechanical power, not the input electrical power so we should considering the efficiency for full load current calculation, and copmaring it with the rated current on name plate of the motor
Good Answers: 103
03/06/2009 7:48 AM
It is obviuos that you are not aware of the IEC/NEMA codes.. These codes, either of them are now adopted by most of the nations/ national codes are mede inline.
Excerpts from the first link that I referred
The NEC states that the motor nameplate must show the following information:
  • Rated voltage or voltages
  • Rated full-load amps for each voltage level
  • Frequency
  • Phase
  • Rated full-load speed
  • Insulation class and rated ambient temperature
  • Rated horsepower
  • Time rating
  • Locked-rotor code letter
  • Manufacturer's name and address
In addition to this required information, motor nameplates may also include data like frame size, NEMA design letter, service factor, full-load efficiency, and power factor.
Finally, some nameplates may even include data like bearing identification numbers, certification code, manufacturer serial number, and symbols and logos.
Since there is already the full load rated current on the name plate, which you are agreeing too, I don't see any fun in comparing with the calculation. As a regular user of the motors in various applications, from few KW to a couple of MWs, at least we do not take the pain.
03/06/2009 3:11 PM
Mr. sb
thanks for your clarification for motor name plate !!!!!!!!
but the question for Mr, msamad was
"Should we consider the efficiency to calculate the motor full load current?"
and any one can read the name plate data easily but the engineering wise is how to
learn more about it,
and if you think that the rated power on the name plate of any motor is for output
power, so????!!!!!!
Regards
Good Answers: 103
03/06/2009 10:46 PM
power.
It is not what I think, it is..
Input = output/η.
KVA = KW / cosΦ
KVA = (√3) V I
where is the question (as per as the OP is concerned) ?
and if the question is whether the motor rating KW/ HP is input (electr) of output (mech) it is already covered in quite a few threads.
In the end still the question remains - if the motor name plate already has clearly the rated current (FLA) at the rated voltage why to calculate . Unless it is a class assignment. (Of course I didn't look from this angle).
And if the voltage/ load is not the rated , even η can not be taken.
06/08/2010 9:26 AM
i will do it with you soon
02/22/2012 8:14 AM
dear Mr sb
I hope that you realize that the motor efficiency will cause extra input power than mentioned on the name plate so the motor full load line current will be greater what is mentioned on the motor name plate as all data mentioned on motor name plate based on shaft power not input power, for this reason we have motor effieciency
03/05/2009 5:28 AM
Dear
Motor Full Load Current = (0.746 x 25 ) / (1.732 x 460 x 0.8 x 0.89)
Above formula is correct
S.Pathan
India
03/05/2009 1:37 PM
The formula to be used in your case is the following:
P = I * U * sqrt(3) * pf * eff, which is
I = P/(sqrt(3)*U*pf*eff), (for Y connection)
I* sqrt(3) = P/(U * pf * eff )(for delta connection)
where
I = full load current [Amperes] or (I * sqrt(3) for delta)
P = output power [Watts]
U = voltage (line-to-line) [Volts]
pf = power factor as decimal
eff = efficiency as decimal
Since you have the output power in HP (horse-power) you have to convert it to Watts, where 1 HP = 746 W
For your data:
P = 25 * 746 = 18650 W
U = 480 V
pf = 0.8
eff = 0.89
This way you get:
I = 18650/(sqrt(3)*480*0.8*0.89) = 31.5 A (for Y/wye/star)
and I = 54.56 A (for delta connection)
The frequency does not intervene directly in the formula. To get the result in the indicated measuring unit [A] all data have to be entered in measuring units as shown above [W,V,..]
I represents in this case the full load current. For other values for other parameters you get other currents at lower loads. If the power supply system is the same ( voltage, frequency), the values for P, pf and eff vary, as other participants also pointed out.
Be careful that the value of 31.5A is valid only for a motor designed to be connected in Y (wye/star). If the motor has been designed to be connected in delta, the current value is 54.56 A.
Scientes et audaces fortuna juvat !
Good Answers: 244
03/07/2009 10:54 AM
Thanks everyone who participated in this discussion. I know it is a silly question but it is very important as I came through the problem in my design work.
I truly understand the NEC 2008 article 430 (especially 430.6(A), Table 430.250 etc.).
My problem here is:
In my design I have to use 350 HP, 4160 V motors. I don't have the motor vendor data (name plate data) at this stage of my design. It is needles to say that I have to find the motor full load current at this stage of my work. I know NEC Table 430.250 should work but Table 430.250 doesn't have any column for 4160 Volts (it has 2300 Volts column). NEC 430 doesn't say anything about how to determine the FLA for a motor of Voltages that is not available in this table. So, I have only 2 options:
(1) To convert FLA from 2300Volts to 4160 Volts with a multiplying factor (4160/2300). The FLA of the motor can be 83 x (4160/2300) = 150 A.
(2) To calculate FLA using the basic electrical formula that we are discussing.
There is nothing in NEC that we can do the option 1 (I think that is a flaw in NEC). I was trying to use the option 2 and then I came through this silly question.
I need valuable suggestions in this regards.
Hope it should now clear why it was posted.
Thanks,
- MS
Good Answers: 103
03/07/2009 1:06 PM
That's why you should put the cards down in the beginning .
Well now you have the answers. (Several of the threads but boils down to same)/
But what is your assumed η ?
And remember you have to take care of the starting current too.
03/09/2009 12:28 PM
MS,
When going from a lower voltage to a higher voltage the current goes down. Considering the efficiency, power factor nearly similar, for the same rated power, the full load current in your case should be 83 x 2300/4160 = 45.3 A.
The NEC is not a design tool, so it does not indicate any possible situation.
Item under 2 (basic formulas) is always valid if applied correctly.
Good Answers: 244
03/09/2009 12:49 PM
Thanks so much. It is my mistake - realized after the post.
Good Answers: 103
03/09/2009 10:01 PM
Getting clarifications always welcome (never mind our barbs)
The problem is with so menay homeworks going on (Is it homework season?) it becomes difficult for us to distinguish homework from actual doubt.
At least put your biodata in profile, since at least we can check and answer accordingly.
Good Answers: 804
04/05/2010 12:36 PM
Just as a general rule-of-thumb, 4000V motors can be estimated at .14A/HP. This value is shown in most EASA motor application booklets, unfortunately you can no longer get those on-line for free, they sell them now. If you know of a good EASA member motor shop in your area, they may give them away to customers.
04/05/2010 1:57 AM
Why need to calculate when there is name plate? How about if there is none? I think the point here is to be able to know how you derived the answer, what is the correct formula in getting the answer. Its just like how you get the 3.1416 on Phi? oh yeah because my teacher said so.
Good Answers: 804
05/31/2010 5:58 PM
From Post #13...
"My problem here is:
In my design I have to use 350 HP, 4160 V motors. I don't have the motor vendor data (name plate data) at this stage of my design. ..."
08/08/2014 10:52 AM
Dear Mr.msamd
For your Point " Should we consider the efficiency to calculate the motor full load current? " my answer is yes it is to be accounted. That is as you have stated "Motor Full Load Current = (0.746 x 25 x 1000) / (1.732 x 460 x 0.8 x 0.89)
DHAYANANDHAN.S
11/03/2014 11:47 AM
Dear Mr.msamad,
Yes. The Motor Efficiency will have to come in to picture while arriving at the Full Load Current.
DHAYANANDHAN.S
01/04/2021 11:19 AM
The motor manufacturer will have done this already. The answer is on the rating plate attached to it.
01/05/2021 1:52 PM
Reading the other comments about nameplate data, I had to reconsider the original posters question and how it in itself is lacking. For instance, other factors that can effect a motors efficiency and it's power requirement would include things like, how long are the wires and how large are they and how far from the overloads? What are the ambient temperatures? What is the mechanical load type? (A fan blade would have different effects than a piston compressor for instance.) Also, full load current on the nameplate also assumes at a given rpm. A true max would be at locked rotor.
Don't follow in the footsteps of someone who you wish to emulate. Instead, seek what they sought.
Good Answers: 137
01/06/2021 9:53 AM
Apart from the fact that this question dates back to 2009, I don't agree with most of that.
The OP was just asking which of 2 formulas is the correct one, and as several posters have said, it's the 2nd. The rated (output) power, efficiency and power factor are given, and would be at specified conditions. If the user wants to run the motor outside those conditions, eg at high altitude, high temperature it's up to him to apply derating factors, but doesn't affect the calculation here.
Provided the specified voltage is available at the motor, the supply cable details don't affect the question. Neither does the type of load, this would just be 25HP at rated (full load) conditions. The power at different speeds (via an inverter) would vary with load type, but that has not been asked.
The rpm will be what it is for that motor, and doesn't come in to the calculation. The OP didn't ask for locked rotor current, just full load current.
01/06/2021 10:35 AM
I guess my point is that just knowing what the calculated full load current is , is just a starting point and not the end value. I didn't even mention that an oversized motor will work better/cooler than an exact sized motor and using a VFD the HP can be limited to what the load requires.
Good Answers: 137
01/06/2021 11:43 AM
OK no problem.
It's unlikely the power absorbed by the load exactly matches the motor rated power, usually it's in between and the next higher motor power is selected.
Register to Reply 30 comments
Anonymous Poster (2); Codemaster (2); dhayanandhan (2); EBrown (2); eng.hmk (3); jebronx (1); JRaef (3); k.dhana (2); msamad (2); PWSlack (1); rakesh_semwal (2); sb (6); tomad (2)