Fire Tube Boiler Tube Leaks

03/06/2009 12:06 PM

What can cause fire tube water leaks at the expanded (flaired) ends in low-med (7 kg/cm2) pressure boilers (Cleaver Brooks CB 250 4 pass)? Feed water temp was low 160F and deaerator not working up to par. Two failures occured simultaneously in two different boilers.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Fire Tube Boiler Tube leaks

03/06/2009 12:24 PM

To give any comment on this we require lot of parameters.

Please share your contact details sp that we can talk and get parameters

Register to Reply
Commentator

Join Date: Feb 2008
Posts: 59
#2
In reply to #1

Re: Fire Tube Boiler Tube leaks

03/06/2009 12:44 PM

I am the facility manager for a US govt project in Panama. In our boiler room we have 3 CB 250 4 pass fire tube boilers. We have a maintenance contract with the local CB rep, and we do water treatment. Makeup water is softened to zero ppm hardness. The deaeration system needs some work (the auto pressure regulator doesn't work and the steam pressure and temperature is maintained by opening a manual block valve). Given all this we shouldn't have suffered double failure on two different machines, unless something else is afoot. Maybe my question should have been: what could cause tube failure at the flaired ends (first pass) in a fire tube dry back boiler?

hughes838@yahoo.com

Register to Reply
Power-User
United States - Member - USA Engineering Fields - Control Engineering - Never enough money

Join Date: Feb 2007
Location: Oregon
Posts: 292
Good Answers: 4
#4
In reply to #2

Re: Fire Tube Boiler Tube leaks

03/07/2009 3:02 AM

(the auto pressure regulator doesn't work and the steam pressure and temperature is maintained by opening a manual block valve).

Two things jump out at me, pressure and thermal shock. If you have instrumentation on your boiler and trend the data to a chart recorder or SCADA, I would look for temperature and pressure spikes, both positive and negative. Human operators are notorious for doing things the wrong way and breaking things, then lie about what they did.

I suspect that your operators are letting too much air/gases to build up in the boiler then they vent too fast causing the boiler to expand and contract destructively. Boilers do best when ran in a steady state with slow changes.

If you do not have pressure and temperature for each boiler being automaticly recorded I would stronly suggest that you include it as part of your repair of the boiler.

Register to Reply
Commentator

Join Date: Nov 2008
Posts: 72
#3

Re: Fire Tube Boiler Tube Leaks

03/07/2009 1:33 AM

i think you have to check the refractory brick in the reer end

may be it causes thermal expansion makes the leak

Register to Reply
3
Power-User

Join Date: Dec 2006
Posts: 408
Good Answers: 5
#5

Re: Fire Tube Boiler Tube Leaks

03/07/2009 4:11 AM

Well I spent about 12 years working on steam boilers- the CB were known to have weak backs- ie they liked a steady load- any excess could strain(over expand) the expanded joints- then leak. The most likely thing I found was inadequate water chemical treatment coupled with no blowdown to manage tds of boiler water- the tubes became insulated, overheated,over expanded-leaked. Before I arrived at this establishment, the previous had believed b/s & fitted a magnetic feed water inlet device guaranteed to eliminate corrosion, automatically soften water, eliminate blowdown etc!!!. Well, at annual inspection, I had never seen such scale& corrosion inside a boiler! Oh& needed to r/p several tubes, & expand all others!.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#6

Re: Fire Tube Boiler Tube Leaks

03/07/2009 6:09 AM

Corrosion occurs due to carbonic acid attack and oxygen pitting. Carbonic acid attack occurs due to CO2, which is the breakdown product of carbonate alkalinity in the boiler, condensing with water to form H2CO3. This results in the "grooving" of condensate piping, which usually shows up first in leaks at threaded sections. Oxygen pitting occurs as steam condenses and the vacuum created pulls air into the system. Because of the localized nature of oxygen pitting it can cause relatively quick failure in boiler tubes and condensate piping system.

The most common method of addressing carbonic acid attack is through the use of neutralizing amines. These chemicals, such as morpholine and cyclohexylamine neutralize the carbon acid, and increase the pH of the condensate

This is also known as Ferric Oxide Attack caused this. This is a mixture of Oxygen + Water (CO2) and obvious due to presence of oxygen because:

1. Feed water temperature to be 212F where the oxygen content is 0.

At your lower feed water temperature of 160F the oxygen content was 3.75 cc/litre.

2 . deaerator not at par.

This damage has been due to your own negligence as not maintaining a higher feed water temperature at 212F as recommended by all Boiler manufacturers and neglecting the De-aerator.

Check also the ph of your condensate return for not being acidic.This must be maintained at 8.3 or higher.

Reading your para I am able to figure out that your pipelines both steam & condensate have aged and the return is corrosive.

Regretfully, the damage inside the Boiler is more than that you've already discovered only with the tubes leaking. Other tubes may have also been pitted and sitting to be explored with passage of boiler operation.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2008
Posts: 59
#7
In reply to #6

Re: Fire Tube Boiler Tube Leaks

03/07/2009 9:53 AM

I would like to thank all the professionals who answered my question with such a wealth of knowledge on the subject matter! I am an electrical engineer saddled with the responsibility for O & M at this facility, so my knowledge of mechanical engineering is rudimentary at best. Maybe I'll keep my job! Just one more detail that remains unanswered, in my understanding of boiler technology. What is the optimum temperature for the feed water to avoid possible cavitation of the feed water pumps (DA tank bottom is 10 feet off the floor)?

hughes838

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#8
In reply to #7

Re: Fire Tube Boiler Tube Leaks

03/07/2009 2:52 PM

What is the optimum temperature for the feed water to avoid possible cavitation of the feed water pumps. Stay below 80C. But for every drop of 6C feed water temperature there is a 1% increase in the fuel consumption and drop in Boiler efficiency.It is better off buying preferably a Grundfos/equivalent Feed Pump that can withstand above 110C feed water temperature.

(DA tank bottom is 10 feet off the floor)?- This is the cause for your pump cavitation.

Recommended height for 100C feed water temperature - 4.5 metres minimum tank bottom

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 408
Good Answers: 5
#9
In reply to #7

Re: Fire Tube Boiler Tube Leaks

03/09/2009 3:07 AM

In my experience, we heated feed water to reduce thermal shock & to release dissolved gases such as oxygen & CO2- we mainly found that 90'C to 95'C was enough- despite low height of tank- the reason for cavitation was found in every case to be nrv leaking back(using centrifugal pumps)- the steam was forming vacuum in pump inlet- refurbish of nrv fixed the problem in every case.

Register to Reply
Associate

Join Date: Jun 2008
Posts: 25
#10

Re: Fire Tube Boiler Tube Leaks

03/15/2009 11:03 AM

Deaerator is very essential to remove dissolved oxygen from the feed water.Dissolved oxygen may be one of the cause for you failures. Please heat the feed water upto 100 Deg.C (min.) and then fed to the boiler.

Register to Reply
Commentator

Join Date: Feb 2008
Posts: 59
#11

Re: Fire Tube Boiler Tube Leaks

03/15/2009 12:50 PM

Thanks again to all! The DA tank is working properly now (95 - 100 C) and the water chemistry is indicating that we may be OK so far. The boiler tubes have been repaired also. The check valves (nrv's) in the boiler feed lines are holding (thanks Neil!) well, so far. Thanks again to all who provided such great assistance!

hughes838

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); ducon (2); hughes838 (3); mostafaalkholy (1); Neil Kwyrer (2); Richard L (1); takle (1)

Previous in Forum: help? with pressure   Next in Forum: ASTM

Advertisement