what is difference between primary current injection & secondary current injection

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: current injetion

04/24/2009 1:41 PM

These two terms are related to the testing of the protection system which involves the CT and protection relays.

Primary current injection is the injection of current in the primary circuit of the CT, while secondary current injection is the injection of current directly to the protection relay. In the case of primary current injection, the bad thing is you need high current value to inject (generally the phantom set is used to generate the high current value), but the good thing is the protection system is tested including the CT. On the other hand, for the case of the secondary current injection, you can inject a current up to 5A (generally a secondary current injection set is used) but only the protection relay is tested.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2
In reply to #1

Re: current injetion

04/27/2009 8:57 AM

I would like add it also makes sure the polarities of ct and pt .

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#3

Re: current injetion

04/28/2009 5:28 AM

The primary current injection comes before the secondary current injection.

i.e. the first recent inject occurs prior to the prior previous injection.

Got it?

Reply
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#4

Re: current injetion

01/08/2011 7:27 AM

MSAMAD respone is correct. In addition, it would be best to carry out both primary and secondary injection test to ensure protection circuits are operational.

In the primary injection, you could check 1) polarity of the CT 2) accuracy of installed wiring 3) protection relays and meters in the circuit could be verified if they are all fully functional, most important, the circuit breaker is tripping.

In the secondary current injection, 1 A or 5 A is injected, wiring from protection relay to breaker is verified, but not wiring from CT to protection relay.

Best regards,

rudy_fernando5r

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); msamad (1); nesubra (1); rudy_fernando5r (1)

Previous in Forum: Short Circuit Matter   Next in Forum: Contactor Electrical Maintenance in Practice

Advertisement