Anonymous Poster

Touching a HT Line

06/15/2009 5:02 AM

The "Times of India' (news paper) dated 14.06.2009 carried a news that one person in bangalore, got fatal injuries by accidentally stepping on a HT (high tension) line which was laying on the ground.

My question is how can a line be "alive" even after touching the ground?. Don't we expect the nearest (as per zones of protection of relays) circuit breaker to trip, in such cases.

I expect the CB to operate, the moment the HT line disconnects from the mains and before touching the ground (a case of open circuit).

Regards,

PG

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#1

Re: Touching a HT line

06/15/2009 6:52 AM

You are right protection should have operated.But it is possible th line was close to ground and not actually touching .In all probability it should have been a 11kv line when they say HT.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Commentator

Join Date: Mar 2009
Posts: 71
Good Answers: 6
#2

Re: Touching a HT line

06/15/2009 7:20 AM

Since for most journalists "High Tension" ("High Voltage") might be anything starting at 110V, I checked the news. Well, it was 11 kV, as Nesubra correctly guesses. But it turns out that it wasn't a live wire lying on the floor. The wire, which ran "across a roof", was touched by a boy with a piece of metal wire:

http://timesofindia.indiatimes.com/Cities/Bangalore/Boy_suffers_90_burns/articleshow/3480970.cms

So CBs are not to blame. The power company's carelessness is.

Perhaps the following is off topic, but I think it's somewhat related. I've been living in Florida for a full year, and had been here a few times before. Since then I've noticed that after a few months with little or no rain there are always blackouts when the first rain happens, even if it is light and with no signs of thunderstorms.

My conjecture (which is just that, a guess) is that these first coming rains make some tree branches heavier, and then they bend over the wires. The power company has a poor inspection/maintenance record, so it's easy to suspect that they wouldn't care much about lopping potentially dangerous branches.

Can anyone clear this up?

Reply
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Touching a HT line

06/15/2009 7:36 AM

<...So CBs are not to blame. The power company's carelessness is....>

Oh, so unauthorised access to the roof wasn't a factor, then?

And a lack of parental guidance wasn't a factor either, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 3)
Commentator

Join Date: Mar 2009
Posts: 71
Good Answers: 6
#4
In reply to #3

Re: Touching a HT line

06/15/2009 7:50 AM

Surely are they. But personal safety shouldn't rely just on parental guidance. Please, spend a minute reading The Times of India, especially the final paragraph:

"Hanging high-tension wires are a menace. Climb up any terrace, ans you will see a clutch of wires tangled together, all perhaps within arm's reach".

Reply
Anonymous Poster
#19
In reply to #3

Re: Touching a HT line

06/15/2009 11:33 PM

Oh, but you are ever so English sometimes

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #2

Re: Touching a HT line

06/15/2009 8:20 AM

Since then I've noticed that after a few months with little or no rain there are always blackouts when the first rain happens, even if it is light and with no signs of thunderstorms.

And I thought it happens only in India .

We are smarter (or rather our power companies are, we are poor consumers) They normally cut the power with the premonition that something may happen..

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Off Topic (Score 5)
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#27
In reply to #2

Re: Touching a HT line

06/16/2009 1:01 PM

Although trees may account for some of the momentary outages (or sustained outages if the resulting fault cannot be automatically cleared) another more likely cause is contamination flashover. Contamination flashover of insulators typically occurs when heavily contaminated insulator surfaces are lightly wetted by fog, dew, light rain, etc.

As long as the contamination coating remains dry, there is no danger of flashover but when the contaminant includes water soluble salts and is lightly wetted, leakage currents begin to flow in the interface between the contamination coating and the insulator surface. Flashover occurs if those currents reach 100 milliamps or so.

The most severe contamination is hard, crusty buildup from fertilizers, salt, cement dust, discharge stacks, bird droppings, etc. that is not removed by natural heavy rain washing. In those cases, utilities must remove the contamination by washing with high pressure water, abrasion blasting with soda, crushed walnut shells or some other media while the line is energized or chipping and hand washing if the line can be deenergized for cleaning.

Reply
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#6

Re: Touching a HT Line

06/15/2009 8:24 AM

I remember reading several stories of people in india stealing power from the lines by attaching hooked bare wires to the lines. This may also had been a factor. They would pay children to shimmy up poles and clip on the wires. Maybe he attached to the high tension by accident. It's a shame it happened to anyone, never mind a young boy.

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Reply
Guru

Join Date: Dec 2008
Location: nj,usa
Posts: 1253
Good Answers: 33
#7

Re: Touching a HT Line

06/15/2009 8:29 AM

Never trust a circuit breaker or automatic disconnect. These protections are expected to work but if they are not maintained properly they can fail. I always expect that a circuit is still live (even with the CB open) until I test it with a meter.

__________________
CARPE CRUSTULORUM!
Reply Score 1 for Good Answer
Anonymous Poster
#17
In reply to #7

Re: Touching a HT Line

06/15/2009 3:59 PM

Don't you test the meter, first?

Reply Off Topic (Score 5)
Guru

Join Date: Dec 2008
Location: nj,usa
Posts: 1253
Good Answers: 33
#42
In reply to #17

Re: Touching a HT Line

06/20/2009 7:36 AM

good point.I tend to keep my meter well calibrated.

__________________
CARPE CRUSTULORUM!
Reply Off Topic (Score 5)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#8

Re: Touching a HT Line

06/15/2009 8:31 AM

I saw a video several days ago with a guy on top of an electric train in either India, Bangladesh, or some other country nearby, who started walking down the train car and casually reached up and grabbed the HV wire above it. Needless to say, he's no longer with us.

I don't know how to upload the video, and it may be a good thing, as it's rather gruesome!

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Associate

Join Date: May 2009
Location: Kansas City, Missouri
Posts: 48
Good Answers: 2
#9
In reply to #8

Re: Touching a HT Line

06/15/2009 9:02 AM

hey bill. i think those were just low-lying power lines...don't ask me why they were that low, but here's the link to the video you might be referring to.

__________________
E pur si muove -- Galileo
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#10
In reply to #9

Re: Touching a HT Line

06/15/2009 9:31 AM

Yep, that's it. If the train isn't electric, I wonder why anyone would run a power line down the tracks above the train??? Most are off to one side . . .

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
2
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#11
In reply to #10

Re: Touching a HT Line

06/15/2009 2:17 PM

I would have to assume that the train is electric and that the man touched what New York subways call the "Third Rail." In New York some trains are electrically powered by an electrical conductor that runs on the ground. Brushes under on the train contact the rail to power electric motors. The current carrying capacity through this rail is very high, so the fault current produced by electrocuting a man would not be nearly enough to trip the circuit breaker or blow a fuse. The same is generally true for an power distribution line which is why access is supposed to be limited to only trained personnel.

Going back to the boy on the roof:

Assuming the electrical resistance of the boy's body is 10 kilo-Ohms, and the voltage in the line is 11 kilo-Volts, then then by Ohm's Law:

V=IR => 11kVolt / 10kOhm = 1.1 Amps

Such a small amount of current wouldn't even trip a residential AC branch circuit. Solid state devices such as Ground Fault Circuit Interrupters (GFCI) and Arc Fault Circuit Interupters (AFCI) are available to protect against electrocution hazards for small circuits, but it would be very impractical to use such devices for power distribution lines.

This is why it is important that build standards must exist to prevent accidents, and that such standards must be enforced to prevent deliberate actions that lead to tragedy. If no authority enforces the rules, then no matter how high the line is run someone will make a stick long enough to reach it. Also, the general public must be educated to be wary of electrical lines and cables from an early age to help them understand the danger of careless behavior or tampering with wires.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply Good Answer (Score 2)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#12
In reply to #11

Re: Touching a HT Line

06/15/2009 3:33 PM

" . . . then no matter how high the line is run someone will make a stick long enough to reach it."

Yep, you're right! I gave a deposition to a lawyer for an insurance company (as a so-called expert as well as a professional engineer) saying that the 7.5 kV line running across the plaintiff's property was above the minimum height requirement, and when asked, "What do you think happened?," I replied, "I think the guy and his wife lost control of his 80 foot CB antenna pole when they were trying to move it to a new location, and they allowed it to fall onto the power line."

Luckily for them, the pole was so flimsy that it bowed enough to contact the ground line running beneath the three hot legs just after it first contacted the lowest hot leg, blowing the fuse, and they escaped with their lives, although the arc burned them both and actually blew the shoes off the woman and set them on fire.

The case never went to court.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#14
In reply to #12

Re: Touching a HT Line

06/15/2009 3:49 PM

So let me get this straight... They were trying to move an 80' tall antenna without dismantling it???

I guess no matter how hard you try to make something idiot proof the world will always produce a better idiot

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply Off Topic (Score 5)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#16
In reply to #14

Re: Touching a HT Line

06/15/2009 3:58 PM

Spot on!

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#25
In reply to #9

Re: Touching a HT Line

06/16/2009 11:12 AM

I hads to search first to find it, here is the link I believe:-

http://www.youtube.com/watch?v=ausFe4svcLs

Traction current is often 6000volts I believe on many railways.......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#39
In reply to #25

Re: Touching a HT Line

06/17/2009 8:31 AM

I think I saw the video you refer to. Traction voltages often used on overhead traction lines are 25kV AC, 3kV DC, 1,5kV DC, 50kV AC, and some non-standard frequencies AC in Europe. Lower voltages are often fed by a third-rail method, mostly in urban areas. The line seen in the picture is often called the contact wire, as it is the wire that the pantograph contacts to draw current, and is always "live". It is suspended from the wire above it (often called the catenary wire, due to the catenary curve of such free-hanging wires) with dropper wires or jumpers to keep the contact wire parallel with the track.

In South Africa we also have the so-called train surfers, that stand on top of moving suburban coaches as the train moves through the section on overhead line-fed sections, swerving to duck the steel structures and registration arms that register the contact wire. Needless to say many of them don't make it, touching 3,000V DC is rather bad for your heart. Remember that DC traction systems as a rule cannot discriminate between a fault current, overload or earth faults - it just measures the current flowing through the CB and it trips at a given calibrated value (between 3000A-5000A in our case). The fact that the breakers sometimes do trip when these events take place just goes to show how unpredictable electrical parameters can be!

BTW, from the actions of the bystanders, I'm of the opinion that the chap in the video was committing suicide, or was doped/drunk.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#40
In reply to #25

Re: Touching a HT Line

06/18/2009 6:14 PM
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#41
In reply to #40

Re: Touching a HT Line

06/18/2009 6:24 PM

Well done.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#13

Re: Touching a HT Line

06/15/2009 3:47 PM

OK getting back to the original question.......

My question is how can a line be "alive" even after touching the ground?. Don't we expect the nearest (as per zones of protection of relays) circuit breaker to trip, in such cases.

I expect the CB to operate, the moment the HT line disconnects from the mains and before touching the ground (a case of open circuit).

This is not the case when there is a high impedance path thru earth back to the CB (in the case of a bonded earth power system). A live line can fall on, say a dry tarmac road and the current flowing back thru the CB could be as little as 5A, much too low to trip the CB. In these cases additional protection called sensitive earth fault detection is necessary to ensure that if a line falls the small fault current is detected and the CB is told to open. This form of protection is commonly employed down here.

__________________
jack of all trades
Reply Good Answer (Score 3)
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#15
In reply to #13

Re: Touching a HT Line

06/15/2009 3:55 PM

Good Point J-o-a-T

The OP originally asked about a line that falls to the ground. Everyone is trying to explain what happened based on an altogether different situation.

GA from me.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply
Anonymous Poster
#18
In reply to #13

Re: Touching a HT Line

06/15/2009 4:04 PM

I gave you a GA, too, but I want to remain anonymous, in case that your answer is ...wrong

Reply Off Topic (Score 5)
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#21
In reply to #13

Re: Touching a HT Line

06/16/2009 4:10 AM

I agree with your explanation. When we were in the 6th semester of engineering, we studied, the following types of faults:

line to ground,

line to line,

double line to ground,

all 3 lines to ground and

Series fault.

What about the last type of fault. I think, the moment the HT line got disconnected from the pole ( a case of open circuit), some CB should trip, indicating unbalance.

what are your views?

Regards,

PG

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#31
In reply to #21

Re: Touching a HT Line

06/16/2009 3:30 PM

What about the last type of fault. I think, the moment the HT line got disconnected from the pole ( a case of open circuit), some CB should trip, indicating unbalance.

Like a loss of load trip. I am not sure as I have never come across this specific form of protection. It may just be implemented at the SCADA level as a warning to the control room operators that the load to a feeder has suddenly been lost, as the common problems are momentary or permanent short circuits due to trees touching lines or lines knocked down by cars hitting power poles. Normally the fallen power line has to fall on something and create a fault path thru ground back to the protection (in the case of an earthed electrical system).

__________________
jack of all trades
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#33
In reply to #31

Re: Touching a HT Line

06/16/2009 3:40 PM

I agree in principle, but do they do that on the HV side? It would be interesting to find out!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#35
In reply to #33

Re: Touching a HT Line

06/16/2009 3:51 PM

All the protection monitoring I deal with is on the HV side, as is most of the lines company SCADA operator control room monitoring. LV transformers branching off the HV lines are protected by their own fuses so in the event of a problem on the LV the fuse opens and isolates a few (or one) customers, and generally the fault will occur inside a specific home and as such will be disconnected by the customers protection inside their home before the LV transformer fuse operates (hooray for circuit protection discrimination).

__________________
jack of all trades
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#28
In reply to #13

Re: Touching a HT Line

06/16/2009 1:12 PM

So you're saying that not all earth connections should be considered a good ground. Interesting.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#30
In reply to #28

Re: Touching a HT Line

06/16/2009 3:11 PM

And fully correct.

It also depends upon when it last rained as to how conductive or not, the ground is at any one point.....what the composition of the ground is, how far away it is from the sunstation etc etc etc etc.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#32
In reply to #30

Re: Touching a HT Line

06/16/2009 3:38 PM

Sorry, "Substation" was meant, it was dark and the characters are next to each other on the keyboard....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#34
In reply to #28

Re: Touching a HT Line

06/16/2009 3:44 PM

So you're saying that not all earth connections should be considered a good ground

Or at the same potential.

We have one site example where the earth resistance between a substation and remote piece of concrete pad-mounted metal switch gear was large enough to create a potential difference between the switchgear metal case and the ground next to switchgear, during a permanent low current phase to earth fault (to low to be detected by the MCB protection). Some time later a child standing in the grass touched the metal switchgear and recieved a shock, fortunately the child was not seriously injured.

An earth is an earth is an earth? Yeah right, its a lot more complicated than most people think (that's why we Engineers get paid the big bucks end up trying to sort out all the real world problems).

__________________
jack of all trades
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#20

Re: Touching a HT Line

06/15/2009 11:44 PM

Apparently we must have overloaded YouTube. The link given in post #9 has been taken off line. I saw it earlier but it is no longer available.

Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#22

Re: Touching a HT Line

06/16/2009 7:43 AM

Many years ago I was staying at a farm in Maine. A hurricane knocked over a high voltage pole in a field, and a cow that was near the live wire was electrocuted. When the workers came to fix the power line, they wore rubber boots and took very small steps as they approached the live wire. Upon inquiry, they told me that the surface of the earth is not always at ground potential. Voltage gradients from the wire potential to ground can easily be lethal and chances of electrocution increase with the distance between ones feet. The poor cow didn't know this and even if she did, there was probably little she could do about it.

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#24
In reply to #22

Re: Touching a HT Line

06/16/2009 10:09 AM

that is called a step pottential .Quadrapeds have this problem .step pottential can be high enough to harm them.In Mumbai enter in to any apartment and look at the main Distibution board.Except the wireman who is in charge no one can even guess which wire goes where.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply Off Topic (Score 5)
Anonymous Poster
#43
In reply to #22

Re: Touching a HT Line

06/20/2009 9:29 PM

So, if you are playing golf and a thunderstorm comes up, stand with both feet firmly on the ground, and your hands gripping a putter likewise held to ground.This will form a 3 legged voltage divider so it wont hurt so bad when you get struck by lightning (:;).

Reply
Guru
Engineering Fields - Nuclear Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Apr 2009
Location: From going to and fro on the peninsula and walking up and down on it
Posts: 538
Good Answers: 6
#23

Re: Touching a HT Line

06/16/2009 8:45 AM

welderman brought up an important point and I think someone with the knowledge should clarify it. I took an OSHA class and one of the discussions was on how to dis-mount from an accidently energized vehicle. Now my memory is fuzzy on it, but it seemed to involve jumping clear and shuffling feet, not lifting feet above surface to exit danger zone. Anyone qualified to discuss this. maybe prevent a tragedy in the future?

And those rubber tires, definitely NOT INSULATED!

__________________
oderint dum metuant
Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#26
In reply to #23

Re: Touching a HT Line

06/16/2009 12:37 PM

If the vehicle is not burning or arcing and there is no danger of explosion, it's best to remain in the vehicle, without touching door handles, frame or any other metal object until the voltage source has been disconnected or removed and the vehicle deenergized.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#36
In reply to #23

Re: Touching a HT Line

06/16/2009 4:16 PM

You've mentioned a few things about impedances here. First rubber tires today often have the semi-conductor carbon added to them to bleed off static charge produced by the air rubbing against the body of the car. So a high voltage power line dropped onto the chassis of an automobile will rarely be considered an electrical fault condition to any of the power distribution circuitry. (This resistance is high enough that I don't expect overheating of the tires but depending on the line voltage on the fallen wire I guess a rare case this might happen.) So to not be electrocuted the safest thing is to stay in the vehicle. Do not touch anything outside of the vehicle until a lineman tells you. You are like the bird on the wire. If and only if you will lose your life by staying in the vehicle, should one attempt to leave the vehicle. You now must leave the vehicle without ever simultaneously touching the vehicle and anything else. In simple terms, jump for your life.

Now when a power line is discharging to the earth back to the power distribution grid, the current path will be a chaotic, unpredictable shape that will likely be changing as moisture boils out of certain parts of the soil. Since water and soil are not a good conductor, the ground will be at different voltage potentials depending on the path taken at that instant in time. (Think about the wiper on a potentiometer.) So to get oneself out of this problem, keep your feet together and shuffle your feet slowly away from where the power line lies. DO NOT walk or run. The voltage difference between your front foot and your back foot just might be enough to kill you. This is only a method for getting out of a bad situation. Hopping can work but is more prone to causing a stumble. If you fall over or spread your feet for a mechanically more stable position you might find to big of a gradient.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 4)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#29

Re: Touching a HT Line

06/16/2009 1:53 PM

Here are another couple of You Tube videos of power lines discharging directly to earth without causing immediate circuit breaker interruptions.

http://www.youtube.com/watch?v=p3T9qF0nMxY&feature=related

The above video shows a live cable lying on the ground. The constant quiet growl in the audio background implies to me that this is just 120/240VAC house current.

http://www.youtube.com/watch?v=zcW3dbyRLxY&feature=related

The above video shows a power line that has fallen into a creek. The arc is very bright.

People wrongly think that circuit breakers are to protect people, they are not. They protect wiring from overheating from excessive current. As somebody earlier stated, Ground Fault Circuit Interrupt (GFCI) protect people. This is why in the US they are mandatory for outlets installed in close proximity to plumbing and outside services.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#37

Re: Touching a HT Line

06/16/2009 4:48 PM

I had a 25 kva sub 12.46 kv where a phase fell into a ditch with water and did not trip the breaker. I stopped and watch the water boilling. The sub was fairly close by and the ground fault relay was set to pickup at 250 amps but never triped the breaker..

Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#38
In reply to #37

Re: Touching a HT Line

06/17/2009 4:29 AM

You are absolutely right. This has been a common problem in india, especially during rains seasons and is story of many movies.

Regards

PG

Reply
Reply to Forum Thread 43 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (5); Anonymous Poster (4); Bill (4); Bluestone (2); charsley99 (1); EElectrician (3); fernandotasso (2); FLIPFLOP (1); gideon (1); jack of all trades (4); nesubra (2); not so smart (2); packrat561 (1); prashanthng (2); PWSlack (1); redfred (3); sb (1); wareagle (3); welderman (1)

Previous in Forum: How to wire GFCI recepticle with non GFCI recepticles   Next in Forum: current carring capacity

Advertisement