Maximum Flow in a Piping System

07/27/2009 8:25 AM

Hello,

I am having a little determining the maximum flow in a piping system I have. I have a regulator with an output of 0-50 psi and I would like to know what is the maximum flow rate I can have with 50 psi.

I remember a formula I used for needle valves which was:

GPM = Cv * sqrt[pressure drop / specific gravity of the liquid]

GPM:gallons per minute

Cv: Coefficient of volume (specific to the valve)

Pressure drop: pressure differential between the regulator and the pressure at the exit of the piping

Specific gravity of the liquid: specific to the liquid used

I guess there should be a way to determine the maximum flow rate in a piping system the same way or not?

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Maximum Flow in a Piping System

07/27/2009 9:07 AM

What pipe size is the regulator?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#2
In reply to #1

Re: Maximum Flow in a Piping System

07/27/2009 9:09 AM

I think I had stated it in the question:

Pipe size: 1/4"

Regulator: 0-50 psi

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Maximum Flow in a Piping System

07/27/2009 9:20 AM

9.5e-5 m3/sec for 1/4" Ø at 3 m/sec liquid max velocity, or about twice the rate a human can send urine. Is this in the right tennis court or is there something wrong with the question data?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#5
In reply to #3

Re: Maximum Flow in a Piping System

07/27/2009 9:31 AM

and how do you get to this result with the pressure of 50 psi?

Does the fact that the gas is CO2 changes something?

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Maximum Flow in a Piping System

07/27/2009 9:42 AM

The fact that is it gas changes everything, for the original post mentioned liquid.

3 m/s is about the max for liquids, and 10m/s for gas. So multiply 9.5e-5 m3/sec by 10/3.....

Oh, say, a balloon-full in 5 seconds? Is this on the right cricket pitch?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jun 2009
Posts: 43
#7
In reply to #6

Re: Maximum Flow in a Piping System

07/27/2009 10:11 AM

I don't really understand why the limit is 10m/s.

For example if I have:

Pressure = 0.5*(density*v^2)

for 50 psi, and the density for the gas (let's say methane which is 0.68 kg/m^3) then I get v=1006 m/s

Is the flow speed limited because of the size of the pipe (1/4")?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Maximum Flow in a Piping System

07/27/2009 10:40 AM

Flow speed is limited because of the economic limit in the pipe. If the fluid is doing more than 3m/s for a liquid and 10m/s for a gas, then the pipe is too small. If the flow is sonic, then the valve is too small.

What is the process? First it was liquid, then it was carbon dioxide, now it's methane....

What is it doing - gas reservoir boost equipment or something? If so, then why only 1/4in Ø? Very confusing......

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#9
In reply to #8

Re: Maximum Flow in a Piping System

07/27/2009 10:48 AM

well sorry for the mix.

In fact I have a tank of methane and another one of CO2. Both merge to a a single pipe going to a diesel engine (to simulate biogas injection). (all the pipes in the setup are 1/4")

The biogas flow rate I am looking to obtain is around 40 L/min. I wanted 100 psi regulators but I could only get 50 psi regulators. So I want to make sure I can get that flow rate of 40 l/min (about 30 l/min of methane and 10 l/min of CO2) to the engine

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Maximum Flow in a Piping System

07/27/2009 10:51 AM

How big is the engine?

Why are pressure regulators being used?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#11
In reply to #10

Re: Maximum Flow in a Piping System

07/27/2009 10:57 AM

Well biogas has a composition of:

60% CH4 and 40% CO2. Injecting biogaz in the air inlet of the diesel engine reduces the consumption of diesel. The goal of the project is to study the effect on performance in a diesel engine functionning with dual fuel (biogas-diesel).

Thats why it's interesting to inject CO2 in the engine.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: Maximum Flow in a Piping System

07/27/2009 11:11 AM

Right, so now the gas is going into the air intake instead of the fuel injection system. That wasn't clear. It is now. OK. Next question.

Instead of expensive pressure regulators, why not use a simple needle valve instead?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#14
In reply to #13

Re: Maximum Flow in a Piping System

07/27/2009 11:15 AM

Well at the university we don't have much methane and CO2 available so we took high pressurized tanks and we found some 0-50 psi pressure regulators, so the price isn't much important.

The question now is to know is the pipe of 1/4" can prevent a flow of 40L/min or if the pressure of 50 psi isn't sufficient to delivre the required flow rate.

PS:

I am using a needle valve to make precise adjustements of the flow rate of biogaz (in order to have a stoechiometric combustion).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #14

Re: Maximum Flow in a Piping System

07/27/2009 11:41 AM

OK. Arrival at last.

Use the Weisbach-Darcy generalised pipe flow equation on the pipe to determine the pressure drop along its length for a flow of 40l/min. If the answer exceeds 50psi, then the pipe is too small, and either a larger pipe or a higher pressure regulator will be needed.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#16
In reply to #15

Re: Maximum Flow in a Piping System

07/27/2009 11:45 AM

CH4 tank----- 1 meter pipe

CO2 tank----- 1 meter pipe merging of the 2 pipes ------- 2 meters pipe ----- engine

Hope it's clear enough

Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#12
In reply to #10

Re: Maximum Flow in a Piping System

07/27/2009 11:10 AM

the engine is a 3.3 kW engine. Pressure regulators are used to place on the pressurized tanks of CO2 and CH4.

Does that make sense now?

Register to Reply
Commentator

Join Date: Jul 2009
Posts: 63
#4
In reply to #2

Re: Maximum Flow in a Piping System

07/27/2009 9:25 AM

I would first determine the acceptable velocity of the fluid down the pipework,in theory you could push what you want down it but may need some pretty good ear defenders to live with it.

Unfortunately my tables only go down to 3/8",but as a rule of thumb I would use 1.8 to 2 m/sec for wateR.

Register to Reply
3
Power-User

Join Date: Mar 2009
Location: United Kingdom
Posts: 308
Good Answers: 28
#17

Re: Maximum Flow in a Piping System

07/27/2009 5:14 PM

You could download this prog and estimate the pipes Cv ...then use this number as a basis for getting a possible flow.

http://www.airlinehyd.com/webpages/Information/Knowledge_Center/Pneumatics/Software/vlvsize.xls

Regards Woody

Register to Reply Good Answer (Score 3)
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#19
In reply to #17

Re: Maximum Flow in a Piping System

07/28/2009 1:13 AM

GA. Good to have. The OP should be happy with that, Ky.

__________________
The Twain Has Met
Register to Reply
Associate

Join Date: Jun 2009
Posts: 43
#21
In reply to #17

Re: Maximum Flow in a Piping System

07/28/2009 7:27 AM

Thanks your spreadsheet is really well done.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18

Re: Maximum Flow in a Piping System

07/28/2009 12:01 AM

Another useful link might be this:

http://www.engineeringtoolbox.com/darcy-weisbach-equation-d_646.html

On a quick glance, it appears that your desired flow through the given pipe size would be way supersonic, so it won't work. Also, Cv's differ for liquids (essentially incompressible) versus gases. To echo another question, why not use needle valves and flowmeters, rather than pressure regulators, so that you could make comparisons between different flow rates and mixtures?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2009
Posts: 43
#20
In reply to #18

Re: Maximum Flow in a Piping System

07/28/2009 7:26 AM

Thanks for your link. I tried it to get a flow of 30 L/min for methane (0.68 kg/m^3) and everything seemed to work fine.

As a result I think it's a really small amount of flow so I don't really understand why would it be supersonic?

I was just looking to get the flow rate of 30L/min and the pressure regulator can go to 50 psi, but I can adjust it to just a couple psi to get the flow I want. Then make precise adjustements with a needle valve.

Register to Reply
Power-User

Join Date: Mar 2009
Location: United Kingdom
Posts: 308
Good Answers: 28
#22
In reply to #20

Re: Maximum Flow in a Piping System

07/28/2009 8:44 AM

In low-pressure drop flow—when outlet pressure (p2) is greater than half of inlet pressure (p1)—outlet pressure restricts flow through the orifice: as outlet pressure decreases, flow increases, and so does the velocity of the gas leaving the orifice.

When outlet pressure decreases to half of inlet pressure, the gas leaves the orifice at the velocity of sound. The gas cannot exceed the velocity of sound and—therefore—this becomes the maximum flow rate. The maximum flow rate is also known as choked flow or critical flow.

It seems that your required flow rate will be well below this maximum.

Regards Woody

Register to Reply Score 1 for Good Answer
2
Anonymous Poster
#23

Re: Maximum Flow in a Piping System

07/28/2009 2:54 PM

That depends on a lot of factors. Mostly of the i.d. and equivilant length of line, which I am sure you realize, and the final answer is almost an iteration depending on whether or not your resultant flow rate pushes the boundary layer into a turbulant condition.

The equation is: dP = (2.15x 10-4 (fpLQ2)) / d5

dP - Pressure drop (psig per foot of length)

L - 1 foot

p - density (lbs/ft3)

f - friction factor

d - inches

Q - gpm

F is 64/Nr if Nr is less than 2000, or 0.316/Nr0.25 if over 2000

Nr = 3162(Q)/ud

u - viscosity of fluid in centistokes

Good luck!

Register to Reply Good Answer (Score 2)
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!