22.5 kw Motor Not Able to Start From a 60kva DG

08/26/2009 7:14 AM

i have a 30hp submersible borehole pump that works well from mains power but cannot work from 60kva DG i have tried to check on all possible reasons but i cant find the reason please assist on this

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/26/2009 8:03 AM

Does the DG trip out on overcurrent, then? If so, then one possible solution is to inroduce a soft-start unit in the motor starter. Another is to install a programmable variable speed drive unit and program it to run-up to speed more slowly than were the pump to go direct-on-line.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Anonymous Poster
#5
In reply to #1

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/27/2009 5:00 AM

Check Block loading character curve of you Generator first,You haven't mentioned what would be the base load on your generator when it comes on line ,check once again it looks like your generator is undersized.

crm

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #1

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/27/2009 7:24 AM

GA for a good answer in my book....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Apr 2009
Location: ras al khaima
Posts: 25
#2

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/26/2009 11:51 AM

Because starting current of your motor is more than your generator rated output current. In your case star delta starter will not work it out. as per mr.pwslack metioned select softstarter or VFD or autotransformer.

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/26/2009 12:57 PM

Your generator is under capacity to start the motor. In general, when a larger motor (compared to generator capacity) starts on generator, the generator capacity should be at least:

4 times of the motor capacity for DOL starting,

2-3 times of the motor capacity for Soft Starters starting and

1.4 times of the motor capacity for used with VFD

A Good article can be found here:

http://ecmweb.com/training/electrical_basics/electric_sizing_gensets_large/?smte=wr

This type of problem has been discussed recently in this forum. You can search and find more information from there.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
2
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/26/2009 11:34 PM

Dear Mr. Kirmani,

In addition to the advise by other CR4 MEMBERS, I would like to addthe following:

What about the delivery line valve. Normally a pump should be started with DELIVERY VALVE CLOSED and you have not mentioned about this. I presume valve is there. If not, install a valve in the delivery line and try.

When you want to start your pump on DG SET, close the delivery valve and start the pump. I am sure you will succed.

This suggestion may look cilly, I have come across a case where the pump was started directly without controlling the flow while starting. After installing a valve in the delivery line the pump was started with VALVE CLOSED and succeeded.

DHAYANANDHAN.S,

CR4 FORUM MEMBER

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Sep 2007
Location: Christchurch, New Zealand
Posts: 168
Good Answers: 18
#10
In reply to #4

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/27/2009 5:12 PM

I don't believe a submersible pump has a delivery line control valve, does it?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11
In reply to #10

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

11/15/2009 2:37 AM

Dear Maths,Physics, Maniac,

For submersible pumps valve may not be there, but the question here was related to the MOTOR HP and GENERATOR CAPACITY. The EXAMPLE WHAT I HAVE MENTIONED AND COME ACROSS is 30 H.P. Motor and 60 kVA Diesel Generator Set.

If the submersible pump is of 3 Hp or 5 HP, we do not need a valve in the delivery line when the DIESEL GENERATOR is of 60 kVA. If the motor is of 30 HP and DG Set is of 60 kVA, definitely valve is required in the delivery line, and close before starting, and this will help and solve this particular problem.

I hope the matter is clear to you now.

DHAYANANDHAN.S,

CR4 MEMBER, INDIA.

Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 18
#7

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/27/2009 7:45 AM

please let me know

if the dG is tripping ?

What typr of Starter you are using Star Delta type of DOL ?

If DG is tripping that means your stsrting load is very high. If DG is not tripping and motor is working but not delivering the water means there is no enough torque.

So check Frequency and Voltage of Generator it shoud be as given in name plate of 30 Hp motor.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/27/2009 10:47 AM

As usual the person who needs to (seemingly) fix/find the problem, has not a clue about:-

a) Electric motors and their starting currents/starters....

b) DG sets in general

c) How to supply the limited amount of data needed to allow an intelligent and helpful reply......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Sep 2007
Location: Christchurch, New Zealand
Posts: 168
Good Answers: 18
#9

Re: 22.5 kw Motor Not Able to Start From a 60kva DG

08/27/2009 5:07 PM

I work for a soft starter company called Aucom Electronics www.aucom.com

As many have indicated, your problem is because the 22.5kW pump can need 6 times or more current than it would normally need when running to start DOL or Direct on Line with a contactor. This is termed a starting current of 6 X FLC ( Full Load Current ). As current is directly related to power ( Power = Voltage X Current ), this means that a DOL start would need a minimum of 22.5 X 6 = 135 kW generator, which you haven't got.

If you can supply me the details of the pump I can determine for you if a soft starter will be able to start your pump with a starting current limit of about 2.5 X FLC. This will demand about 22.5 X 2.5 = 56.25 kW from your 60kVA generator which should be fine.

Good Luck.

Register to Reply Score 1 for Good Answer
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!