IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/30/2009 6:28 AM

Hello Sir,

We have purchased a new generator set as to be used in our small plant.Its a 200KVA, 3 phase and 440 Volts. We have series of motors in our plant the highest is 25 HP motor. We uses 220 volts for our domestic appliances and ligthings by putting one line to ground to create 220 volts.Is this set-up is it ok or we still need to have a step-down transformer for our plant? and why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2008
Location: nj,usa
Posts: 1253
Good Answers: 33
#1

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/30/2009 8:38 AM

When you say that you put one line to ground are you referring to one of the three phases of the 3 phase 440V generator output?

__________________
CARPE CRUSTULORUM!
Register to Reply
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/30/2009 4:10 PM

Is this set-up is it ok

No. Connecting a single phase supply to the earth is a big no-no, if you want to do this you use the neutral.

Even if you did connect your motor across one of the 440V three phase supplies to neutral (which is allowed depending on which country you are in, local regulations, site wiring, etc) you would get a single phase voltage of 254V ac ( 440V/(sqrt3) = 254V) not 220V, which is far too high for 220V single phase motors (and likely to not comply with your local electrical regulations regarding single phase supply voltage tolerance).

Use a proper step-down transformer and consult an electrician or electrical engineer for further advice.

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Member

Join Date: Jul 2009
Posts: 5
#3
In reply to #2

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/30/2009 11:26 PM

Hallow dear .

1-Some generators have options to get required voltage by changing power cables (consult a technically awared person who under stand the mater of winding)

2-Tro to control the voltage from AVR

Register to Reply
Associate

Join Date: May 2009
Location: INDIA
Posts: 25
#4

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/30/2009 11:33 PM

Dear Friend,

By connecting a phase for a single phase source will create the following problem.

1) It is not safe to connect directly to earth.

2) Connecting a single phase load in a single phase will create unbalance in the DG set.

Better to provide a step down transformer 440 V/ 215 V, it will avoid unbalance in the system.

Register to Reply
Member

Join Date: Jul 2009
Posts: 5
#5
In reply to #4

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/31/2009 1:08 AM

When you will see power connection commimg out from winding you can see jumpers at out side of generator (before out put breaker) if so an expert can change power connection from 400volt out put to 230 volt out put three phase (this set up is for 3 phase arrangement not for single phase.

if power connection set up is not arranged by company(manufacturer of generator) than you have to go to arrange a transformer.

Register to Reply
Anonymous Poster
#6
In reply to #5

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/31/2009 1:55 AM

All confusing..

Dear, Why are you worrying about all this. Dont You have an electrician who can understand all this logic. I am unable to undersand the logic behind the idea of using ground. First of all ground the neutral of ur genset. Then run your load up to ur genset capacity without any worry.3phase motors will use all three phase and single phase 200V can be obtained from any phase and neutral. You will only need to care of equally distributing the load.No need of transformer if you genset is not kept far away from ur utilities or in other words, u dont have much voltage drop.440 volts are rarely set as genset out put. they are actuaaly kept up415V and u can also control ur voltage up to +-10% with the help of voltage adjustment pot....

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#7

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

08/31/2009 2:08 AM

It can't be.

Getting the power from one out of the three-phases at 440v 3-phase system will give you 440 divide by 1.732 = 254Vac. The voltage difference is 254-220=34volts which is high enough to burn your motor windings if plugged in longer time.

Some manufacturers in compliance with NEC the voltage supply for motor shall be plus or minus 2.5%-3% of the nameplate rating, thus 220x0.025= 4.4volts

At +2.5%; 220V+4.4V = 224.4V @-2.5%; 220-4.4V = 215.16V, though this scenario will affect the ambient motor temp but will little bit hurt your motor windings compared to 234V applied.

Hence, other option is to use the auto-transformer at least 25kva capacity to carry your 25hp, thus 25hp divided by 1.34kw/hp = 18.65 kw x 1.25 = 23.3 or say next higher rating is 25kva.

Your auto transformer will be 25kva @440/380/220 volts 3-phase

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Active Contributor

Join Date: Aug 2009
Location: India
Posts: 12
#8

Re: IS STEP DOWN TRANSFORMER REALLY REQUIRED ON OUR SET-UP

09/02/2009 4:13 AM

Please mention the type of winding of your generator. (star or delta). Also, if neutral is not available, a transformer is compulsory. If neutral is available , it is to be used for single phase loads, but not the ground wire.

__________________
Mind is like a parachute, no use if you do not open it
Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

anbarasu.pr (1); Anonymous Poster (1); hentoyk (1); imandi007 (1); jack of all trades (1); not so smart (1); Shakar99 (2)