Anonymous Poster

Electrical Load Calculations

09/08/2009 11:12 AM

can anybody tell me about electrical load calculation and what are the parameter required, and any freely available software.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: elecrical load calculation based on network

09/08/2009 11:22 AM

elecrical load calculation based on network ? What does that mean? What type of load? Utility, commercial, residentail, industrial?

Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#10
In reply to #1

Re: elecrical load calculation based on network

07/12/2010 11:36 AM

Wareagle, most of my applications are onsight power, mostly shipboard. However, I think that a Load Flow Analysis such as sold as a seperate module from SKM, ETAP, etc. would probably be better suited for Plants, High Rises, etc. but I'm not an expert on those applications as my 45 years in the marine industry never required it.

I think I see where you guys are headed but NEC has guide lines as ya'll well know for Load Analysis's and has gone as far as watts per square foot by some engineers as a guesstimate.

__________________
Thank you for your help - By far the best info site!
Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#2

Re: Electrical Load Calculations

09/08/2009 7:28 PM

Electrical load calculations are based on "duty factors", i.e., What percentage of the load (individually), represented in kilowatts, operate in a 24 hour period. I've attempted to find software as I perform these calculations frequently in order to determin the size of generators or transformers. Couldn't find any! The idea behind it is not to oversize your power supply weither it be a generator/s or transformer/s. Here is an example: Suppose you have a refrigerator, it's rated at say, 1 hp which equals 746 watts. It runs about half of the day. Then your duty factor would be 0.5 times 746 watts. Calculating all connected loads and assigning duty factors to them will determine your power requirements. Then add about 1.15% as a cusion.

__________________
Thank you for your help - By far the best info site!
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Electrical Load Calculations

09/08/2009 7:59 PM

Jraubsr Quote "Suppose you have a refrigerator, it's rated at say, 1 hp which equals 746 watts. It runs about half of the day. Then your duty factor would be 0.5 times 746 watts.

Suppose everything only runs half of the day, but it all comes on at 8:00 AM. Then what happens?

Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#8
In reply to #3

Re: Electrical Load Calculations

07/12/2010 10:39 AM

Demand factors are based on years of recording eqpt. for specific applications. Common sense plays and important role as well. For example, using the refrigerator analogie, could be if the refrigerator was sitting outside in the summer time it would certainly run more than it would if it were in a controlled enviourment. A crane or gantry could operated only while unloading ships. If the dock worked 24 hours a day doesn't mean that the eqpt. is operating at full capacity. Subsequently you must have knowlege of your application. Basically it's a guestimate! Here is one formula used under NAVIC 2-89 Shipboard regulations.

LOAD FACTOR=OPERATING KW/RATED KW X NO. HRS OPERATION/24 HOURS or you can substitue Rated KW with Rated bhp.

__________________
Thank you for your help - By far the best info site!
Reply
Associate

Join Date: Aug 2009
Location: India
Posts: 25
#4

Re: Electrical Load Calculations

09/09/2009 4:53 AM

Hello,

For the purpose of load calculation in a particular system, you need to know the following factors :

Demand factor is the ratio of the sum of the maximum demand of a system (or part of a system) to the total connected load on the system (or part of the system) under consideration. Demand factor is always less than one.

Diversity factor is the ratio of the sum of the individual maximum demands of the various subdivisions of a system (or part of a system) to the maximum demand of the whole system (or part of the system) under consideration. Diversity is usually more than one.

As an example :

Suppose a main feeder from substation switchgear that is supplying five feeders with connected loads of 400, 350, 300, 250 and 200 kVA with demand factors of 75, 80, 85, 90 and 95 percent respectively. What shall be Transformer rating feeding the switchgear if the diversity factor is 1.5?

Solution

Calculate demand for each feeder:

- 400 kVA × 75% = 300 kVA

- 350 kVA × 80% = 2805 kVA

- 300 kVA × 85% = 255 kVA

- 250 kVA × 90% = 225 kVA

- 200 kVA × 95% = 100 kVA

The sum of the individual demands is equal to 1250 kVA

Using the diversity factor of 1.5, the required Transformer rating shall be 1250/1.5

= 833 kVA. Considering safety factor of 20% the transformer rating shall be 1000 kVA

Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#5
In reply to #4

Re: Electrical Load Calculations

09/09/2009 7:48 AM

The base is

100% of Continuous Load + 50% Intermittent Load + 0% Standby Load

__________________
BNDas
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: Electrical Load Calculations

07/12/2010 9:39 AM

The calculation will be easy if the load is lighting and small office appliance only.If central air conditioning is used you should consult its supplier.If large motors are used you should consider the sequence of starting ,starting kVA etc.If a pf correcting capacitor bank is used ,for generator sizing you should omit it.If the installation is already energised the kVA reading of the utility company would guide you but as it indicates kVA in a 15min window starting current of large motors will influence the rating of the generator

__________________
pnaban
Reply
Participant

Join Date: Feb 2009
Posts: 2
#6
In reply to #4

Re: Electrical Load Calculations

10/09/2009 6:31 AM

KKK,

Can I use this method to determine Generator rating? And is it okay to use diversity factor & demand factor per small load (such as lighting point,socket,cooker unit,A/C unit,etc) when calculating ? How can I get latest diversity & load factor Table?

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #6

Re: Electrical Load Calculations

07/12/2010 11:11 AM

The diversity factor,load factor etc should be applied by experience only, depending generally on the type of occupancy(home,office,super market,industry,roads etc) and sequence of operation of equipment in a particular situation.Some diversity factors are given in BS 7671 to send you I do not have a soft copy. Do you watch " myth busters"?

__________________
pnaban
Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#11
In reply to #6

Re: Electrical Load Calculations

07/12/2010 11:40 AM

KKK, thats exactly what I use it for. I have typical tables as mandated by regulatry bodies involved with the marine industry. Many times my job is to size generators and transformers. Again, the application is everything when it comes to heavy eqpt. But general usage as you've referred to are pretty standard unless your kitchen is open 24 hours/day.

__________________
Thank you for your help - By far the best info site!
Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aboo (1); biswanath.das (1); jraubsr (4); KKK (1); pnaban (2); wareagle (2)