Knee Point Voltage and Current Transformers

09/23/2009 10:22 AM

dear friend,

kindly any one explaine me what is the effect of knee point voltage in CT.

If one PX Class CT having Vk>300V, Ia<30 mA how i calculate this CT BURDEN also what is the primary current when th ct is satsurated,

thanking you,

yours ,

B.JEYACHANDRAN

Register to Reply
Pathfinder Tags: ct
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Sep 2009
Location: ABB Limited, Nashik
Posts: 9
#1

Re: Knee Point Voltage and Current Transformers

09/26/2009 2:26 AM

Dear friend,

Knee Point voltage is nothing but a point at which the CT saturates. Thatsy its always better to design the CTs which can operate without saturation even at a voltage appears in the CT during fault condition. Pls find below the following formula for calculating the Knee point voltage.

Vk=2If(Rct+2Rl).

where, If is the current refected to the CT secondary during fault condition,

Rct is the resistance of the CT which can be adopted by means of a thumb rule considering the CT ratio,

Rl is the lead resistance i.e. sum of the resistance of the wire connected between the relay & CT and Impedance offered by the internal circuitary of the relay

For PS class CT's designed considering the above,burden is not applicable.

Pls revert back if you have any further queries.

Regards,

Manimaran.V

Register to Reply
Associate

Join Date: Apr 2009
Location: Muscat Oman
Posts: 27
#2
In reply to #1

Re: Knee Point Voltage and Current Transformers

09/26/2009 2:42 AM

dear friend,

thank you for your guidence, how i calculate the fault current limit in primary side with knee point voltage

Register to Reply
Member

Join Date: Sep 2009
Location: ABB Limited, Nashik
Posts: 9
#3
In reply to #2

Re: Knee Point Voltage and Current Transformers

09/26/2009 7:44 AM

Dear Friend,

Pls find below the formula for calculating the fault current,

Fault current(in KA) = Rated Curent/(% Impedance*1000)

% Impedence shall be calculated for the system from the point of source to the point of occurence of the fault.

Regards,

Manimaran.V

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#4
In reply to #3

Re: Knee Point Voltage and Current Transformers

09/28/2009 4:12 AM

Dear Manimaran,

Can you please explain, how to calculate Ia and what is its significance?

Register to Reply
Anonymous Poster
#5
In reply to #3

Re: Knee Point Voltage and Current Transformers

09/28/2009 11:19 AM

dear friend,

thankyou friend

Register to Reply
Anonymous Poster #1
#12
In reply to #1

Re: Knee Point Voltage and Current Transformers

05/29/2012 1:48 AM

Dear Sir,

Please send one example calculation for knee point voltage.

Regards,

Push

Register to Reply Off Topic (Score 5)
Member

Join Date: Apr 2008
Location: Doha Qatar
Posts: 8
#6

Re: Knee Point Voltage and Current Transformers

09/30/2009 12:38 PM

Dear member

For PX class CTs , the burden is not normally mentioned . There the CT is defiened based on the CT kneepoint voltage , magnetising current etc . The burden is mentioned in class P CTs

In PX class CTs the kneepoint voltage is normally based on the max fault current and a diamensioning factor based on system X/R ratio

Ayub

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#7
In reply to #6

Re: Knee Point Voltage and Current Transformers

09/30/2009 9:06 PM

Understand from above formula to calculate knee point voltage. Can you please explain how to calculate magnetising current.

Register to Reply
Member

Join Date: Apr 2008
Location: Doha Qatar
Posts: 8
#8
In reply to #7

Re: Knee Point Voltage and Current Transformers

10/01/2009 12:24 AM

There is no formulae as such for calculating the magnetising current . However some a application demands minimum value of mag current for relay setting ( eg; REF protection ). Iin any case a magnetising current of less than 30 mA would be sufficient for most of the application

Register to Reply
Member

Join Date: Sep 2009
Location: ABB Limited, Nashik
Posts: 9
#9
In reply to #8

Re: Knee Point Voltage and Current Transformers

10/01/2009 3:31 AM

ya.. thats right.. there is no formula for calculating magnetising current. however, lesser the magnetising current, better is your CT performance.

Regards,

Manimaran.V

Register to Reply
Participant

Join Date: May 2012
Posts: 2
#11
In reply to #9

Re: Knee Point Voltage and Current Transformers

05/07/2012 7:57 AM

The formula for calulating the required magnetising current for the CT =

[(IOP / CT Ratio) - IR] / n

Where,

IOP = Relay operating current (absolute current value in terms of CT primary)

IR = Relay setting current (in terms of CT secondary)

n = Number of parallel CTs forming (87) protected zone

Register to Reply
Anonymous Poster
#10

Re: Knee Point Voltage and Current Transformers

06/20/2010 6:35 AM

Dear Sir,

so for PS class CTs how max we can burden it . please revert with answer.

Register to Reply Off Topic (Score 5)
Participant

Join Date: May 2012
Posts: 2
#13
In reply to #10

Re: Knee Point Voltage and Current Transformers

05/29/2012 2:01 AM

Please note that the Knee point voltage of the ct is arrived only after knowing the Burden which is connected to the CT + the fault current + X/R at fault point etc

Register to Reply Off Topic (Score 5)