Rectification for Wrong Tapping Point for Liquid Service D/P Flow Transmitter

10/02/2009 7:47 AM

Dear All,

With reference to the picture below, The flow transmitter tapping points are on a condensate line (meaning liquid service), the line is quite near to the floor and at this moment it is not possible to get a new tapping point on the line at 0 degree or 45/60 degree below instead of the current wrong angle.

Is there an intelligent solution to this dilemma where i cannot change the tapping point and still get an accurate flow reading because with this incorrect impulse installation the only way i can get a correct flow reading is when the line is full filled.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#1

Re: Rectification for Wrong Tapping Point for Liquid Service D/P Flow Transmitter

10/02/2009 4:28 PM

If the line is not filled, I doubt you will get any kind of accurate reading no matter where you tap it.

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Associate

Join Date: Oct 2007
Posts: 29
Good Answers: 1
#2

Re: Rectification for Wrong Tapping Point for Liquid Service D/P Flow Transmitter

10/03/2009 12:04 AM

You may crack-open vent plugs on transmitter's HP & LP side and make sure all the trapped air is vented and impulse lines are completely filled with condensate, then close the plugs. This may last till your line is empty again.

Again, this will not be correct solution as at later stage trapped gas or air bubbles may be present in condensate again.

Best solution to get rid off this problem will be to SHIFT the orifice to some another elevated location and place the Transmitter below it.

Regards

__________________
Best Regards, srzambre.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Rectification for Wrong Tapping Point for Liquid Service D/P Flow Transmitter

10/03/2009 5:54 PM

The photo shows the DP element with two sensing tubes off the top, which might allow for stray air to collect. But what would prevent rotating this element so that the sensing tubes were in the below-minus-45-degree quadrant, as others have described? This would help to ensure liquid in the sensing tubes, and if not completely at the bottom would also help to avoid sediment in them.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#4

Re: Rectification for Wrong Tapping Point for Liquid Service D/P Flow Transmitter

10/06/2009 3:18 PM

well your photo seems insufficent to clarify

If possible can you provide direction of flow? further Is the pipeline gets elevated above the transmitter on downstream of Orifice ? what is the line pressure ? Is the condensate clean ? what is the type of Orifice plate connected ? Is it a continious condensate flow?.what is the required accuracy and criticality of this flowmeter?

45/60 degree tapping angle are required if the tappings are at different plane here I feel nothing to do with tapping angle, as they on same plane . This type of Orifice flanges have two points to take out the impulse tapping the other unused tapp may be plugged may be on down side , you take a short shutdown and fixed two isolation valves at the flange bottom taps and connect the instruments .

Register to Reply
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#5
In reply to #4

Re: Rectification for Wrong Tapping Point for Liquid Service D/P Flow Transmitter

08/08/2010 4:22 PM

Usman,

If it possible move the transmitter down in the same support, but in a position below of the pipe or below the taps, then makes a new impulse lines downward to the transmitter, I mean both tubings with slope to the FT not for the pipe, the idea is get full filled the tubing with water in order to prevent the in bubbles or air.

Maybe this little modification can improve the measurement of the flow and minimize the tapping points effects.

Regards

JP

__________________
Instruments-guy-SAV