RTD Cable Shield Connection

10/14/2009 10:28 PM

We are using 8 triad cable for the connection between the Multilin 469 relay and Motor winding RTD. There is the terminal of shield connection to the relay side but no terminal available in the motor side. Do we need to leave the shield unconnected in the motor side? The Cable length is almost 600 feet.

Please help.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: RTD Cable shield connetion

10/14/2009 10:51 PM

Yes, you must ONLY connect the shield at one end.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#2
In reply to #1

Re: RTD Cable shield connetion

10/17/2009 9:40 AM

A ground loop condition occurs when two or more electrical paths exist in a ground line.If the shield connects to both chassis grounds, this will be creating current path to flow from one ground to another since both grounds have different potentials.

The current flowing through the shield could be as high as severalamperes, which would induce significant magnetic fields in the signal transmission. This could create interference that would result in a possible misreading of the analog signal.

To avoid this problem, the shield should be connected to ground on only one side of the chassis, preferably the controller side.