I have some doubts on threading of the galvanized pipes.
It is a normal practice to accept threading of a pipe after it is galvanized and it is not felt that the corrosion inhibiting factor imbibed by galvanizing is not affected by threading. Please clarify my few questions:
a. How deep does galvanizing go into a metal so that threading does not affect the corrosion performance of galvanizing?
b. NPT pipe threads seem to remove more metal than BSP Parallel threads. Am I right? If so, is the corrosion resistance compromised in NPT threads?
c. Is welding of a galvanized pipe acceptable? I have seen in some cases that the threads start to leak and the ultimately site-devised strategy is to weld the fittings. If acceptable, how should the welding be done?
d. Does deep grooving affect the corrosion resistance of galvanized pipes?
e. Manufacturers do not seem to make the pre-galvanized sheets to more than 340 grams / sq. m of coating both sides put together, while in hot-dip-galvanizing even 380 grams / sq.m single side is accepted as possible by the galvanizing personnel. What are the reasons?
f. Please suggest good literature on galvanizing?
Sorry lot of questions but all are related to galvanizing.
Thanks
K. Muthukrishnan
Pathfinder Tags: Galvanizing
Re: GM
10/29/2009 4:23 AM
<...Is welding of a galvanized pipe acceptable?...>
No. The welding fumes will be loaded with Zinc, which will affect the health of the operator carrying out the welding.
Assuming the pipe material underneath the galvanising is steel, what is in the pipe, its temperature and pressure?
Re: GM
03/05/2021 2:31 AM
Mechanical Engineers often don't consider this question. Yet it is fundamental to the selection of the piping materials.
Good Answers: 58
Re: Threading and Galvanized Pipes
10/29/2009 4:18 PM
1. You have to thread after galvanizing, because galvanizing after would interfere with proper sealing of the threads. Threading cuts off the metal and galvanizing at that spot, it's unavoidable. It's usually the inside of the pipe that the galvanizing is protecting.
2.Galvanizing is bonding at the molecular level; like chrome plating it is done electrically, or hot dip plating. Hot dip is a lot like soldering, requires cleaning and other dips to prepare the metal for bonding.
3.I don't quite understand how anybody expects straight threads to hold pressure, not familiar with BSP. Maybe the last thread bottoms, and the seal is there. In NPT, the thread is tapered, on both the male and female, for pressure pipe. When the tapers take up on each other, the threads literally crush into each other. On brass fittings I was told thread sealant wasn't even necessary, because of the crush. Of course, taking a part loose and re-tightening would have some affect, I'm sure.
4.Like the other poster said, welding zinc releases poisonous gasses. If you have to weld it, I use 6011 rod and a big fan to blow away the smoke. Paint the weld with a good rust preventer.
5.As far as the sheets, electroplating is fairly controllable, hot dip is done with molten metal, can get quite lumpy sometimes. Triple hot dipped bolts and the like are galvanized after threading, but the threads are cut very loose to accommodate for the buildup of the zinc. If you look in the nuts, you may see the galvanize cut away by a tap, to make sure they fit.
6.Wikipedia is a great source for data.
mike k
Good Answers: 153
03/05/2021 5:21 AM
Point 3 Parallel threads are not designed to hold pressure. They are used in conjunction with a washer that is compressed between the pipe or pipe fitting and a machined seating face on whatever the pipe is screwed into. On hydraulic systems, which usually are at higher pressures, this washer is often made as metal annulus with a concentric rubber, nitrile or teflon sealing material annulus bonded to the inside edge. The joint is seated tight onto the faces of the outer metal ring but the seal is made by the inner one. The outer ring also prevents high pressures from extruding the soft seal material out of the joint. Tapered threads are problematic if they have to be remade several times so in situations where this is likely to happen ie. hoses that have a shorter service life than the equipment they are attached to, parallel threads are used instead. It is good practice to replace the sealing washer every time a parallel joint is remade.
Good Answers: 68
10/30/2009 12:12 AM
Hello K.Muthu,
Can I suggest you do actually get a book for on-site work, as all these questions are relatively unconnected one with the next.
The cutting of the thread depending on what grade you are working to ASME, BS etc, each has a slightly different thread and thread depth, but, whatever the thread it will alway cut through the relatively 'surface layer only' of galvanising.
From my experience the pipe is usually threaded on the outer surface. But whatever the galvanising, when you cut a pipe to length you are left with bare black pipe. Check out the sites below and you may see a tape which can be applied to a joint after making. But note: The area of about an inch (~25 mm) from the end of the thread must be clean. So only ever clamp the pipe to cut and to thread it about 4 inches (~100 mm) from the end.
The type of thread I think you will find depends on the size, and the intended use of the pipe. What it carries and the type of 'atmosphere' the outer surface with be likely to have to live with.
You can read about galvanising on-line or get a book on it but, make sure you are judging like with like. Industrial galvanising and joint-making may be entirely different and a lot more 'substantial' than 'domestic' pipe.
Why are you so worried about this. Are you using an acid in the pipe, or is it for air, or water, or something else?
If you refer to a straight Galvanised coupling as below, the externally threaded pipe will be screwed into the internally threaded coupling, from both ways. So at that point the pipe after it is connected will have at least twice the thickness of the rest of the pipe at this joint.
Galvanized Pipe Fitting - Galvanized Coupling [2007-11-21]
Items Name: Pipe/tube fittings, like elbows(45&90), tees, corsses, nipples, sleeves, couplings, unions, bushings, plugs, caps, flanges, hex lock ...
Steelinking Galvanized Pipes Industry Ltd-Fitting Dept. [Province:Guangdong, China]
  1. Pipe: Information from Answers.comMany industrial and government standards exist for the production of pipe and ..... The most common process pipe joint is the butt weld. The ends of pipe to be ... The most common pipe thread in North America is the National Pipe Thread .... Can Black steel pipe be replaced with Galvanized piping for gas piping? ...
    www.answers.com/topic/pipe-material
  2. galvanized pipe products, galvanized pipe manufacturers ...galvanized pipe supplier catalog - himfr.com provides what you want, ... We produce lead forged particular for automotive industrial, electric, ... Ball features a recessed rope attachment for protection from injury. ... Acid Regenerat... category: [Metallic Processing Machinery] (pipe accessory pipe joint ) ...
    www.himfr.com/buy-galvanized_pipe/busitype_importer.html
Galvanized Steel Pipe On GlobalSpec15 May 2009 ... Find galvanized steel pipe related suppliers, manufacturers, ... Industrial pipe is a broad category of fluid and solid transport hardware ... Common thread types include national pipe thread (NPT) and British standard pipe (BSP). .... stocking difficulties associated with ground joint pipe unions. ...
flow-control.globalspec.com/Industrial.../galvanized_steel_pipe
Has details of pipes, pipe joints, and welding of Galvanised pipe.
  1. Steel Pipes - Large Stockwww.cleveland-steel.com Tubes for structural & construction Over 40,000 tonnes in Stock UK
Search Results
      Results include your SearchWiki notes for
galvanized pipes and joint protection
      . Share these notes
      Copy and paste this link into an
email
      or
IM
  1. galvanized pipe Manufacturers - Verified galvanized pipe ...galvanized pipe Manufacturers directory - World's Largest Manufacturers Trade Platform with ... Security & Protection, Service Equipment, Shoes & Accessories .... part,steel elbow,composite pipe,construction pipe,union joint,pipe joint ...
    www.alibaba.com/.../galvanized%2Bpipe-manufacturers.html
  2. ERW hot dip Galvanized pipes tubes India,Galvanized pipes tubes ...SPEL India - Galvanized pipes tubes in India by ERW hot dip galvanized steel pipes tubes ... Zinc's natural corrosion resistance provides long-term protection, ... after applying a small amount of pipe joint compound on the threads. ...
    www.sparkelectrodes.com/erw-hot-dip-galvanized-steel-pipe.htm
Check out the various links below. The Manufacturing Process link is interesting.
I hope you will view all these sites and details and perhaps keep a written Document about this for future use?
Take care and I hope you find what you are looking for in my advice, good luck.
08/05/2020 1:16 AM
Thanks For the information on Galvanized Pipes.
Tushar Mankar
10/30/2009 1:30 AM
K;
I hope this helps some.
BST is also a tapered thread I believe the same 1/16th inch taper per inch of thread as NPT however it has a 55 degree included angle and different root and peek profiles. Both threads are available tapered or parallel (BSP / NPP) and both are about the same depth in either case. The 5 degrees difference is trivial if you consider the allowed variabilities in pipe diameter, thickness (respective of pipe schedule), and roundness (or should that be out of roundness?). Parallel threads are typically used for electrical or mechanical joints where you may wish to use more thread length. Tapered threads are used for fluid transfer as they compress some what during assembly and provide a more leak resistant joint. Straight threads should never be used with any gas applications (natural / propane) and typically are not advisable for the transfer of other fluids.
Welding of any pipe after it is threaded into a fitting as a means to prevent or stop leaks is a taboo. During the thread cutting process oils are used and typically during the thread connecting process some type of sealant is used. Thereby imparting impurities into the weld zone and creating an inferior weld. Rust and corrosion will do the same thing. Also even if everything were sufficiently clean you still have a compromised weld area due to the threads themselves. (Never weld on threads)
Typically welding is done with weld fittings. (look up "Weldbend" they are a major manufacturer of weld pipe fittings.) with either a butt weld, socket weld or slip joint. Threaded fittings are not suitable for welding.
Welding threads on galvanized pipe is a triple taboo. You have the above issues plus, zinc has a melting point of around 900 degrees Fahrenheit. When welded on, the zinc oxidizes (zinc oxide) and becomes poisonous in certain concentrations (trust me I have experience with this. and no it was not a mistake of my own). This is also self defeating as when you burn through the exterior coating to perform the weld you also burn off the internal coating behind the weld zone and compromise your corrosion resistance internally where it is needed the most.
The proper way of dealing with leaky galvanized joints unfortunately usually involves some disassembly followed by reassembly with fittings that are not corroded or simply making sure that during reassembly you use the proper amount, and type of sealant as well as tightening it sufficiently.
The galvanizing does not truly "penetrate" the surface of the pipe save for surface imperfections. The steel beneath has a melting point of around 2600 deg. Much higher than the zinc and therefor the two are in bond and not fused together. This means that deep gouges can also compromise corrosion resistance.
As far as the thickness of the zinc coating goes I do not believe I can be of assistance as what I learned about it some 30 years ago may no longer be applicable.
Hobbies - DIY Welding - pipewelder
10/30/2009 2:11 PM
A galvanizing does not penetrate very much if any into the pipe and it is acceptable to thread galvanized pipe, And I have done this many manuy times in the past. i am not sure but all the galvanized pipe I have used the was threaded after it was galvanized. Threading it will remove some of the coating and it must be reapplied after the joint is made up. it does not affect the galvanizing on the interior of the pipe though and this is the normal reason most people use it. If the pipe was galvanized after it was threaded the additional thickness added with the coating would make it impossible to use standard fittings. I am not sure if they make a type of pipe and fittings with over sized threads in order to be able to galvanize the pipe after it is threaded live galvanized bolts but I have never seen it.
B. I am not sure about BSP threads but NPT threads are tapered and more metal will be removed from the end that the threads are started from.
C. Yes it is but to make a sound weld you must grind the galvanizing back in order to not contaminate the weld metal. I have welded galvanized piping to ASME B31-3 codes with x-ray quality welds many times but I 'd rather sand paper a wildcats tail than weld galvanized pipe after I got galvanize poisoning a few years back from welding on it. If you are thinking about welding on anything galvanized please look into the safety factors and PPE required to keep your welders from breathing the fumes.
D.If you go groove it through to the base metal it will rust. Galvanizing is a coating.
E. I am not sure of this but I would assume it is because of the costs and the fact that making the coating any thicker may not help with the corrosion resistance properties or it could be that it hinders the bond to the metal from being so thick. I would bet you could get the coating any thickness you want if you offered to pay extra for it.
F. Please start here for this request I think they may have some free pamphlets and such. http://www.galvanizeit.org/
One thing I found out years ago that I thought was interesting is that on hot dipped galvanized angle iron it is not possible to just cut out a angle section on one leg and bend it to make pipe supports or knee braces. Even if you grind all the galvanizing back to bare metal in the area it will still crack or break when you heat it up and bend it. I have never figured out why this happens and I have always heard that hot dip galvanizing does not effect the metal properties. I have bent hundreds of pieces of non coated metal shapes to make supports from without them breaking but never bent a galvanized piece that did not a least crack badly and some actually broke into. I also know that hot dip galvanizing heat treated studs will lessen thier strength because the heat from the galvanizing process will anneal the studs and they will no longer stand up to the specification.
pipewelder
06/19/2017 5:20 AM
Very Nice Information about Galvanized Pipes..thanks
Rajveer Asha Aurum Ganpat
11/08/2018 12:46 AM
Galvanized pipes are steel pipes that have been dipped in a protective zinc coating to prevent corrosion and rust. hence, Galvanizing protects the underlying iron or steel.
Thank You For This Information, Will be waiting for more updates. - SA 179, SA 214
02/12/2019 6:07 AM
Galvanized steel can be welded; however, one must exercise caution around the resulting toxic zinc fumes. Galvanized steel is suitable for high-temperature applications of up to 392 °F (200 °C). The use of galvanized steel at temperatures above this will result in peeling of the zinc at the inter metallic layer. Electrogalvanized sheet steel is often used in automotive manufacturing to enhance the corrosion performance of exterior body panels; this is, however, a completely different process which tends to achieve lower coating thicknesses of zinc. Galvanised Steel - Jain
Good Answers: 137
08/10/2020 10:42 AM
When we bought galvanised nuts and bolts we specified that the nuts must be free-running after galvanising. If standard kit were galvanised the nuts would be stiff all the way, a pain for the fitters. I don't know offhand whether the supplier modified them or whether he bought specials with greater clearance.
Maybe a similar approach would work with pipes and fittings.
Location: Level 19, Creative Tower, P.O.Box 4422, Fujairah, UAE
03/04/2021 7:58 AM
Very nice post. I absolutely appreciate this site. Continue the good work!
Tycoon Piping Solution
03/05/2021 12:07 AM
While threading, zinc coated on the mild steel pipe, does scrape off .
I have seen a bit of corrosion near the threading .
Even if galvanising is done after threading, when the socket or valve is being fitted. Some scrapping does occur .
03/05/2021 6:14 AM
Galvanising is only a surface corrosion inhibiting coating, like paint or epoxy.
b. NPT and NPS threads have a 60 degree thread angle. NPT = National Pipe Taper.
NPS = National Pipe Straight. In BSP we have BSPP parallel thread, BSPT taper thread.
You can not mix BSP and NP threaded fittings not only do they have a different thread profile but mostly have different number of threads per inch for each size.
Refer to the following link for threads; https://www.valvesonline.com.au/references/threads/
From these tables it is possible to see the differences.
Before galvanising the metal needs to be degreased and then pickled in an acid to remove scale and oils.
Hot dip galvanising involves dipping the material into molten Zinc and the cost to coat the material is worked out on the weight of the object and the number of dips given.
Electro galvanising is plating of zinc onto the material which imparts a thinner coating which erodes away sooner on exposure to contaminents. I call theis the CNN coating , cheap n nasty. I have been told that it is possible to suffer hydrogen embrittlement to the base material like happens with the other forms of plating. Ever had a spring chrome plated for looks and then have it snap?
To weld on a galvanised surface the zinc has to be ground or sanded away to the parent metal and forced air ventilation or pressurised air helmet used by the welder and the fumes collected in a metal fume extractor.
Welding threads on coupling depends on the material of the coupling, malleable or cast iron fitting will often suffer from weld failure unless special rods and heat treatment are used for the pipe is usually mild or black steel and unless the fitting is of the same material then welding is problematical unless welding rods for welding dissimilar metals or weldall rods are used and only for low pressures.
If high pressures are involved then special weld coupling are used as in steam lines. Demin water lines erode the inside galvanising and require special alloys for that purpose.
Hare today, goon tomorrow!
03/05/2021 7:07 AM
I have worked in the piping industry for 40 years and this is what I learned.
It all comes down to application and system design. For normal water systems that are not acidic not a problem. You have to make sure the piping is properly protected for galvanic corrosion. Also for buried pipe if the soil is acidic then the threaded area should be wrapped with protective tape. It can not be used for aggressive water such as RO water or DI water.
The galvanizing is not deep enough to protect where the thread are made. In fact you would not want to cut threads out of the galvanizing metal. It does not have much strength.
Welding of galvanized pipe is possible but it require the removal the galvanizing to have clean metal for welding. Also if the welder welds through the galvanizing the fumes are very hazardous and will make him / her very sick. Long term exposure will cause chronic heath damage.
If you see threads start to leak look for the following:
  1. The pH of the water, look for corrosive environment,
  2. Causes of galvanic corrosion,
  3. Power lines running near by that can cause transient currents in the piping,
  4. Biological build up in the pipe (bacteria will create acid and cause pitting.
03/05/2021 9:11 AM
Factory threaded rigid conduit will have straight threads.
This ensures there is no gap in the coupling to damage wiring.
Field threading of conduit allows the use of tapered threads,but care must be taken to properly ream the inside of the conduit,and the threads must be cut to full length to ensure meeting of the conduits squarely and flush within the coupling.
The factory conduit threads are not tapered.
The conduit threads are not meant to be water tight,the conduit is meant mainly for physical protection only,however most field threaded conduits are tapered,unless expressly forbidden by contract.
If conduit is to be buried,it is recommended that it be configured to be rain-tight,using tapered threads and sealants.
The AHJ may also require other measures for underground Rigid conduit,such as a protective coating.
Never weld galvanized except as a last resort,and as others have mentioned,use the proper PPE and ventilation.
03/08/2021 10:10 AM
if you took a paint brush and put house paint on a pipe, its the same thickness.
to be more exact.. 75-100um thickness.
welding of course burns the coating away.. and don't breath the fumes.
cutting threads leaves zero trace of galvanized coating.
using pipe dope will protect your metal.
if you are in a very corrosive environment, maybe you need a different pipe, such as stainless?
and.. do not use galvanized pipe for your compressed air lines, the moisture will spall the coating over time and clog your air tools.
09/13/2022 8:58 AM
You are correct about the use of galvanized pipe on pneumatic supply lines.Pneumatic instrumentation controls have very small orifices which can be clogged with spalling from the galvanized coating.
When galvanized conduit is buried,it must be coated with a corrosion inhibiting layer, including the external threads on couplings,such as bitumen(in the old days,but it was very effective,surviving over 50 years in acidic soils).
I am sure there may be more effective high tech coatings available now.
09/13/2022 2:58 AM