We are manufacturers of LV,MV and automation panels. We have a 4000A 440V AC,50Hz switchboard
with 200(mm) x10(mm) x 2 runs busbar system and the busbars have to with stand 50 kA short circuit level. the ambient temperature is 40 degree celcius and IP is IP 54. Please guide me how do i calculate the temperature rise in the enclosure and what is the derating factor to be considered
for the busbars. It would be great help if you could give me the calculation chart.
Thank you. have a nice day.
Re: Calculation of busbar size for temperature rise in 440 V LV Panels
12/21/2009 1:58 PM
I am a little disturbed that you make switchboards and yet don't know how to do this or at least know what standards you should be looking at to find the required answers?
There is no single calculation chart but there are standards and lots of technical information and guides on the internet and on CR4 to help guide you (busbar sizing is a very common question).
12/24/2009 4:09 AM
ok
thanks
12/29/2009 8:21 AM
Quite. The standards ought to be readily available within the original poster's operation.
Good Answers: 19
Re: Calculating Busbar Size for Temperature Rise in 440V LV Panels
12/22/2009 9:05 AM
There have been several posts over the years on busbar sizing. On the right side of the screen you should see a "Search this Forum" box. Type in the topic and you will see bas posts on this subject.
Also the Copper Development Association has good info on copper cable, busbars, pipe, roofing, and other uses for copper! http://64.90.169.191/applications/plumbing/techref/cth/cth_toc.html leads to piping, but you should be able to navagate to the cable and bus bar section easily enough!
12/22/2009 9:53 AM
Attached should be our busbar ratings from testing and 40 years experience.
If not I can e-mail.
A day without a smile is a day lost
12/22/2009 1:21 PM
Hi... Could not see the attachments ... can u plz. e-mail it to iftekkar@electroi.com
12/23/2009 12:31 AM
Dear Mr. Peterd,
If you could please mail to shanbhag@sequentindia.com regarding my above doubt, i would be grateful. I do have a lot of technical papers regarding the busbar sizing methods. The reason i asked the above question was to get more information and guidance from engineers who have practical experience.
Thank you for the information. Have a nice day
04/08/2010 10:02 AM
Hello sir, I want to know how to design bus bar for high dc current. I dont know how to start designing it? what are the parameter's i need to consider and how they affect the design of busbar ??
04/08/2010 10:03 AM
04/30/2010 3:03 AM
peterd, I cannot find the attachment too. Could you please send it to my email: skywalker@bigfoot.com? Thank you very much.
Engineering Fields - Power Engineering - Siswanto
Good Answers: 15
12/23/2009 12:33 PM
inform me your email address, I will sent you the bus bar design, I cant attached in this forum due to lot of figures, graphs and tables.
Rgds
Sis
Types of Busbar
Busbars can be sub-divided into the following categories, with individual busbar systems in many cases being
constructed from several different types:
a) Air insulated with open phase conductors
b) Air insulated with segregating barriers between conductors of different phases.
c) Totally enclosed but having the construction as those for (a) and (b)
d) Air insulated where each phase is fully isolated from its adjacent phase(s) by an earthed enclosure. These are
usually called 'Isolated Phase Busbars'.
e) Force-cooled busbar systems constructed as (a) to (d) but using air, water, etc. as the cooling medium under
forced conditions (fan, pump, etc.).
f) Gas insulated busbars. These are usually constructed as type (e) but use a gas other than air such as SF6,
(sulphur hexafluoride).
g) Totally enclosed busbars using compound or oil as the insulation medium.
The type of busbar system selected for a specific duty is determined by requirements of voltage, current, frequency,
electrical safety, reliability, short-circuit currents and environmental considerations. Table 1 outlines how these
factors apply to the design of busbars in electricity generation and industrial processes.
Calculation of Current-carrying Capacity
A very approximate method of estimating the current carrying capacity of a copper busbar is to assume a current
density of 2 A/mm2 (1250 A/in2) in still air. This method should only be used to estimate a likely size of busbar, the
final size being chosen after consideration has been given to the calculation methods and experimental results
given in the following sections.
Methods of Heat Loss
The current that will give rise to a particular equilibrium temperature rise in the conductor depends on the balance
between the rate at which heat is produced in the bar, and the rate at which heat is lost from the bar. The heat
generated in a busbar can only be dissipated in the following ways:
(a) Convection
(b) Radiation
(c) Conduction
In most cases convection and radiation heat losses determine the current-carrying capacity of a busbar system.
Conduction can only be used where a known amount of heat can flow into a heat sink outside the busbar system or
where adjacent parts of the system have differing cooling capacities. The proportion of heat loss by convection and
radiation is dependent on the conductor size with the portion attributable to convection being increased for a small
conductor and decreased for larger conductors.
Convection
The heat dissipated per unit area by convection depends on the shape and size of the conductor and its
temperature rise. This value is usually calculated for still air conditions but can be increased greatly if forced air
cooling is permissible. Where outdoor busbar systems are concerned calculations should always be treated as in
still air unless specific information is given to the contrary.
Heat Generated by a Conductor
The rate at which heat is generated per unit length of a conductor carrying a direct current is the product I2R watts,
where I is the current flowing in the conductor and R its resistance per unit length. The value for the resistance can
in the case of d.c. busbar systems be calculated directly from the resistivity of the copper or copper alloy. Where an
a.c. busbar system is concerned, the resistance is increased due to the tendency of the current to flow in the outer
surface of the conductor. The ratio between the a.c. value of resistance and its corresponding d.c. value is called
the skin effect ratio (see Section 4). This value is unity for a d.c. system but increases with the frequency and the
physical size of the conductor for an a.c. current.
Rate of Heat generated in a Conductor,
W/mm = I2 RoS
where I = current in conductor, A
Ro = d.c. resistance per unit length, Ω/mm
S = skin effect ratio
Skin Effect
The apparent resistance of a conductor is always higher for a.c. than for d.c. The alternating magnetic flux created
by an alternating current interacts with the conductor, generating a back e.m.f. which tends to reduce the current in
the conductor. The centre portions of the conductor are affected by the greatest number of lines of force, the
number of line linkages decreasing as the edges are approached. The electromotive force produced in this way by
self-inductance varies both in magnitude and phase through the cross-section of the conductor, being larger in the
centre and smaller towards the outside. The current therefore tends to crowd into those parts of the conductor in
which the opposing e.m.f. is a minimum; that is, into the skin of a circular conductor or the edges of a flat strip,
producing what is known as 'skin' or 'edge' effect. The resulting non-uniform current density has the effect of
increasing the apparent resistance of the conductor and gives rise to increased losses.
The magnitude and importance of the effect increases with the frequency, and the size, shape and thickness of
conductor, but is independent of the magnitude of the current flowing.
It should be noted that as the conductor temperature increases the skin effect decreases giving rise to a lower than
expected a.c. resistance at elevated temperatures. This effect is more marked for a copper conductor than an
aluminium conductor of equal cross-sectional area because of its lower resistivity. The difference is particularly
noticeable in large busbar sections
etc.......................................................................
sorry I cant copy the article to this form... its very dificult....
Rgds
Sis
LOVE FORUM AND DISCUSSION
12/24/2009 12:36 AM
Dear Sir,
Thank you so much for the information. I would be grateful to yourself if you could help me more by forwarding the above information to shanbhag@sequentindia.com.
it is indeed my pleasure to interact in such a forum .
Regards
03/13/2010 8:24 PM
pl send me busbar calculation.
my mail id is mitulcshah@gmail.com
thanks.
11/15/2015 7:31 AM
Dear Sir,
Can you also send me the design. Im actually new in designing busbars.
Thanks and regards,
claud
01/26/2018 9:42 AM
Inbox me , busbar calculation for temperature rise test . No
Good Answers: 170
12/24/2009 7:42 AM
I suggest you attend to our 4-days training programme on Electrical Design of Switchgear Assembly, scheduled to be held at our training centre at Coonoor (near Ooty) from 18th to 21st Jan. 2010. Pl. mail me thro this forum's mailbox for further details.
12/26/2009 6:17 AM
Dear Sir, Thank you Sir, If you are calling from L&T, then i have already attended the same 4 years back. But what happens is that.. for different applications.. considerations are different..
That was the reason i gave a specific example of 4000 A...
you may remember me.. Shrimant Shanbhag ( Ex-Marketing- Load Controls,Bangalore)
01/05/2010 12:27 AM
Dear Sir Please send me details of the course to my email id s.santhiraj@gmail.com best regards