Transformer Turn Ratio (TTR) Testing

01/19/2010 7:35 PM

Can someone explain what the purpose of TTR (transformer turn ratio) testing is suppoed to catch? Why we test for it?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
11
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#1

Re: What is TTR (transformer turn ratio) purpose?

01/19/2010 9:15 PM

what the purpose of TTR (transformer turn ratio) testing , Why we test for it?

Dear : rabat:

Transformer Turn Ratio (TTR)

Turns Ratio Test . The transformer turns ratio (TTR) test detects shorts between turns of the same coil, which indicates insulation failure between the turns. These tests are performed with the transformer de-energized and may show the necessity for an internal inspection or removal from service.

Measurements are made by applying a known low voltage across one winding and measuring the induced voltage on the corresponding winding. The low voltage is normally applied across a high voltage winding so that the induced voltage is lower, reducing hazards while performing the test. The voltage ratio obtained by the test is compared to the nameplate voltage ratio. The ratio obtained from the field test should agree with the factory within 0.5%. New transformers of good quality normally compare to the nameplate within 0.1%.

Example test ratio ( this measurement is example only not for the winding as attached below)

Primary Voltage : Tap #1. : 4368 volts

Secondary Voltage : 2400 volts

Calculated turn ratio

Voltage turn ratio = 4368 / 2400 = 1,820

Measured Turn Ratio :

H1 : High Voltage Phase 1

H2 : High Voltage Phase 2

X1 : Low Voltage Phase 1

X2 : Low Voltage Phase 2

etc... measured also for other phases remaining

Sample fig for damaged transformer winding ( 30 MVA , 70 / 20 KV)

Winding damaged

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Good Answer (Score 11)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#2
In reply to #1

Re: What is TTR (transformer turn ratio) purpose?

01/19/2010 10:48 PM

Hi Siswanto,

Great post! Very informative - pictures very helpful.

GA from me!

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#3
In reply to #1

Re: What is TTR (transformer turn ratio) purpose?

01/19/2010 11:58 PM

Great answer Siswanto. Thanks for the info.

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: What is TTR (transformer turn ratio) purpose?

01/20/2010 9:24 AM

plz let me know one thing as well that what should be the applied voltage level for this test?

Register to Reply
2
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#5
In reply to #4

Re: What is TTR (transformer turn ratio) purpose?

01/20/2010 10:49 AM

what should be the applied voltage level for this test

Hi guy...

If automatic TTR Instrument has not available, you can test by Volt Meter Method, following is the voltage test should be applied with refer to IEEE Std.

Voltmeter method on TTR Test

Transformer ratio test is conducted to ensure that the turns ratio tally with the name plate details and also that tap changer connections are done correctly. Ratio test is done using a transformer turns ratio tester or with voltmeters. With the turns ratio tester, the turns ratio is directly read on the tester for each tap and for each phase of the winding.

The turns ratio can also be tested by applying a single phase ac voltage on the HV side and measuring the voltage on the low voltage side at all tap positions

Two ac voltmeters are used, one connected to the high-voltage winding and the other connected to the low voltage winding. The high-voltage winding is excited to a voltage not exceeding the rating of the voltmeter, in approximately 10%,

in practically (approximately 230V)

Both voltmeters are read simultaneously. A meaningful ratio measurement may be made using only a few volts of excitation. The transformer should be excited from the highest voltage winding in order to avoid possibly unsafe high voltages. Care should be taken during the application of voltage and during the measurement. It is important that simultaneous readings of both voltmeters be made.

Ref :

IEEE Std C57.12.90-2006

IEEE Standard Test Code for Liquid-Immersed Distribution, Power, and Regulating transformers

IEEE Std 62-1995

IEEE GUIDE FOR DIAGNOSTIC FIELD TESTING OF ELECTRIC POWER APPARATUS

Good Luck

Rgds

Sis

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Nov 2009
Posts: 14
#8
In reply to #5

Re: What is TTR (transformer turn ratio) purpose?

01/21/2010 1:46 AM

respect to Siswanto !

could you, pls explain why winding resistance test is to be done too - generally both of them - TTR and W resistance are to comfirm health of winding insulation ?

and btw one more question -

Power factor - Dissipation factor - watt loss test- Doble test - are all of them just diffirent names of the same ? am I right?

BR

AndreY

Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#9
In reply to #8

Re: What is TTR (transformer turn ratio) purpose?

01/21/2010 5:50 AM

Dear Friends

andreY:

vinukumar

Thank you for your questions and feedback. I appreciate to all of you…

To Andrey. Its good question, why winding resistance test is also done,

Yes you right, both of test are basically used to diagnostics transformer, and both of these measurement are used to detect winding problems such as, short inter turn, bad connections, loose contacts etc..

Measurement of Winding DC Resistance should be compared to factory measurement, agreement within 5% to factory measurement is consider satisfactory.

Winding DC Resistance to be converted to the reference temperature used at the factory measurement (usually 750C)

Note. Its important the final measurement of Winding DC Resistance is when the meter is stable (winding resistance cant not be measured instantaneously), its normally need long time to get stable due to the charging time in the winding.

Winding DC Resistance is supplements test and its useful when DGA shows generation of heat gases ( C2H6, C2H4, CH4, C2H2), as we know that when XFMER produce gases over the limit value is generate by thermal fault round 3000C up to 7000C. these thermal fault can resulting over heating on the winding and even they are not short insulation found.

So Winding Resistance is useful also to calculation of I2R component conductor losses, to analysis of XFMER we should test as much as we can do , its helping us easier to make a conclusion.

Due to the resistance very sensitively to temperature change, during measuring, winding temperature must be recorded, unfortunately almost of winding temperature sensors are usually using RTD's, and the sensors can not installed close the copper, so the temperature measurement is not precise ( app 150C less than hot spot temperature). Its very difficult to get exactly information temperature winding, inaccurate measurement during test can occur, thus the Winding DC Resistance mostly used as highlight what happening with the XFMER winding. That why the other test such as TTR should be performed also.

Andrey quote:

Power factor - Dissipation factor - watt loss test- Doble test - are all of them just diffirent names of the same ? am I right?

Yes its just the name, but for the doble test should be included the capacitance test, when you test Power factor or dissipation power factor, you can also directly measure the capacitance and excitation

To vinukumar,

Please let us know detail tests to be performed on Transformers before and after commissioning or guide us to good study material with practical illustrations.

How to install the meter and how to do when we inspect the TTR test, its very simple, voltage source (use variable voltage / slide regulator single phase), install the outgoing slide regulator to HV side XFMER (phase H1, H2), set the voltage (normally 230V) , measure by volt meter-1 and hold, and then read the induction voltage at LV side x1-x2 by voltmeter-2, do to other phases remaining and tapping, calculate the maximum deviation from each test tapping to name plate , the good quality for new transformer normally within 0.1% max 0.5%.

Damaged XFMER Winding, 40 MVA, 150 kV / 20 kV

Damaged on the OLTC, MR V / I / 250

Good Luck

Regards

Sis

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2009
Posts: 59
#6
In reply to #1

Re: What is TTR (transformer turn ratio) purpose?

01/20/2010 4:53 PM

Great post. Greatly appreciated.

Register to Reply
Active Contributor

Join Date: Nov 2008
Location: Bangalore
Posts: 22
#7
In reply to #1

Re: What is TTR (transformer turn ratio) purpose?

01/20/2010 11:47 PM

Hi Siswanto

Excellent answer and illustrations. Please let us know detail tests to be performed on Transformers before and after commissioning or guide us to good study material with practical illustrations.

Regards

Vinukumar

__________________
Let Noble Thoughts Comes to Us From All The Sides
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#10
In reply to #7

Re: What is TTR (transformer turn ratio) purpose?

01/21/2010 9:43 AM

let us know detail tests to be performed on Transformers before and after commissioning or guide

Dear : vinukumar

INSPECTIONS ITEMS

Winding

DC Resistance
Turn Ratio
Percent Impedance / leakage reactance
Sweep Frequency Response Analyzer (SFRA)
Doble test for winding and oil
- Capacitance
- Excitation current
- Power Factor Capacitance Tan Delta

Bushing and Arrester

Capacitance (Doble Test)
Dielectric Loss Watt
Power Factor
Temperature (Infra red camera)
Oil level on bushing
Visual inspection for Percelin crack and chip

Insulation Oil

DGA (Dissolve Gas Analysis)
Dielectric Strength
Moisture
Power Factor / Dissipation
Interfacial Tension
Acid Number
Furance

Tank and Auxiliaries

Fault pressure relay (function test)
Pressure relieve devices (visual test)
Bucholze Relay (visual check for gas)
Top Oil Temperature Indicator
Winding temperature indicator
Infra Red temperature Scan
Fault Analyzer (Ultrasonic)
Sound Analysis

Conservator

Visual (oil leake and leake in diagpragm)
Inert Air Systems ( desiccant color)
Level gauge calibration

Cooling Systems

Clean ( fan blade and radiator)
Fan and control (check fan rotation)
Oil Pump (check flow indicator , check rotation)
Pump bearings ( vibration, sound and temperature)
Check Radiator ( valve open)
Check Cooling System with infra red camera

Core

Insulation Resistance
Ground Test
__________________
LOVE FORUM AND DISCUSSION
Register to Reply Score 1 for Good Answer
Anonymous Poster
#11
In reply to #1

Re: What is TTR (transformer turn ratio) purpose?

11/08/2010 1:45 PM

Can you tell me where I can find the .5% deviation spec? What the testing standard is? IEEE, ANSI

Register to Reply
Participant

Join Date: Jan 2015
Posts: 2
#12

Re: Transformer Turn Ratio (TTR) Testing

01/22/2015 12:14 PM

Is there a IEEE or IEC for "The ratio obtained from the field test should agree with the factory within 0.5%. New transformers of good quality normally compare to the nameplate within 0.1%" wich states that for NEW TRANSFORMERS TTR should be 0.1%?

Please let me know. Thank you.

Register to Reply
Participant

Join Date: Jan 2015
Posts: 2
#13

Re: Transformer Turn Ratio (TTR) Testing

01/22/2015 12:17 PM

Is there a IEEE or IEC which states that for New transformers of good quality normally compare to the nameplate within 0.1%?

Please let me know.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: