Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system

02/23/2010 2:41 PM

Hello all,

Will there be any drawbacks if we install a 50 Hz 200 KVA 3 KV transformer in 60 Hz system?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system

02/23/2010 5:01 PM

If the transformer is designed for 50 Hz, you can use it in 60 Hz system but not the vise-versa.

The induced voltage formula is

V = 4.44 x f x B x A x N

OR

A = V / (4.44 x f x B x N)

Where V = induced voltage, f = frequency, B = flux density, A = Cross sectional area of core and N = Number of turns

The cross sectional area of the transformer core is 20% bigger for 50 Hz than 60 Hz. So, in terms of flux saturation, it should not be problem but the transformer % impedance (or voltage impedance) will be 20% more than the one you find from nameplate, because impedance is directly proportional to frequency (X = 2 x PI x f x L). If the increase of 20% impedance is not a problem for your system (for increase voltage drop or voltage regulation), you can use it.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system

02/23/2010 5:26 PM

Just to add few more drawbacks:

- The eddy current loss will be increased and generate more heating

- The transformer will create more sound than usual

- The 60 Hz system will create more mechanical stress (due to rapid flux change) to the transformer body and eventually will decrease the life of the transformer.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#3
In reply to #2

Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system

02/24/2010 12:46 AM

Dear Mr. Msamad Sir,

With reference to your answer for the above question, i had a doubt which i wanted to have a clear clarity. I have observed static electrical machines like transformers and chokes, reactors emit sound . From my fundamental knowledge of electrical engineering, i came to know that the sound was because of effect called magneto-striction. further to this information, i came to know that since the laminations cannot be ideally 100% mechanically stacked, the noise emits due to individual lamination vibration and also due to inter-lamination vibration. I request yourself to give me a bit more practical information regarding this matter.

All our esteemed forum members are also requested to give their expert advice.

Thanks

Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#4

Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system

02/24/2010 11:08 AM

Losses and induced voltage will be more. It will cause damage to insulating material. proper cooling arrangement should be done.