Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system
02/23/2010 5:01 PM
If the transformer is designed for 50 Hz, you can use it in 60 Hz system but not the vise-versa.
The induced voltage formula is
V = 4.44 x f x B x A x N
OR
A = V / (4.44 x f x B x N)
Where V = induced voltage, f = frequency, B = flux density, A = Cross sectional area of core and N = Number of turns
The cross sectional area of the transformer core is 20% bigger for 50 Hz than 60 Hz. So, in terms of flux saturation, it should not be problem but the transformer % impedance (or voltage impedance) will be 20% more than the one you find from nameplate, because impedance is directly proportional to frequency (X = 2 x PI x f x L). If the increase of 20% impedance is not a problem for your system (for increase voltage drop or voltage regulation), you can use it.
- MS
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system
02/23/2010 5:26 PM
Just to add few more drawbacks:
- The eddy current loss will be increased and generate more heating
- The transformer will create more sound than usual
- The 60 Hz system will create more mechanical stress (due to rapid flux change) to the transformer body and eventually will decrease the life of the transformer.
- MS
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Re: Installing 50 Hz 200 KVA 3 KV transformer in 60 Hz system
02/24/2010 12:46 AM
Dear Mr. Msamad Sir,
With reference to your answer for the above question, i had a doubt which i wanted to have a clear clarity. I have observed static electrical machines like transformers and chokes, reactors emit sound . From my fundamental knowledge of electrical engineering, i came to know that the sound was because of effect called magneto-striction. further to this information, i came to know that since the laminations cannot be ideally 100% mechanically stacked, the noise emits due to individual lamination vibration and also due to inter-lamination vibration. I request yourself to give me a bit more practical information regarding this matter.
All our esteemed forum members are also requested to give their expert advice.