PVC Cable Glands

03/11/2010 2:26 PM

1CX 300 sq.mm unarmored Cable using PVC Gland .It was terminated in the LV panel.Now the client was not accepting because,the reason is the gland plate was mild steel,so the cable entry area the magnetic path form so that to refuse. Now all the cable was terminated its very difficult to remove and again terminate after fixing SS gland plate

even pvc gland use how the magnetic path will form Its correct or not if correct means now what we can do.

Register to Reply
Pathfinder Tags: pvc gland
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: PVC Cable Glands

03/11/2010 4:50 PM

This has been covered before on CR4 and this is the best response I could quickly find.

http://cr4.globalspec.com/comment/60648/Re-Trefoil-of-single-core-cables-for-3-Phase-AC-power

I am assuming you have multiple single core cables (3 perhaps) passing through a single mild steel gland plate. If this is the case you can either replace the gland plate with an aluminium one or perhaps cut a slot between each of the single core conductors (at right angles to the electromagnetic field created by the current passing through the cables) to break up the electromagnetic heating effect. You can seal up the holes with a filler or aluminium plate (as long as it isn't magnetic).

The slot option above may be able to be done with the cables connected, if you are careful (but you need to go all the way through the metal to the cable, which means moving the glands out of the way). If it were me I would replace the gland plate (you are MUCH less likely to accidentally damage the cable this way).

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2009
Location: Townsville, Australia
Posts: 149
#2

Re: PVC Cable Glands

03/11/2010 5:19 PM

I've just got through the same drama, and it really is a pain. Yes, the answer is to break the magnetic circuit with a slot between the cables. I achieved this by drilling a series of small diameter holes, in line between the glands, I then slackened off the locknut securing the gland, leaving the gland body still in place on the cable, and drilled right up against the gland. With a series of holes now between the glands, "waggle" the drill so that the holes break into each other. In my case, I finished it off by inserting a flat bladed screwdriver, and levering, this will break any whiskers remaining. I then replaced the locknut. The enclosure integrity was restored by applying a bead of silastic along the slot. I used a 3mm drill bit, powered by a cordless drill.""IT GOES WITHOUT SAYING THAT EXTREME CARE SHOULD BE USED, AND THAT THE POWER SHOULD BE OFF!!"" I am assuming that there is room to get the drill in!

Good luck.

Register to Reply
Anonymous Poster
#3

Re: PVC Cable Glands

03/11/2010 10:57 PM

During detailed Engineering stage itself these issues should have been checked and the panel builder should havebeen instructed to provide Aluminium Gland plates of adequate thicknes of minimum 4 mm.

Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#4

Re: PVC Cable Glands

03/12/2010 12:22 AM

Dear Sridhar Ganesan,

May be you are getting confused with cable gland and Aluminium gland plate. Aluminium gland plates are used because they are non magnetic. whenever a current flows in a conductor( specially 200 A & above), magnetic field is created and eddy currents circulate around the metal where the cable enter the panel( it is true for any case, not only panels). Since steel is magnetic, eddy currents circulate and produce heat. the heat in this case is very high. if aluminium is used, due to non magetic nature, eddy currents WILL NOT BE INDUCED and heating of sorrounding metal will not take place. This concept is quite old and by default,panel manufacturers provide them during commissioning.

Thanks and Regards

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #4

Re: PVC Cable Glands

03/12/2010 8:50 AM

Many responders are incorrect. Eddy currents are also induced in aluminium in a variable magnetic field. This is why AC induction motors work!

To prevent eddy currents flow in an electrically conductive plate (steel, aluminum, copper...) you need to balance the current flow in each holes to obtain a near zero difference. This means that balanced three phase conductors must use the same hole.

That being said, I have seen many installations (to my great surprise) in Mexico where each phase has its own hole in a steel cabinet. The loads were DC drives generating >30% THD. I didn't measure any temperature rise at the cabinet surface while drawing > 600A AC. That reduced my fear of conductors in different holes described above. The heating doesn't seem to be so important at low frequency.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#6
In reply to #5

Re: PVC Cable Glands

03/12/2010 11:37 PM

Thank you for the better clarifications sir.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); marcot (1); Normbourne (1); shanbhag (2)