Will PVC Glands Nulify Eddy Currents in Single Core Termination?

03/12/2010 3:55 PM

hi,

I want to know whether the use of pvc gland in metallic gland plate will nullify the effect of eddy current in single core cable termination.

Rightnow i have a problem in one of my site where people had terminated single core cable by making holes in metallic gland plates and used pvc glands as it is unarmoured cable but cables are in trefoil arrangement that too only in cable trays and in the cable entry they have seggregated cable according to phases. there are 9 runs of single core 300sq.mm cable per phase.

kindly help me out. just want to know use of pvc gland will no effect of eddy current or magnetic path in cable entry point.

regards.

saimahadev.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Will PVC Glands Nulify Eddy Currents in Single Core Termination?

03/12/2010 4:40 PM

No.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#2

Re: Will PVC Glands Nulify Eddy Currents in Single Core Termination?

03/12/2010 11:36 PM

Dear Saimahadev,

check this thread http://cr4.globalspec.com/thread/51723.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#3

Re: Will PVC Glands Nulify Eddy Currents in Single Core Termination?

03/13/2010 3:03 AM

Dear all,

You can continue using PVC cable gland for single core cables. For gland plate, you must use nonferrous material such as aluminum, brass or plastic such as PVC should be used for single core cables.

Eddy current will be induced even in nonferrous metal, but it does not have hysteresis loss. Heat produced eddy current in nonferrous metal is negligible.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4

Re: Will PVC Glands Nulify Eddy Currents in Single Core Termination?

03/13/2010 9:52 AM

Are you measuring any temperature increase around the cables in operation with the present configuration? If not, why do you have a problem?

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 12
#5
In reply to #4

Re: Will PVC Glands Nulify Eddy Currents in Single Core Termination?

03/15/2010 4:27 AM

If you can cut a line between the glands, you will break the eddy current path, alternatively is as mentioned a non metallic gland plate is required.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); DSM2512 (1); marcot (1); shanbhag (1); Tornado (1)

Previous in Forum: How to Generate Electricity with a Gas Turbine   Next in Forum: Split Core Transformers vs. Ordinary Transformers
You might be interested in: Cable Trays, Cable Laying Services, Cable Assemblies

Advertisement