A Industrial Plants Ambient Temperature is 50 Deg C
A motor with Insulation Class F with Temperature Class Limited to Class B is to be procured
Is it correct to procure the same
Good Answers: 244
Re: Motor Insulation Class
06/02/2010 10:58 AM
The chart for the Motor Insulation class is (see http://cr4.globalspec.com/thread/35356 also):
Ins. Class
Max Temp.
Amb. Temp.
Temp. Rise
Hot Spot Allow.
A105°C40°C55°C10°C
B130°C40°C80°C10°C
F155°C40°C105°C10°C
H180°C40°C130°C10°C
Note: Hot Spot Allowance - The value that takes into account the additional temperature variations within the inaccessible spots of a motor winding. These spots are located in the stator slots or coil heads. 10° C is considered a standard for design purposes.
"A motor with Insulation Class F with Temperature Class Limited to Class B" means the motor insulation is rated at 155°C (with class F) but its maximum temperature rise will be limited up to 130°C (with class B). So, it should be ok. Make sure the motor vendor clearly understands your requirement including the 50°C ambient temperature.
- MS
Good Answers: 169
06/08/2010 10:44 AM
It is excellent to go for such a motor (with Class F insultaion & temperature rise limited to Class B). Under such ambients too, the life of the motor is extended.