How neutral grounding resistor will protect HT motors and transformers from ground fault.How can i use it.Anyone can explain the application area of neutral grounding resistor(NGR)
NGR is installed at the transformers and alternators particularly when the units are large in order to limit the fault currents to a considerably low magnitude.
In the event of an earth fault, E/F relay acts to protect the equipment.(Please note it is not NGR similarly mentioning HT and motors is ambiguous).
__________________
Knowledge sharing is a WIN-WIN situation
NGR protects the electrical system and equipment by limiting the ground fault currents. Because of the use of resistance between the neutral and the ground, the ground fault current is minimized for the single line to ground fault (most common type of fault) and hence there is less damage to the system as well as the faulty equipment.
There are two types of NGR: High Resistance Grounding (HRG) and Low Resistance Grounding (LRG)
High Resistance Grounding (HRG): It is used where service continuity is vital, such as process plant motors. With HRG, the neutral is grounded through a high resistance so that very small current flows to the ground if ground fault occurs. In the case of ground fault of one phase, the faulty phase goes to the ground potential but the system doesn't trip. This system must have a ground fault monitoring system. The use of line to neutral (single phase) is prohibited (NEC, 250.36(3)) in HRG system, however, phase to neutral is used with using the additional transformer having its neutral grounded. When ground fault occurs in HRG system, the monitoring systems gives alarm and the plant operators start the standby motor and stop the faulty one for the maintenance. This way, the process plant is not interrupted.
Low Resistance Grounding (LRG): This is used for limiting the ground fault current to minimize the impact of the fault current to the system. In this case, the system trips for the ground fault. In this system, the use of line to neutral (single phase) is prohibited here as well.
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
When the three phase supply voltage is balanced, the voltage between neutral point and the earth is zero. In case of earth fault or arcing or transient in the system , the current in all three phases get unbalanced. The unbalance current in phases produce voltage between the neutral and ground. If the neutral of the transformer is not earthed the voltage of healthy phases increases up to 1.73 times of the healthy phase voltage. To prevent this, the neutral of the transformer is earthed.
The resistance is inserted between the neutral and earth point to limit the fault current to equipment safe current limit. The NGR grounding impede the fault current path.
The calculation of the resistance value is a very important criteria for equipment protection.The discharging current of the capacitor formed between the line and ground must also be considered. The system fault current and the system voltage should be taken into consideration for NGR selection.
The below link may be helpful for understanding NGR concepts.