Hello Everyone:
Would you kindly please help me with this?
I want to know the steps toward creating P.M.S (Especially, selecting the materials and wall thickness calculation) in projects.
For creating the P.M.S for a project we usually use the previous experiences or sometimes the client asks us to use their P.M.S as a base.
As I know the following steps should be taken for selecting the materials and calculating the wall thickness:
1- Generating the PFD from Process Dep.
2- Generating the Material Selection Diagram by Material & Welding Dep.
3-Calculating the Corrosion rate.
4-Calculating the corrosion allowance (which is a part of wall thickness calculation in P.M.S)
After these 4 steps we are going to calculate the wall thickness according to the paragraph 304.1.1 of standard ASME B31.3)
My questions are as follow:
1-For generating the MSD how we should select the material? I have reviewed a lot of standards and specs but I could not find what I am looking for. I am really interested to have a reference for selecting the materials in this regards).
2-How we should calculate the corrosion rate in Normal condition (without CO2)?
3-I am looking for a few solved examples for both, with CO2 and without CO2.
4-Please let me know if I am wrong, and also please advise me.
Best regards,
This discussion was "closed" on 08/23/2010 8:25 AM. No new comments are allowed.
Message from admins:
This thread is a duplicate. Please see the open discussion here: http://cr4.globalspec.com/thread/58971
Good Answers: 101
Re: Creating P.M.S
08/22/2010 5:19 AM
PMS: Pre-Menstrual Syndrome? Why on Earth do you want to create that for? Aside from the fact that it occurs naturally for many women on that particular time of the month, do you know just how unpleasant it really is living with a girl with that problem?
Re: Creating P.M.S
08/22/2010 5:27 AM
HYwindgenerator.com is the professional manufacturer of Wind generator,small wind turbine,wind turbine generator,windmill, wind mill,wind generators in china ,if you want to 3KW, 2KW Wind generator,5KW wind turbine, 10KW,20KW wind turbine generator and grid tie inverter,please contact us. lower carbon text
china wind turbine generator, small wind turbine, wind generator-HYwindgenerator.com
Register to Reply Off Topic (Score 17)
Good Answers: 145
Re: Creating P.M.S
08/22/2010 5:39 AM
There is only one thing that's worse than a woman with P.M.S., and that's one going through Menopause as well...
Re: Creating P.M.S
08/22/2010 11:06 AM
Creating P.M.S. is a CRIMINAL offence.
Good Answers: 83
Re: Creating P.M.S
08/22/2010 12:35 PM
Re: Creating P.M.S
08/22/2010 12:43 PM
Many a Military contract has included apparent Purely Meaningless Systems that do require proper integration. Many but not all of these integrations follow the EIA-933 standard for COTS. The more cryptic and baffling the standard one has chosen to comply to, the more the standard will help to preserve the security of your system's meaning along with a bolster of your own linguistic capability to obfuscate.
All meant in fun.
Re: Creating P.M.S
08/22/2010 3:33 PM
Could you please explain what PMS and MSD are? MSD may be Material Safety Data sheet but I don't know PMS, I am guessing it isn't any of the guesses above. You have mentioned ASME B31.3 (Standards for Pressure Piping) but this still doesn't help.
Please provide more information.
Good Answers: 83
Re: Creating P.M.S
08/22/2010 3:37 PM
Maybe...
Performance management system, performance measurement system or performance monitoring system [Note that these are NOT synonymous, but are used in the same field, so intended usage should be confirmed if important. ...
en.wiktionary.org/wiki/PMS
Good Answers: 141
Re: Creating P.M.S
08/22/2010 6:48 PM
In Europe PMS is "post menstrual syndrome". I didn't know it was that complicated.
Plenty of room here
Re: Creating P.M.S
08/23/2010 12:23 AM
I had sample simulation below may will help you, this is had formulated at excel but can.t dis play here. This is folowing API579, hope help u
CALCULATION WALL THINING/WALL LOOSSE/ PITTING
TECHNICAL DATA
DESIGN PRESSURE(P)150(PSI)
RADIUS OF VESSELS(R)60(INCH)
ALLOWABLE STRESS(S)17500(PSI)( Allowable stress at T condition;chapter4-10)
SEAM WELD FACTOR(E)0.85(TABLE 302.3.4;chapter 4-12)
VALUE OF KOEF OF TEMP(y)0.4(TABLE 304.1.1;chapter 4-14)
MINIMUM DESIGN THICKNESS(t
min)
((P*R)/((S*E)-(0.6*P)))
(t
min)
0.608725(inch)
(t
min)
15.46162(mm)
PARAMETER
Condition 1(pitting evaluation)
(tmm – FCA > 0.1) inch
Thickness minimum as per readingt
mm
0.36inch
Future corrosion AllowanceFCA(((t2-t1)/span)*time))
First reading referencet10.75inch
Second reading referencet20.36inch
Span time from t1~t2span10yr
Periode time predictiontime11yrs
0.039(Cal.support )
FCA0.039
0.321>0.1ACCEPTABLE
Condition 2 (Limit wall loss within reason)
(tmm – FCA > tmin / 2)
0.321
0.304363ACCEPTABLE0.472668
Condition 3 (Will not fail due to pressure)
(L ® tam – FCA > RSFa x tmin)
Reading thickness at span Lt
am
0.750.480.470.550.360.480.490.75
Average thicness at span Lt
am
0.54125
Span efective wall loosse lengthL:1.123*(((((1-((tmm-FCA)/tmin))/(1-(((tmm-FCA)/tmin)/RSFa))^2)-1)^0.5)*((D*tmin)^0.5)
Out side diameterD20inch
remaining strength factor alowableRSFa0.7(0.7~1)
abcda(tmm-FCA)/tmin
(cal.support)0.5273320.7533313.671846.0434681.634576ba/RSFa
c(1-a)/(1-b)^^2
AVERAGE READING AREA NEEDEDL11.09357INCHd(D*tmin)^^0.5
(t
am – FCA > RSFa *t min)
0.50225
0.426108ACCEPTABLE
Re: Creating P.M.S
08/23/2010 2:02 AM
P.M.S is stand for Piping Material Specification and MSD is stand for Material selection Diagram.
Good Answers: 145
Re: Creating P.M.S
08/23/2010 2:43 AM
If you had put the plain language labels of "Piping Material Specification" and "Material Selection Diagram" in your initial post then you would have saved yourself an awful lot of ridicule.
Acronyms are only appropriate once their meanings are firmly established. That stands for posts on forums or technical documentation.
When you assume,, as Prof Julius Sumner Miller was want to say.
Re: Creating P.M.S
08/23/2010 4:27 AM
Honestly I have to say I did not think that some members in "Material and Petrochemical" section did not know what P.M.S and M.S.D stand for!!!!
I assumed members are going to read the question completely and then try to answer it, If they had read it completely they would not have replied to my question like this.
An engineer who works in Material and petrochemical field even for a period of one or two years knows what is P.M.S or M.S.D.
Good Answers: 101
Re: Creating P.M.S
08/23/2010 7:41 AM
Would it have killed you to just simply state what you mean? MSD could also mean material safety data as in MSDS, and for that matter, how do we know that by PMS you don't mean Process Method Statement? By the way the most common meaning for PMS was what I stated.
Really, what is it about guys like you that you always find the need to blame others for your own mistakes?