Capacitor Selection

09/17/2010 10:34 AM

Hi friends

I want to know how to choose a capacitor value to improve the power factor of a motor. For example, if I have a 11 kw, 415v, 1440rpm motor and assume it operates at full load current and takes 0.85 pf, with no capacitor added. Now, I want to run the motor operates in 0.95 pf. Then how much value of capacitor i need to add if there is any calculation, please tell me.

Register to Reply
Pathfinder Tags: capacitor selection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: capacitor selection

09/17/2010 10:46 AM

Why dont you search in the forum.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Capacitor Selection

09/17/2010 11:33 AM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: Capacitor Selection

09/17/2010 2:42 PM

Is that Guinness?

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Capacitor Selection

09/17/2010 2:32 PM
__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5

Re: Capacitor Selection

09/17/2010 3:05 PM

Here is a generic calculation:

Let's assume these input data,

The total load in KW = kw

Initial power factor = pf1

The target power factor = pf2

System Voltage in KV = V

System frequency = f

For power factor improvement, pf2 shall be greater than pf1 (pf2 value closer to 1)

Calculation:

The initial KVAR, kvar1 = sqrt{(kw/pf1)2 - (kw)2}

The target KVAR, kvar2 = sqrt{(kw/pf2)2 - (kw)2}

Since pf2 > pf1, kvar1 > kvar 2

To improve power factor from pf1 to pf2, the required KVAR of the capacitor, kvar3 = kvar1 – kvar2

Again assuming it is a 3 phase system and the capacitors to be connected in Y, the required capacitor/phase, kvar = kvar3/3

Phase to neutral voltage vn = V/1.732

The required capacitive reactance Xc = (vn)2/(kvar x 1000) ohm

The required capacitor is C (in μf), then

Xc = 1/(2 x PI x f x C) (PI = 3.14)

C = 1/(2 x PI x f x Xc) μf (micro-farads)

For additional help, see these links:

http://www.powerstudies.com/articles/PowerFactorBasics.pdf

http://www.nepsi.com/kvar_calculation.htm

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); kvsridhar (1); lyn (1); msamad (1); PeterT (1)

Previous in Forum: How to assign duty class (S1 -….S9) of electrical motor.   Next in Forum: RCD for Heat Trace

Advertisement