Hello Experts !

This is with reference to the title. I had one AB PV plus 600 whose touch screen failed and consequently it was not starting after resetting it(power toggle & reset button). I have its replacement which is brand new(of course blank). Referring to its manual, configuration of the same requires CompactFlash card which I do not have. My question is that, "Is it possible to program/configure it without having flash card?" I do have its ".mer" & ".apa" files of my application. Also, even if I had the blank or new CompactFlash card, How would I load/copy my backed up files to it? OR can I use any other means, like writing a CD etc..? and then transferring to the PV plus 600.

I would be glad if any of you guide me for my problem.

Thanks in advance for your concern...

Jitesh

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
CR4 Admins - CR4 Admin - CR4 Admin

Join Date: Jul 2008
Posts: 372
Good Answers: 33
#1

Re: Allen Bradley Panel View Plus 600 Configuration

11/18/2010 7:49 AM

According to the manual, it looks like the only way to add your configuration (your .mer and .apa files) is through a CompactFlash card.

You can attempt the following:

1) Buy a supported CompactFlash memory card. From the manual:

PanelView terminals running firmware 3.0 (or later) and computers
with an ATA card drive support the following cards.
• 4M flash ATA card (Catalog No. 2711-NM24)
• 8M flash ATA card (Catalog No. 2711-NM28)

• 16M flash ATA card (Catalog No. 2711-NM216)

2) Find access to a computer with a memory card reader. Most built in memory card readers have a CF slot. If you cannot find a computer with a built in memory card reader, you can buy a USB Memory Card reader, such as this one.

3) Copy your configuration files to the root of the memory card.

4) Insert the memory card into the PV 600 following the manual. You can open Configuration Mode by pressing Left and Right simultaneously. The rest of the process is detailed in the manual.

Welcome to CR4, and good luck!

Register to Reply Score 1 for Good Answer
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#2

Re: Allen Bradley Panel View Plus 600 Configuration

11/19/2010 7:53 AM

Another possibility to get you going immediately is this . If you have another machine with a panelview plus download the .mer program into the second panelview. Make sure you do not check the box, run with download complete. Copy the file from the second panelview to a standard compact flash card and remove the file from the second panelview.

Take the flash card to the new panelview and download it using the flash card. Make sure you check the box , run with download complete, or you will have to load the file from memory every time the power is cycled. You can buy an Allen Bradley flash card but they are more money and a standard flash card will work.

Elroy

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply Score 1 for Good Answer
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#3

Re: Allen Bradley Panel View Plus 600 Configuration

11/19/2010 9:54 AM

If you have a liscensed copy of FactoryTalkViewME installed on a laptop, then it is possible to download the .mer file into the Panelview Plus by Ethernet or Seriel Communications using the "Transfer Utility." This does not require a Compact Flash card. For Ethernet, the IP Address can be entered in the Panelview's Configuration Menu which is automatically displayed whenever a "blank" Panelview is powered up.

Be warned that you may run into a firmware compatability issue after attempting to load an old .mer on a new Panelview. In FactoryTalkViewME you must "Create a Runtime Application (.mer)" that matches the Firmware version of your Panelview.

If you do not have FactoryTalkViewME, then you may have to Flash the Panelview back to the revision level that your .mer was created with.

Check to see what firmware version the Panelview is operating on by selecting "Terminal Information" -> "About RSViewME Station" from the Panelview's Configuration Menu.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

EElectrician (1); Elroy (1); yamdankee (1)

Previous in Forum: Static Pressure   Next in Forum: Zero Trim and Calibration of X'mtr

Advertisement