Motor Starting Problem

01/08/2011 10:58 AM

At the time of changeover from Star to Delta, the motor's MCCB (400A) trips. Motor details:160kW, 415V, 50Hz,3Φ. Star Delta time: 8sec. Stating current: 870A, IR is OK and the motor is free for rotation. All connections are checked and are perfectly OK. Can somebody give any suggestions?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: Motor Starting Problem

01/08/2011 11:11 AM

MCCB is undersized, change to 600 Amps.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Motor Starting Problem

01/08/2011 11:32 AM

Maybe the motor has not accelerated fully in 8 sec (Is the load a high-inertia one)? If so, when transition takes place, it may still act as DOL and trip the MCCB. What is the magnetic setting of the MCCB? Is there a "transition delay" in the starter ? (a small delay like 100ms between star contactor drop and delta contactor pickup)....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Participant

Join Date: Aug 2010
Location: Mumbai
Posts: 3
#18
In reply to #2

Re: Motor Starting Problem

01/13/2011 1:13 AM

Thanks for your comment. There is no transition delay in the starter. I will try with extending the time delay by another 2 seconds... is this OK?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#19
In reply to #18

Re: Motor Starting Problem

01/13/2011 3:25 AM

i am afraid that increasing the main dekay won't help.

The "transition delay" timer specially designed for ΥΔ starters has TWO timing functions :

1. The main timing function to change from star to delta, usually site-adjustable to suit the acceleration time of the motor.

2. A "transition delay" timing function which delays the pickup of the delta contactor after the star contactor has dropped. Usually 30ms for small motors, going up to 100ms for large ones. This delay ensures that the arcing in the star contactor has completely died down, and its arcing zone is completely de-ionised, before the delta contactor picks up. Without this delay, you may have a short-circuit. This short-circuit will trip the MCCB magnetically.

If this is the reason, you have two options.

a) Buy a standalone Star/delta timer (electronic, DIN rail mountable) available from several good manufacturers. Pneumatic timers are also available, but they are usually contactor-mountable, and you need to ask the original starter supplier if he has such a timer.

b) You can wire an interposing relay, which is given a command to close when star contactor drops, and its main contacts switch on the delta contactor. This will introduce a small (unknown) delay, but should do the job.

i would recommend (a). But to check if this transition delay is really the culprit, you can wire up a slave relay as per (b) assuming you have some relay lying around in the workshop.

Good luck, please feel free to ask if something is not clear.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#20
In reply to #19

Re: Motor Starting Problem

01/13/2011 3:52 AM

"i am afraid that increasing the main delay won't help."

Sorry for the typo...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#27
In reply to #18

Re: Motor Starting Problem

03/11/2017 5:58 AM

Yes. It may solve the problem. Why two seconds ? Try more time.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Motor Starting Problem

01/08/2011 2:47 PM

This is a very common occurrence in open transition Star-Delta starting. If the transition conditions are not perfect, the phase shift that takes place when switching from Star to Delta can interact with the residual magnetism in the motor and create a huge voltage spike if leading, or a huge current spike if lagging, theoretically as high as 2000% of motor FLA! It can be like connecting a generator that is out of phase with the line. Transition current spikes can also create very damaging torque spikes as a result, I have even seen it twist the shaft off of a motor on a 500HP refrigeration compressor.

The best solution is to avoid using Star-Delta in the first place, because it's very difficult to fix if it happens. Use a Solid State soft starter instead, they are not much more expensive and have none of these issues.

If that's not possible, you can try to rebuild the existing open transition into a Closed Transition Star-Delta starter. It involves adding a 4th contactor and a set of transition resistors to absorb the energy off of the motor during transition. In my opinion this never makes sense as a first course of action, because Closed Transition starters are always more expensive than Solid State soft starters, but as a retrofit, it may be less.

Before you go to that expense, a possible cheap fix is to "roll" the conductors. This means move 3 of the 6 motor conductors, the ones on the Delta contactor going to the motor, over by one terminal. Keep the relative rotation sequence the same, just move them on the terminals, i.e. A to B, B to C, C to A. What this may do is take advantage of the connection pattern to change the transition phase shift from lagging to leading, so the spike becomes voltage instead of current and your breaker will no longer trip. The voltage spike may cause other damage, such is the risk of using Star-Delta, but it solves the immediate problem. I learned this trick on Fire Pump controllers, but in that application a voltage spike is irrelevant compared to the fire pump failing to come on.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#4
In reply to #3

Re: Motor Starting Problem

01/08/2011 4:43 PM

Dear Lumberjack, Thank you for sharing your valuable experiences, we readers can not google this type of information.

__________________
klearzen
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#8
In reply to #3

Re: Motor Starting Problem

01/09/2011 2:28 AM

It can be like connecting a generator that is out of phase with the line.

You ain't wrong there chief.......

Houston............we have a problem!!!!

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12
In reply to #8

Re: Motor Starting Problem

01/09/2011 9:03 AM

WOW!

I've seen shafts sheared clean off, but never anything like that.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#22
In reply to #12

Re: Motor Starting Problem

01/13/2011 9:34 AM

I've seen shafts sheared clean off,

Broken crankshafts can be the result as well.

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Motor Starting Problem

01/08/2011 4:43 PM

I'll start by asking a question, has this motor run OK in the past? If it has then something has changed, it's up to you to find out what.

If it's a new install I'd go with mountk2's advise to begin.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Aug 2010
Location: Mumbai
Posts: 3
#17
In reply to #5

Re: Motor Starting Problem

01/13/2011 1:08 AM

Thanks for your comment. The compressor motor could started for just 6 months without any starting problem, but later it started tripping during the transition from Star to delta. But once it tripped I need to wait for another 20 minutes and then it starts normally without any problem. I am operating this motor since 2008 and is still in operation except this kind of starting problem once in a while. Normally I start this motor twice in a week and will continuously for next two days. Expect your further comments. ka.jaison

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#21
In reply to #17

Re: Motor Starting Problem

01/13/2011 7:39 AM

Can you remember any maintenance work done after the first six months?. Check the timer,connections and contacts of the starter

__________________
pnaban
Register to Reply
Anonymous Poster
#6

Re: Motor Starting Problem

01/09/2011 12:18 AM

Whey/Delta starting? I thought it was obsolete in 70-ties when frequency inverter allowed huge electricity savings during starting up. Who keeps this obsolete start-ups?

My suggestion is to scrap the junk and install proper frequency converter so no current surge impacts rest of the installation. 160 kW is not so difficult to control.

Register to Reply
Participant

Join Date: Jan 2011
Posts: 3
#7

Re: Motor Starting Problem

01/09/2011 1:13 AM

Dear User,

I have noted your query. One possible solution is as under.

At the time of change over delta-contactor should operate first, then after 2-3 secs star contactor, so as to avoid open rotor..is this happening??

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #7

Re: Motor Starting Problem

01/09/2011 4:38 AM

i am surprised. If both Star and Dela contactors are ON at the same time, there will be a dead-short-circuit of the mains. In fact, star and delta contactors are interlocked electrically (and preferably mechanically) so that they are never ON at the same time.

There are special closed-transition ΥΔ starters, but that is another story...

Can you give the circuit diagram of what you mean? It will be interesting for many of us.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #9

Re: Motor Starting Problem

01/09/2011 9:15 AM

Wouldn't like to be around when it starts!

Not after my escapade with the 800HP star/delta.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14
In reply to #13

Re: Motor Starting Problem

01/09/2011 9:27 AM

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster #1
#26
In reply to #9

Re: Motor Starting Problem

03/11/2017 5:05 AM

Star delta contactor starts at the same time what is the problem and solution for this probleem

Register to Reply Off Topic (Score 5)
Anonymous Poster
#10

Re: Motor Starting Problem

01/09/2011 6:18 AM

Is it a newly connected motor?(may be new motor or the existing motor installed after overhauling). If yes, in your case there could be a chance of wrong connection. i.e for delta connection one windings start end to be connected to other winding finish end(R1Y2, Y1B2 AND B1R2).If it is connected for example R1Y1 then it will lead dead short during delta changeover. In star mode it will not give problem and it will start normally.

Register to Reply
Participant

Join Date: Feb 2013
Posts: 1
#25
In reply to #10

Re: Motor Starting Problem

02/14/2013 9:42 PM

Dear Sir, This is Manikandan from chennai. Incomer MCCB is tripping while switching on one of the Star/Delta closed transition starter during S/D changeover. It's a new installation. I beleive that It could be a wrong connection like you mentioned.Can you please help me in sending the drawing of this kind of connection in S/D starter.Your immediate replym is highly appreciated. my mail ID is maniking1@yahoo.co.in.

Regards

K.Manikandan

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: Motor Starting Problem

01/09/2011 7:08 AM

Give details of MCCB like make,Im,Ir,adjustable or fixed etc. Check the peak current during changeover from star to delta. Increase the time delay between star and delta. Try to start on no load,see whether tripping. Check the setting of magnetic trip.If 500A MCCB also trips inform manufacturer and get his advice.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#15

Re: Motor Starting Problem

01/10/2011 12:05 AM

Is this a new installation?

If so does the circuit breaker trip the instant that it changes over to delta, or is there a slight delay?

It the circuit breaker that you are using a D curve type?

8 seconds for that size of motor seems a bit to short, has the motor reached a minumin of 60% full speed when it changes to delta?

Help us to help you by giving me the answers to these questions.

Cheers

Joe

Register to Reply
Participant

Join Date: Oct 2010
Posts: 1
#16
In reply to #15

Re: Motor Starting Problem

01/10/2011 3:47 AM

Extend the time duration of timer from 10 to 15 sec Please check the Delta Connection of motor Check breaker adjustment current

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#23

Re: Motor Starting Problem

01/13/2011 10:04 AM

Warning, increasing the transition delay can make it WORSE as well! With too much delay, the motor is off-line too long and actually slows down too much, the magnetic field decays too much so the flux penetration is gone and when re-connected, it may as well have been started DOL. This is why I hate Star-Delta, everything has to be just right for it to work properly.

The fact that it only happens occasionally points to the issue of the leading / lagging transition phase angle I mentioned above. You are so close to the ragged edge of acceptability that the line phase angle at the moment of transition is making a difference one way or the other, something you will have ZERO control over. Try rolling the conductors, but otherwise learn to live with it if you are unwilling to fix it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#24
In reply to #23

Re: Motor Starting Problem

01/13/2011 10:50 AM

JRaef is absolutely right. The main reason for softstarters being chosen over ΥΔ. i knew this phenomenon as "frozen rotor"....here is an extract from a paper...

The transfer from star to delta momentarily removes the motor from the supply. During this time the motor is under the mechanical influence of the rotating load and, at the instant of disconnection, current will still flow in the rotor bars due to the time delay necessary for the magnetic flux to die away. Therefore, there is a residual flux "frozen" on the surface of the rotating rotor, which cuts the stator windings, generating a voltage whose frequency dependson the rotor speed. If the load inertia is small, such as in a pump, or if the friction is high, therecould be a significant loss of speed during the time the supply is disconnected. In this case,when the reconnection to delta is made, a large phase differential can exist between the supplyand the rotor fluxes.This can give rise to very large current surges (as much, or more than full-voltage locked rotor current), together with massive transient torque oscillations. (These oscillations can be as much as five times full-load torque.) Although the effects described are only present for a very short period of time (about one fifth of a second), they are sources of great stress and damage to the whole drive system, and where frequent starting is necessary, invoke high maintenance costs.There are methods of control, for example, the closed transition starter, which eliminate or reduce the reconnection transients. However, such starters are expensive and have reliability implications; for these reasons they are not widely applied. The star-delta starter also has disadvantages due to the restricted starting torque available (if you need 40% LRT to breakaway,you can only increase the motor size, or revert to direct-on-line). Combined with the severe effects of the re-switching surges, and the additional costs of bringing six conductors from the motor to the starter instead of only three, star-delta only offers an imperfect solutionto the problem of starting the induction motor.

Here is the full paper.basic_soft_starter_principles.pdf

JRaef and i rest our case.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Joe Sparky (1); JRaef (2); ka.jaison (2); klearzen (1); kvsridhar (7); mahboobiqbal (1); maniking1 (1); MOBI (2); mountk2 (1); pnaban (2); shah.sunil1985 (1); TonyS (3)