Anonymous Poster

Tie Breaker Used In Power Control Center Arrangement

01/10/2011 5:02 PM

I have seen PCC with tie breakers NC. This one is depicted as NO. What would be the advantages of doing one or the other. Also, how having this tie breaker is better than not having one at all?

Any references, opinions etc are welcome.

Primary voltage is 4.16 kV

secondary voltage 480 (At the PCC where the tie is located)

Secondary feeders provide power to Distribution boards, MCC etc.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: tie breaker used in power control center arrangement (load side of TX in picture

01/10/2011 5:19 PM

It depends on the installation. If the transformers are to be paralleled, they need to be the same (or at least compatible) vector group, so that they will be in phase.

If not, the bus tie breaker needs to be interlocked with the other two so that it can be closed only when one of the others is open. There are many cute slider-bar tricks for doing this mechanically among various breaker combinations.

If one transformer is down, the bus tie allows a subset of loads on either side to run on the remaining transformer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#2

Re: tie breaker used in power control center arrangement (load side of TX in picture

01/10/2011 5:47 PM

OR the load can be split between the two transformers/generators when the tie is open. This is usually done for a ship with an infrequent high load mode (like jacking) that is divided with two HPU's on each MCC and the TIE Breaker open when all 4 HPU's would overload a single Feeder

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Tie Breaker Used In Power Control Center Arrangement

01/10/2011 8:48 PM

Two good answers.

Additionally, my thought is that a Circuit Breaker is a protective device and will do its function of protecting when it is ON, and will trip very quickly in the event of a fault. So, i would rather use it in the Normally Open mode.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#4

Re: Tie Breaker Used In Power Control Center Arrangement

01/10/2011 11:08 PM

it may be indicating that it can be closed when only one incomer is closed. Its similar to interlock scheme of 2 incomer+1 B/C. If two incomers are closed, it is not necessary to share the load.

__________________
You don't understand anything until you learn it more than one way.
Reply
2
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: Tie Breaker Used In Power Control Center Arrangement

01/10/2011 11:25 PM

This type of Distribution arrangement is followed for continuous process industry/Software parks/Data centers..

The transformer and PCC is designed for Full load of the Plant.But in operation Both the transformers/ Incomers will be kept on with tie breaker off.Each of the transformer is partially loaded

In case of emergency ,transformer maintenance or failure, tie breaker will be made on and one transformer will feed all sections of the load.

Generally, parallel operation of two transformers is avoided , as otherwise the short circuit capacity of the switch gear ,PCC and down stream Switch gear to be increased.

It is a practice to have interlock the three breakers (2 incomers and one Tie ) such that only any two breakers can be switched on.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Tie Breaker Used In Power Control Center Arrangement

01/11/2011 3:23 AM

That is quite correct. GA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

kvsridhar (2); kwcharlie (1); ramvinod (1); Tornado (1); vijaymail_electrical (1)