Application of Earth Leakage Relay

06/25/2011 3:20 AM

I am very much interested to know the application of ELR 300-500mA to attach to the Main Distribution Board of 2500A 3Phase 4 Wire, 415V 50Hz Capacity.

Is this ELR suitable to be used with the 2500A 3P/4P ACB?

The incoming cables are TOO large for the Core Balance CTs (aka Zero CT)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jun 2011
Posts: 10
#1

Re: Application of Earth Leakage Relay

06/25/2011 5:02 AM

Use ACB with ELR built in function Schneider ACB with 7.0A release

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 12
#2
In reply to #1

Re: Application of Earth Leakage Relay

06/25/2011 6:54 AM

Thanks for the promptly reply.

Is the system workable of 2500A 3p ACB with the 300-500mA ELR? Will the ELR being too sensitive for the system?

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 10
#3
In reply to #2

Re: Application of Earth Leakage Relay

06/25/2011 8:52 AM

It is very difficult to use the ELR with 300 -500mA for such high current breakers. what is the application. if load is directly connected to this then you can use ELR other wise setting required will be higher.

Here settings are available upto 30A in this release of breaker.

If you are using in panel as main breaker and downstream there are multiple outgoings then use earfault at I/C and ELR at breaker close to load.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 12
#4
In reply to #3

Re: Application of Earth Leakage Relay

06/25/2011 9:09 AM

in accordance to the authorities requirement in Abu Dhabi.

The upstream LV Main Distribution Board is required to configured with ELP 300-500mA, though we have explained to the officer that ELP 300-500mA for main incoming is too sensitive and it will not workable.

And it is now we are offering only OC/EF installed as the more practical protection.

The Main Distribution Board is cascaded for the Power Distribution in accordance to the designated Fault Level required for Icu, Ics, and configured with the branching outgoing ACB, MCCB respectively.

Therefore, we would like to know seek the professional comments from the team whether the ELR is practically configured to the Main Distribution Board in this case.

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#5

Re: Application of Earth Leakage Relay

06/26/2011 4:10 AM

Simple solution is to use earthleakage protection built-in the ACB. IN Schneider , i think its micrologic 7.

else u can use a rectangular sensor (cbct) with the ELR.

the rectangular cbct comes in different sizes . u chose them according to your breaker rating and cable size.

the elr has a wide range from 30mA to 30A with instantaneous and time delay tripping.

u can check schneider website and search for RH99M relays .

__________________
shamith gambhir, electrical engineer
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 12
#6
In reply to #5

Re: Application of Earth Leakage Relay

06/26/2011 4:30 AM

Thank you for proposal,

may i know what is the best made, model best fit for the 2500A MDB with 3Phase 4 wire system.

1. For Cable Entry

in order to fit the Core Balance CT with the 12 nos of the 630mm2/1C XLPE cable, i think we have to use the large enough CTs for it.

2. For BusDuct

Possible to use separate CTs for each phases+neutral? Or it is still require to use only the square CT.

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#7
In reply to #6

Re: Application of Earth Leakage Relay

06/26/2011 4:51 AM
__________________
shamith gambhir, electrical engineer
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 12
#8
In reply to #7

Re: Application of Earth Leakage Relay

06/26/2011 5:07 AM

Thanks for the input.

it seems like i have got TWO options on only with

1. NW25H14D2AH with Micrologic 7.0A (selective + earth-leakage protection.)

OR

2. the ACB with external ELR RH99M with Rectangular CTs

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#9
In reply to #8

Re: Application of Earth Leakage Relay

06/26/2011 5:25 AM

whats 4D2AH in NW25H14D2AH. i dont know the exact part no. NW25 is right . but H1 or H2 will depend on yo KA requirement .if you are in abu dhabi then contact schneider customer care (7099333).

__________________
shamith gambhir, electrical engineer
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 12
#10
In reply to #9

Re: Application of Earth Leakage Relay

07/05/2011 11:51 PM

Dear Shamith

NW25H1 = 2500A NW series ACB

4D2AH:

4 = 4 Pole

D = Withdrawable

2A = Micrologic 2.0A

H = Horizontal Connection

Only NW63 with vertical connection

Register to Reply