What is the allowable vibration in electric motors?
Any comments/suggestions??
you need to go, to get something
Good Answers: 181
Re: vibration in electric motors
08/03/2011 2:30 AM
Contacting the manufacturer is the only reliable way to find out. If you have got vibration I would suggest you do so quickly.
Good Answers: 67
08/03/2011 4:51 AM
Its a blunt question, without giving the size/capacity or type of foundation or balancing quality which are necessary to determine allowable vibration. So I shall answer assuming for the most likely.
A motor below 300 W capacity with rigid foundation can have acceptable vibration value up to 4.5 mm/s. However, for new motors it is advised to be under 1.8 mm/s.
Refer ISO 10816 for pedestal vibration and ISO 7919 for shaft vibration depending on requirement to find applicable limits.
Good Answers: 170
Re: Vibration in Electric Motors
08/03/2011 10:26 AM
Please refer to Table-1 of IS 12075
08/05/2011 1:31 PM
Pl. provide the table - 1 of IS 12075. WE ALL WILL BE BENIFITTED.
tHANKS,
RAJESWARI.
08/25/2011 6:24 AM
IS 12075 is available in the following link. You can download it for free
http://www.ziddu.com/download/11358867/3...5.pdf.html
sharath
Good Answers: 244
08/03/2011 9:58 PM
Refer to IEC 60034-14: "Mechanical vibration of certain machines with shaft heights 56 mm and higher - Measurement, evaluation and limits of vibration", Section 8.1, Table 1
The allowable vibration depends on the motor mounting condition and the shaft height:
For the rigid mounted case, the allowable limit is 2.8 mm/s
For the free suspension case, the allowable limit is 1.8 mm/s for shaft height 56 mm to 132 mm, 2.8 mm/s for shaft height 132 mm to 225 mm and 3.5 mm/s for shaft height greater than 225 mm
- MS
08/22/2011 5:25 AM
Article for Vibration analysis and remedy: click here
http://www.brighthub.com/engineering/electrical/articles/122952.aspx