Please have a look at the attached single line diagram and give your comments.
The gensets and transformers are within 15m of the genbus panel.
All the earths will be bonded. Only one (Set at priority 1) genset will be earthed at the star point and the neutral & earth bars will be bonded at the genbus panel.
Myconcern is the prospective earth fault at the step up transformer, would it help if we installed a "Restrictive earth fault CT" on each transformer star point which will in turn shunt the transformer LV ACB's.
Any other protection options?....