What should be fault carrying capacity of grounding electrode for a short period of one second for three phase 100 KVA Diesel Generator
Re: Fault Current Calculation
11/22/2011 12:00 PM
British Standard 7671.
Good Answers: 170
11/22/2011 9:03 PM
Vide IS 3043, the maximum permissible current density at the surface of an earth elctrode is :
{(7.57 x 10power3) / (Root [Rho x t])}
where, Rho is the earth resistivity where the earth electrode is buried and t is the duration of fault.
Now, can you please calculate the electrode surface area required for your application - yourself?
11/23/2011 12:06 AM
Amplitude of fault current plays any part along with duration of fault current?
11/23/2011 4:49 AM
I-squared-t.
Good Answers: 170
11/23/2011 5:30 AM
Fault current divided by the permissible current density will give the required cross section of the electrode surface.
11/23/2011 9:23 PM
For better calculation of the fault current,we need to know the contact voltage and the loop resistance.If=Ue/Rsch, where If is fault current,Ue is contact voltage and Rsch is loop resistance.