This is possibly a simple question to an electrical engineer but I am not an electrical engineer :)
I need to calculate fuel consumption rate per day for a diesel generator. The information I have are electrical loads in A and the fact that the generator will be 550KVa.
Can anyone tell me how to calculate this?
Re: Calculate Fuel Consumption per day for Diesel Generator?
03/15/2012 1:45 AM
03/15/2012 2:25 AM
03/15/2012 2:42 AM
Engine manufacturer offer curve indicating %engine loading Vs fuel consumption in grams/BHP. Optimal engine loading corresponding to best operating point is desirable for energy efficiency. Value around 160 g/KWH is best known.
as you have the loading data you can measure fuel consumption by dip level or flow meter. and put it on specific fuel consumption chart.
04/21/2017 1:29 PM
Nice but is % percent loading is in KVA or KW ?? By the mean of % from KVA or % from KW???
04/21/2017 1:50 PM
Mogtaba, you are replying to a post from 2012, look right under the title of the reply you just replied to, 3/15/2012. Most of these people are not watching this thread anymore, in fact many of them are not here anymore.
If you want answers, start a new question. See my earlier post in this thread on how to do that. http://cr4.globalspec.com/comment/1203342/Re-Calculate-Fuel-Consumption-Per-Day-for-Diesel-Generator
03/15/2012 4:28 AM
Dipstick (no offence).
Good moaning!
Re: Calculate Fuel Consumption Per Day for Diesel Generator?
03/15/2012 10:34 AM
The information you provide is not adequate for any real determination of fuel consumption. Generator load; type of generator; operating environment of generator; overall condition of generator (old/new) and many other factors are involved.
Not everything can be answered by manipulation of a mathmetical formula.
Call the manufacturer of the generator.
If you don't have a generator, the tables provided are more than adequate.
03/15/2012 2:00 PM
Daily fuel consumption cannot really be calculated but it of course can be measured. The wear and tear of the diesel engine, temperature of the engine environment, the quality of the fuel, combined with the varying load of the electric circuits will change the consumption rate constantly. Now one can make a reasonable estimate by using the generator manufacturer's fuel consumption versus electric load curves and estimating the electric power usage one will nominally be consumed in a day.
03/15/2012 9:19 PM
you need to calculate diesel consumption based on the weight of diesel Not Volume in Ltr or Gallan ISO method,You will get Misleading fig if you measure Volume.as the Volume changes with Temperature(Volume increase with Temperature)
03/16/2012 1:27 PM
Dear Mr. Duffem,
It is calculated on the BASIS of SPECIFIC FUEL CONSUMPTION and 0.28 Lb./BHP is the STANDARD at near FULL LOAD. At Partial Load - the Diesel Consumption will be high.
This topic raised few times and you will find quite a lot response from CR4 MEMBERS, from the Link given below:
http://cr4.globalspec.com/search/sitesearch?do=show&sort=textmatchrank&srch=Diesel%20Consumption&order=asc&Pg=1
I have also responded earlier and the Link is:
http://cr4.globalspec.com/comment/699643
dhayanandhan Power-User
Join Date: May 2008 Location: CHENNI, TAMIL NADU, INDIA. Posts: 316 Good Answers: 1
22
Find in discussion
Re: Calculating Consumption for a Diesel Generator 02/27/2011 4:33 PM
Dear Guest,
The Diesel Consumption depends upon the Efficiency of the Engine and Generator. An efficient and GOOD set/system will have a Diesel Consumption of 206.28 gms/kW.Hr. as SPECIFIC FUEL CONSUMPTION at FULL LOAD.
At 75% FULL LOAD the same good DG SET will have a SPECIFIC FUEL CONSUMPTION of 205.9 gms/kW.Hr.
At No-Load the Diesel Consumption will be 10 to 10.2% of the Full Load consumption. Adultered Diesel will not fit in to this band, which will be less in CALORIFIC VALUE.
We should always try to run the set at Full Load or near Full Load in order to achieve best Fuel Economy.
A similar question appeared in this Forum about 6 months back and you can search in this Forum and many CR4 Members responded with their comments. In that Forum you will find that the Specific Fuel Consumption in FPS unit as 0.28 Lb/H.P.Hr (since I studied in FPS SYSTEM) posted by me.
Thanks,
DHAYANANDHAN.S
Safety - Hazmat - New Member Engineering Fields - Mining Engineering - New Member Engineering Fields - Construction Engineering - New Member Hobbies - Hunting - New Member
Good Answers: 12
03/20/2012 1:32 AM
You can always put a meter on the fuel line.
John J Baker
03/20/2012 9:17 AM
But what if the fuel system recirculates back to the fuel tank?
Good Answers: 12
03/24/2012 2:00 PM
There are several models out there that can be used. The gen-set we used at one site I had to hook up a meter that could handle a fuel recirulation system. It's a pretty standard set-up.
John J Baker
12/29/2016 5:26 AM
See #4⇑.
Good Answers: 12
04/20/2017 10:56 AM
Not practical if you need to gauge fuel consumption. Either for economic or environmental regulations.
But I guess you could if you want to station some poor sap in a gen-set during operations. ��
John J Baker
01/03/2024 7:58 AM
Invitation declined.
Good Answers: 75
03/29/2012 3:59 AM
Ok, if we combine duffeyem's two original posts he's asking for the fuel consumption per day and in litres per kWhr for a 550 kVA diesel generator set and the fuel consumption per kWhr. Referring to the table of fuel consumption rates for DGs that has been quoted several times now in both threads. Now in the chart they quote generator sizes in kilowatts kW but normally generator sizes or capacities are stated in kilovolt Amps kVA so I will assume that they mean kVA where they state kW. The reasons for this will become obvious later.
Unfortunately the table doesn't state the figures for a 550 kVA generator so I took the figures for the 500 kVA and 600 kVA and averaged them to get a starting point for a 550 kVA DG as quoted in one of duffyem's threads.
I then extrapolated the results to get the table shown below.
You will notice that there are four columns at the right of the table that contain the figures duffeyem asked for with the left two columns being preceded by a greater than symbol ≥ and the right two by a less than ≤ symbol. Now the problem is that we don't know the power factor so the left two columns contain the fuel consumption in millilitres per hour per kilowatt hour ( ml kWhr-1 ) and litres per day ( l day-1 ) for a power factor of 1.00. However, in the real world it is for all intense and purposes impossible to have an AC load that has a PF (Power Factor) of 1.00 so I have included figures for a PF of 0.85, which is probably the worst PF you would expect to come across without having some sort of PF correction, in the last two columns on the right.
Unfortunately duffeyem didn't elude to the actual load either so to make things simpler I have taken the figures above for fuel consumption per day and fuel consumption per kilowatt hour and plotted them on two charts.
The first chart show the fuel consumption in litres per day ( l day-1 ) for a PF of 1.00 in BLUE and a PF of 0.85 in RED over a range of loads from 25% all the way up to 100% for a 550 kVA DG
The second chart shows the fuel consumption in millilitres per kilowatt hour ( ml kWhr-1) for a PF of 1.00 in BLUE and a PF of 0.85 in RED for a 550 kVA DG
The interesting thing to note about this chart is that the fuel consumption per kWhr is lowest when the DG is running at around 75% load. If you think about it this makes sense as the efficiency of internal combustion engines peaks at about 75% load.
Now I believe that's about as detailed and accurate answers to duffeyem's questions in both threads that is possible given that we do not have sufficient data to give more definitive answers. If duffeyem or anybody else has any further questions then please don't hesitate to ask.
Good Answers: 19
03/29/2012 9:19 AM
WOW. Excellent extrapolation of limited data from the OP with good knowledge of the electrical load and engine-gen operating factors.
May I steal, plagarize, or otherwise make use and/or quote this post?
Good Answers: 75
03/29/2012 9:27 AM
Please feel free to do what you would like with it. If you would like a copy of the Excell spreadsheet send me a personal message with you eMail address and whether your running the 2010 version of excell and I'll send it to you.
05/22/2018 7:33 AM
Good day Mr Masu, please i would like to have your contact details so we can chat and i ask some questions. i have been working on fuel consumption per day for diesel generators and i am having some challenges. I came across your reply on this page and i liked it. thanks so much
Good Answers: 75
06/04/2018 4:57 AM
Hi redsinclaire,
As you can see from the date on the post this discussion was some 6 years ago and unfortunately all the charts, diagrams, calculations, and spreadsheets have now been deleted from the CR4 database which makes it difficult to replicate my train of thinking. I do keep nearly all my research into CR4 posts which is considerable, but I’ve also replaced my computer and moved to a new house some 1,500 km away (Australia is a big place), so I don’t know if I can find my original data.
Nevertheless, I’ll have a look and see what I can find, but as this is basically a cold thread I suggest that you contact me directly using CR4’s Personal Message system, that way we can pontificate to our heart’s content without upsetting everyone else with a plethora of notifications they really don’t want to receive. In the end we can always post our final findings without all the intermediate searching and belly button contemplation.
09/07/2014 7:56 PM
Hello there,
i really appreciate your solution to the above problem '' Diesel Generator foel consumption''.
Email Removed - CR4 Admin
Can i have excel sheet for the fuel consumption estimate. thanks
04/20/2017 5:01 AM
Dear friends,
My name is mogtaba. I freshly graduated as an electrical engineer & not I am working in a mining co. The load is supplied by 2 KVA perkins diesel generator working at low power factor (0.67-0.72). I am wanted to connect power factor correction but Unfortunately transmission lines and transformers are already connected & I can't take the advantage of reducing equipments capacity due to economical reasons. I am interested in power factor correction because I want to reduce fuel consumption.
I am asking about the relationship between fuel consumption and power factor correction (KVA & KVAr reduction) or fuel consumption vs % loading ?
In the diesel generator manual fuel consumption and % loaded relationship is shown but I am confused if the % loaded is in KVA or in KW ?.
Does power factor correction reduce fuel consumption significantly (ex: >15% )if its corrected from 0.72 to 0.95.
Hope you can help :)
04/21/2017 8:37 AM
You posted this on a thread that is 5 years old, nobody is going to see it. Start your own thread and you may get results.
Click the "Ask a Question" on the right side of the CR4 home page, and put your question there.
04/21/2017 1:53 PM
THX
05/15/2012 6:37 AM
hello duff, this is the way i help you to your problem check this out !http://www.dieselserviceandsupply.com/Diesel_Fuel_Consumption.aspx
keep up the good work guys
i want ot helf piple need assistance and to share my knowleged in technical
Good Answers: 75
05/16/2012 6:52 AM
Dear toink,
You really need to read the posts in a thread before diving in head first with an answer. If you had you would have noticed that the exact link you posted was previously quoted in post #1 of this thread by SolarEagle two months ago and since then has been discussed extensively in this thread.
06/29/2012 2:09 AM
calculate fuel consume as per diesell power generator. good fuel saving generator are reduce fuel and give maximum power consume.
Generator on rent
12/09/2014 8:30 PM
07/08/2024 5:15 AM
Intervals between purchases and volume purchased are two pieces of data that can, over time, produce an average consumption rate.