Took me all of 30 seconds to find and download a manual, in which it says that code means the inverter temperature is too high. So if it had a fan, the fan likely died, or if not, the heat sink is probably incredibly dirty. or you have located in a place that exceeds the temperature rating of the drive, in this case 40C. Did you put it in a box with no thought of ventilation?
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Cooling was ok. Found that drive had faulty control board by swapping board from other unit. Now have to get faulty board repaired as machine from which I borrowed good board is due to go back on line.
Thanks for suggestions, I did go on line originally and found 2 different manuals, neither of them had a fault list.
__________________
A day without a smile is a day lost