Underground Cable Laying

08/28/2012 7:47 AM

Dear all.

we are involved in a project of laying underground cables. we planned to lay trefoil arrangement. we have to lay two cables in the same trench. can anyone give me a clue whether any minimum distance requirements in laying trenches.??

if so kindly let me know where i can get the data.

I referred to IS 1255 & 62087 but i couldn't find any data which can solve my issue.

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#1

Re: Underground Cable Laying

08/29/2012 12:32 AM

It should be available in IS 1255. The minimum horizontal distance (axial spacing)between two trefoil formations should be 150 mm.

Register to Reply
Participant

Join Date: Sep 2011
Posts: 1
#2
In reply to #1

Re: Underground Cable Laying

08/29/2012 4:07 AM

In most construction areas, the horizontal distance between trefoils is equal to the diameter of the cable.

Register to Reply
Active Contributor

Join Date: May 2012
Posts: 14
#4
In reply to #1

Re: Underground Cable Laying

08/31/2012 1:06 AM

aup mate...thanks very much.. is there any theoretical way of proving the same..??

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Underground Cable Laying

08/29/2012 9:40 AM

Have you read IS 1255 thoroughly? It is very much given in IS 1255. Please refer to the figure (in page 28) below Clause 8.8.5. It very clearly shows that there shall be a horizontal distance of not less than 2D between two trefoil fomations of three single core cables. It also recommends the transposed arrangement in such a case. Please do read Standards thoroughly.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2012
Posts: 14
#5
In reply to #3

Re: Underground Cable Laying

08/31/2012 2:01 AM

Thank you mate.. your reply was very helpful to me...thanks again

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); electricalexpert65 (1); naanee09 (2); Spartacuz (1)

Previous in Forum: Hydropower Plant 2*1650 kVA   Next in Forum: Ultracapacitor to Recharge My Laptop?

Advertisement