Starting Current Star/Delta Starter

11/14/2012 11:32 PM

A 400v 3 phase motor is started with a DOL starter.

When started the motor draws 90A and produces 200% full load torque.

Whats the starting current if the same motor is started with a star/delta starter?

i know the

i have to x the current by something but im sure

90 x ?? =

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: starting current star/delta starter

11/14/2012 11:45 PM

30A. The starting torque will be correspondingly less, and the motor will take longer to attain full speed. (If it can actually start.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Sep 2010
Posts: 4
#2
In reply to #1

Re: starting current star/delta starter

11/14/2012 11:55 PM

That what im after but how did you get this answer? 90 x 0.33? where does 0.33 come from?

Register to Reply
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: starting current star/delta starter

11/15/2012 12:03 AM

I'll have to recheck. I think it may be 1/√3 for starting current (~52A), and 1/3 starting torque.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
2
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#8
In reply to #3

Re: starting current star/delta starter

11/15/2012 11:27 AM

I also agree with Mr Tornado i-e Starting current will be approximately 52 A. It is either 10 KW or 7.5 KW motor

Rewriting the Question

1.A motor 10 KW, 400 V, 50 Hz, D, 19 A, P.F 0.86, 1450 rpm, when connected in Delta configration takes starting current of 90 A.

How much starting current would it take if it is connected in Star Configuration and 400 V are applied to it

a).When Motor is Connected in Delta Configuration and 400 V are applied:

Starting Current in case of Delta Configuration : 90 A

During Starting Motor takes 473 % of its rated current : 90/19 = 4.736

Motor other Parameters

Mechanical Power : 10 KW

Full Load Current : 19 A

Motor Full Load Torque = 65.9 N.m

b).When Motor is Connected in Star Configuration and 400 V are applied:

Mechanical Power : 3.33 KW (Approximately 1/3 * 10 KW)

Full Load Current : 10.97 A (Approximately / 1.732)

Motor Full Load Torque = 21.966 N.m (Approximately 1/3 * 65.9)

c).From 400 V Delta configuration to 400 V Star Configuration:

Mechanical Power : Reduces from 10 KW to approximately 3.33 KW

Full Load Current : Reduces from 19 A to approximately 10.97 A

Motor Full Load Torque = Reduces from 65.9 N.m to approximately 21.966 N.m

d). Starting Current for 400 V Star Configuration :

When the motor in Delta Configration starting current was approximately 4.736 times the rated current (4.736 * 19 = 90 A)

Starting current for motor in Star configration for 400 V will be approximately 4.736 * 10.97 = 51.95 A

2. For 7.5 KW, 400 V, 50 Hz, D, 14.6 A, P.F 0.85, 1450 RPM

Starting Current in case of Delta Configuration : 90 A

During Starting Motor takes 616 % of its rated current : 90/14.6 = 6.16

When Motor is connected in Star Configration Current will be : 8.429 A

So starting current for 7.5 KW in Case of Star Configuration: 8.429 * 6.16 = 51.92 A

http://cr4.globalspec.com/thread/54100#comment562035

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: starting current star/delta starter

11/15/2012 3:53 AM

It is the load that presents the torque to the motor. A motor consumes the same starting current whether it is unloaded, fully loaded, or any shade of grey in between.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 67
#5
In reply to #4

Re: starting current star/delta starter

11/15/2012 8:19 AM

motor will take 1/√3 times starting current in star as compared to delta

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: starting current star/delta starter

11/15/2012 8:36 AM

That bit is true.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Starting Current Star/Delta Starter

11/15/2012 9:58 AM

33% starting current, 33% starting torque. But on transition, there will be a current surge that can potentially be upwards of 2000% of FLC, albeit very briefly.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply