Dear All

Is it possible to run the electrical cable parallel with instrument 100 apart.

both cable are armoured any interference.

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Electrical and Instrument cable

05/11/2013 10:09 AM

Yes.

Yes.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Electrical and Instrument cable

05/11/2013 11:13 AM

100 what? Mm? Cm? Meters? kM? Inches? Feet? Cubits? What do you mean by armored? Does that mean shielded?

Do you feel that you are qualified to be making these kinds of decisions if you must ask those kinds of basic questions? I'm not trying to be rude, but it appears as though you are not an electrical engineer and are trying to set up something rather complex (instrumentation) without even the most rudimentary knowledge necessary. That means that if we help to facilitate this, someone may get hurt. Hire a qualified electrical engineer please.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Electrical and Instrument Cable

05/11/2013 10:32 PM

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Electrical and Instrument Cable

05/13/2013 12:17 AM

If I well interpreted these sentences no distance is required from power cable[low voltage] if the ITC cable is armored. However the armor has to be well grounded[see NEC Art.250].

According to NEC Art.727.2 Definition.

Type ITC Instrumentation Tray Cable. A factory assembly of two or more insulated conductors, with or without a grounding conductor(s), enclosed in a nonmetallic sheath.

Art.727.4 Uses Permitted.

(7) Direct buried where identified for the use.

Art.727.5 Uses Not Permitted

Type ITC cable shall not be installed with power, lighting, Class 1 circuits that are not power limited, or non-power-limited circuits.

Exception No. 2: Where a metallic sheath or armor is applied over the nonmetallic sheath of the Type ITC cable.

__________________
Julius
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Electrical and Instrument Cable

05/13/2013 8:08 AM

As per IS 1255, the minimum clearance should be 300mm.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6
In reply to #5

Re: Electrical and Instrument Cable

05/14/2013 3:05 AM

I did not find in IS 1255/83 ch.6.3.3 " Clearances" a reference to the minimum desired clearance between power and instrument cable (laid in ground).Control cable is not an instrument cable and-with some exception-control cable in Switchyard-is not shielded or armored.