We have the diesel genset of 82.5 KVA (0.8 pf) at height of 4000m with ambient temp. of surrounding to be around 18°C.
On interpolation,I found the derating factor at that altitude and temp. to be about 0.85.
Using derating factor,the actual genset required for the same output is found to be 97.06 KVA (82.5/0.85).Is the calculation correct?
The nearest genset available is 100 KVA.Should we go for 100 KVA rating? Can the genset be started where air density and pressure at such altitude is very low?Even if the genset is started,can it be problem free from overheating?
Since use of derating factor shows the loss of power.Does it means the decrease in efficiency? Does the efficiency of any machine vary with altitude or is constant during design?