Transformer Tripping Problem

06/27/2013 4:01 PM

What are the causes of tripping of 132\33kv tr. through diff. relay with the tripping of any 132 kv trans. line each time.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: TR tripping problem

06/27/2013 4:06 PM
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: TR Tripping Problem

06/27/2013 9:38 PM

So your transformer trips every time any transmission line attached to it also trips? You haven't supplied any of the important information like a single line diagram, the size and connection type of the transformer, or the type of breakers and relays, loading, etc. making it a bit tough to be precise.

Absent all that information (and more) I'd say that your CTs may not be matched closely enough, the breaker interpole opening times are too great, or the relays aren't set properly. There's a lot more to look at, loose connections, polarities, etc., especially since it's so consistent. You might also consider getting someone out there who knows what they're doing.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#3

Re: TR Tripping Problem

06/28/2013 3:15 AM

Differential protection is an unit protection and should remain stable for faults outside the measuring zone. Assuming the power flow is from 132 KV side, the relay should not even sense any fault unless the fault lies insider the zone CT's. For 2 way flow of power or grid interconnected system, the relay should sense it as a through fault and remain stable. All the points mentioned by RAMConsult to be checked. Carrying out stability checks in offline mode involving all the CT's, 132/33 kv transformer etc., will confirm whether system requirements of zone protection scheme are met. You will need the services of an experienced power systems commissioning engineer to trouble shoot the problem.

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#4

Re: Transformer Tripping Problem

06/28/2013 6:23 AM
Register to Reply
Power-User

Join Date: Feb 2005
Posts: 255
Good Answers: 2
#5

Re: Transformer Tripping Problem

06/28/2013 9:42 AM

gb477 has provided additional information-

Referencing previous post regarding transformer tripping through differential relay-(MAKE-SIEMENS 7UT) TR. NAME -BHEL INDIA RATING-80 MVA 132\33kv power tr. CTR-132kv 800\5A 33 kv 1500\5A Max load 55MVA TR. DGR. STAR- DELTA Addl. info. 132 kv grid system.4 nos. line. 3 nos trs in parallel rating 80MVA SIEMENS MAKE and 50MVA BHEL MAKE TWO BUS SYSTEM ONE MB AND TB

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); lyn (1); Paddy O'Flanigan (1); Pattabhiraman (1); RAMConsult (1)

Previous in Forum: Equation for ANSI 37.42 K Type Maximum Melting Curve   Next in Forum: Need a Variable Frequency Controller

Advertisement