Determination of Transformer Rating

07/15/2013 11:51 PM

I have been given a project to determine the transformer rating of a distribution transformer after adding cooling fans to it. I have all the nameplate rating of the transformer as well as the cooling fan model and rating. I am not sure how to get on with it.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#1

Re: Determination of transformer rating

07/16/2013 12:16 AM

Contact the transformer manufacture.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Determination of transformer rating

07/16/2013 12:20 AM

Have you:

1. Assured that the transformer is real???

2. Contacted the manufacturer of the transformer?

2. Asked the person who gave you the assignment?

3. Nameplate?

4. Etc. Etc. Etc.

The transformer exists? And someone wants to add fans??? And wants to know what?? The "rating"?

This isn't homework is it?

Temperature Rise and Transformer Efficiency - Copper ...

Current transformer - Wikipedia, the free encyclopedia


K-Factor Defined

K Factor Chapter 3 - Federal Pacific

Where have you looked so far?

Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 13
#9
In reply to #2

Re: Determination of transformer rating

07/16/2013 11:17 AM

Yes I have assured all your questions. I have to gauge transformer capacity based On additional fans!he said the transformer rating might have increased to 13.33 mva from 11 mva but he is not sure about it and wants me to find out

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Determination of transformer rating

07/16/2013 11:39 AM

<resubscribes>

Well, on what design basis were the fans installed and on what basis was the necessary expenditure approved?

Is the wiring and are the circuit protective devices each side of the transformer suitable for the proposed increased duty?

Is there an Electrical Engineer on site that could answer the question?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 13
#15
In reply to #10

Re: Determination of transformer rating

07/16/2013 1:11 PM

The fans are already installed. The transformer is working at some higher rating and I have to determine that increased rating.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18
In reply to #15

Re: Determination of transformer rating

07/16/2013 3:55 PM

Measure its amperage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#28
In reply to #10

Re: Determination of transformer rating

07/17/2013 8:50 AM

PW: I will answer your questions, because telepathy tells me the answers!

1. The transformer ran out of capacity, so they want more and had to do something. Fans were cheaper than a whole new transformer.

2. Maybe not, but due to budget contraints the approach will be to run them until thermal failure.

3. No.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#33
In reply to #28

Re: Determination of transformer rating

07/18/2013 10:27 AM

Good guesses.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Determination of transformer rating

07/16/2013 12:21 AM

I imagine you could gain only 5-10% above its existing rating. It will depend on the air flow arrangements more than on fan model and rating.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#4

Re: Determination of transformer rating

07/16/2013 12:23 AM

I think, your boss asked you to get the Transformer rating in AF condition. Look at the name plate . For eg;- AN/AF - 1000/1500KVA

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#41
In reply to #4

Re: Determination of transformer rating

07/30/2013 12:04 AM

I have come across transformers of French make rated 6MVA w/o fan & 9MVA when fans are switched on.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Determination of transformer rating

07/16/2013 3:05 AM

Simple. Load it up until smoke comes out, then reduce the load by 25%.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Determination of transformer rating

07/16/2013 3:46 AM

At least the new fans will blow the smoke away!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Determination of transformer rating

07/16/2013 3:56 AM

Seriously, on what basis was the expenditure on additional fans justified? For some reason, rather than replace the transformer with one of a different, known, rating, the project concept was based on adding fans to the existing. That calculation will exist in the scheme upon which the investment was authorised. It is rather surprising that at this late stage in the project, the basis for fans rather than replacement has been forgotten/put in a drawer/shelved/filed rather than being available for review.

So start digging through the project paperwork. It will be in there somewhere. Good luck with the search.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Determination of Transformer Rating

07/16/2013 11:17 AM

You have not provided enough information. What type of transformer is it, what is its cooling/insulation system, what are its ratings, what type of enclosure is it in, where is it located, what are the existing cooling arrangements, are there fins, radiators, oil pumps, etc., etc.

The best you can do now is estimate the amount of air flow your fans can provide, then determine the amount of heat removal possible and consequently the temperature drop.

Typically, and depending upon all of the above missing information and more, a transformer gets derated 1% for every degree C above its rating. So if its nameplate without cooling is 30°C above ambient and you can somehow lower its temperature by 5°C then you will have increased its rating by 5%.

But be forewarned, there are places in some types of transformers (solid insulation in particular) known as hotspots that may never get the benefit of the added cooling and will cause premature failure and/or accelerated loss of life. Unless it was designed for additional cooling, your "bunch of fans" approach is a short term solution to what was undersized/mis-specified/under-rated to begin with. Use this "borrowed" time to order a properly engineered replacement.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jul 2013
Posts: 13
#11
In reply to #8

Re: Determination of Transformer Rating

07/16/2013 11:40 AM

It is class OA transformer, Type SL,2000 kva, hv is 69kv n lv is 7.2/14.4 kv Temp is 55 deg C Since it is class OA its not solid insulation will the problem of hotspots matter? I read smwhere that by adding single bank of fans( m nt sure what that means) there is a 33% capacity increase. Do u have any idea on this?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: Determination of Transformer Rating

07/16/2013 11:43 AM

Hire a consultant. You are lost.

What does the controlling specification have to offer?????

You do have one, right?

Have you asked the supplier of the device, or, is that too easy.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: Determination of Transformer Rating

07/16/2013 11:44 AM

None here. The transformer manufacturer might, though. How did the phone call go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #13

Re: Determination of Transformer Rating

07/16/2013 11:57 AM

Surly you jest.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#19
In reply to #11

Re: Determination of Transformer Rating

07/16/2013 4:34 PM

Additionally to what others have said, hire a consultant to perform the design calculations and take the risk.

A 2MVA transformer is not a toy, if you are not qualified to perform the calculations and something goes wrong or someone gets killed the transformer warranty is void (for a start) and you will field the blame and possible jail time, not the person who tasked you to perform the work.

This type of work should be done, or at the very least approved and signed off by professional consultants. That's their job.

Additionally consult the transformer manufacturer for advice as there is no single magic number you should use.

Variations in transformer design, fan type and implementation, air flow, hot spots, internal transformer tank construction, local environmental conditions effecting air flow and heat dissipation, transformer uprating reliability analysis, site location, etc mean that it is not as simple a task as you might think.

This is why transformers with fans can look quite different than transformers without fans from the same manufacturer, and why careful design analysis is necessary when making these type of changes to expensive distribution level transformers.

Jack - Actually working in the relevant industry.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#20
In reply to #11

Re: Determination of Transformer Rating

07/16/2013 8:41 PM

Huh? Just a while ago it was 11 MVA (or 13.3); now 2000 kVA (= 2 MVA)?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 13
#21
In reply to #20

Re: Determination of Transformer Rating

07/16/2013 9:21 PM

There are two transformers of different ratings

Register to Reply Score 1 for Off Topic
Anonymous Poster #2
#35
In reply to #21

Re: Determination of Transformer Rating

07/19/2013 5:54 AM

...and you wait until now to tell us? Sheeeesh.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#16

Re: Determination of Transformer Rating

07/16/2013 2:30 PM

A type OA transformer is oil (O) filled and air (A) cooled, and in both cases, no mechanical means are used to move either fluid (no pumps, no fans), instead relying natural cooling via convection, conduction and radiation.

The rated rise and hotspot temperatures are the most important operational numbers for you to follow once it is loaded to its nameplate MVA and temperature. Unless you read that 33% in the manufacturer's literature the best you can do is 15% (according to Westinghouse product sheets) and still be within the factory limits, after that you're on your own, taking years off of the expected life as you exceed the temperature/loading limits.

Sorry to say but when you said "...( m nt sure what that means)..." you indicated that this task is not for you to handle. Follow the advice of the other posters and ask your management for some professional help.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2013
Posts: 13
#17
In reply to #16

Re: Determination of Transformer Rating

07/16/2013 2:52 PM

By saying ' m not sure what that means' I was talking about single bank of fans regarding their rating or air flow.can you tell me the site where u got the product sheets?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#22
In reply to #17

Re: Determination of Transformer Rating

07/16/2013 9:26 PM

Sure, Google on your own words, "class OA transformer, Type SL,2000 kva", from your previous post.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#23

Re: Determination of Transformer Rating

07/16/2013 10:54 PM

In the UK there used to be a children's television program call Jackanory. Fanciful stories for children.

I think we've found out what happened to it.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Active Contributor
Engineering Fields - Electrical Engineering - New Member

Join Date: Mar 2013
Location: Papua New Guinea
Posts: 10
#24

Re: Determination of Transformer Rating

07/17/2013 12:16 AM

Hi AKP

The tranformer rating is what is shown on the name plate. To determine the loading on the transformer after you added the fan, you measure the current or power using a power meter with clamp on leads, or a data logger to find out the maximum power drawn. Take the measurements at various times so you can see when the maximum and minimum loadings occur. Compare the maximum current or power reading with the rating of the transformer to determine if the transformer is overloaded or has space to cater for more increase in load.

__________________
"Whatever your mind can concieve, and believe, it can achieve"...Napolean Hill
Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#25

Re: Determination of Transformer Rating

07/17/2013 12:25 AM

Is the Transformer primarily limited by thermal factors (heating/copper losses)? or by saturation?

If it is thermally limited, cooling may give you some additional output capacity, but contact the manufacturer for details.

If it is limited by saturation, no amount of cooling will give you any output gains.....

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#37
In reply to #25

Re: Determination of Transformer Rating

07/19/2013 9:07 PM

Actually the parameter that governs saturation is flux level, and flux level is determined by the voltage and frequency across the winding, not by the load current. A transformer that is unloaded but subjected to voltages greater than 1.15 (+/-, depends on the properties of the core material, its construction, etc.) times its rated voltage will be at the edge of saturation.

The core losses are constant upon energization and do not depend upon the load current; I²R losses are the load variable (copper) losses that we are talking about here.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#38
In reply to #37

Re: Determination of Transformer Rating

07/21/2013 7:30 PM

Is not the Flux 'Amp-turns'? - input current x primary turns.

Output voltage is input voltage x turns ratio - losses(copper, core)

Output current input current / turns ratio - losses

if the load increases, it means that the output current is increasing, therefore the input current is increasing, and yes the copper losses increase by the square of the current, but the flux also increases proportional to the current. which limit is reached first depends on the transformer design, and the margin built in.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#40
In reply to #38

Re: Determination of Transformer Rating

07/23/2013 10:45 AM

Ampere turns (AT) is the MKS unit of MMF, but Flux is measured in Teslas, they're different but related. It's a common misconception that winding current causes saturation of the core, but that's not the case for ordinary power transformers.

From the IEEE Fundamentals of Power Electronics Chapter 12: Basic Magnetics Theory pg. 30

"...Transformer saturation

• Saturation occurs when core flux density B(t) exceeds saturation flux density Bsat.

• When core saturates, the magnetizing current becomes large, the impedance of the magnetizing inductance becomes small, and the windings are effectively shorted out.

• Large winding currents i1(t) and i2(t) do not necessarily lead to saturation. If 0=n1i1+n2i2 (the numbers are subscripts) then the magnetizing current is zero, and there is no net magnetization of the core.

• Saturation is caused by excessive applied volt-seconds

• Magnetizing current depends on the integral of the applied winding voltage

•Flux density is proportional to a constant times the integral of the applied voltage

•Flux density becomes large, and the core saturates, when the applied volt-seconds are too large..."

The condition "0=n1i1+n2i2" is typical for power transformers since whatever current flows into the transformer is the same (as modified by the turns ratio) as the current that flows out. Notice that except for this equation, winding current plays no role, it is the applied voltage and frequency that governs the saturation.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Anonymous Poster #1
#26

Re: Determination of Transformer Rating

07/17/2013 1:56 AM

We also dont know how because we dont see any information infront of us...you say you have name plate info....we cant help if we dont see that info

Register to Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#27

Re: Determination of Transformer Rating

07/17/2013 8:45 AM

A lot has been said which is relevant, but it really is this simple:

Transformers have a nameplate rating, which you indicated you have. The rating will read something like (fictional example) 2000/25000/3000. The ratings mean something like: air/forced air/circulating oil - depending on the transformer.

For a transfomer that's nampeplate just says one value, and did not come with fans, then it is rated for air, and unknown for other forms of cooling. Anything that we come up with here will be an educated estimate based on knowledge of the workings of things. Not a rating. Rated means the transformer was designed and intended to work within specifications for that application.

There are many things that you can do to get more capacity out of the tranformer - but that does not mean it was rated for it. You added fans. You could perhaps put an oil circulation system on. You could install cold water sprinklers that constantly cool the transformer. You could build a building around it and install air conditioning.

However -still not "rated".

Estimates? I would estimate that you can run a transformer to 125% of its rated value without burning it up. I would estimate that by adding fans that move some serious air, you could get between 10-33% more capacity.

These things would depend on the fans, the air flow, and the configuration of the heat sink fins/fan installation. Wouldn't they? (Yes they would!)

Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 13
#29
In reply to #27

Re: Determination of Transformer Rating

07/17/2013 12:36 PM

Do you have any litreature that explains this estimation?

Register to Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#30
In reply to #29

Re: Determination of Transformer Rating

07/17/2013 12:41 PM

No, I do not. That's why it is an estimate (maybe even a "guess") on my part. - Not something that should be done lightly. If the estimate of the capacity is wrong, depending on any of the multitude of factors, the transformer will be damaged and significant unhappiness will occur.

If there was a specific formula to be used, it wouldn't be guessing.

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#31

Re: Determination of Transformer Rating

07/17/2013 1:29 PM

You can not rely on any of the "guesstimates" provided on this or any other forum, there are just too many variables in the actual design of the transformer to try and apply one person's experience to your situation.

Not mentioned previously is that the most critical element in cooling is the flow rate of the oil since it's providing the heat transfer from the windings/core to the radiators.

Unfortunately this transformer is rated OA, no pumps, no fans, everything relies on convection. Even worse, convection is a function of delta T, meaning that you need a large gradient from the from the bottom oil to the top oil temperatures, and this will negatively effect the hotspot temperature. Overall this means that even if you had enough fan capacity to keep the air temperature at ambient across the radiators, it would not do much to increase the natural flow rate through the relatively small oil passages embedded in the windings.

On the other hand, if there were oil pumps (OF) to circulate the oil, the heat transfer out of the core would be much greater, and the mixing action would result in a much lower gradient across the core/windings. Now the addition of fans (OF,AF) will result in incremental cooling, that combined might get you to 25-33% over the original rating. But only the OEM is knowledgeable enough to design such a modification and grant permission to do so.

If the transformer is relatively old and scheduled for replacement anyway, then go for it. If it's relatively new and still under warranty, then you must follow the manufacturer's rules or you will have a very expensive paperweight with no warranty coverage.

BTW- nothing comes without a price, all that extra capacity you're getting for "free" is being removed in the form of heat, and guess where that heat comes from, fuel that you pay for to convert into greatly increased losses in the transformer plus the fan and pump running costs.

Undersizing/overloading is a penalty you pay for 7x24x365, it's no different than putting a 100kW loadbank at the terminals of your metering equipment, not to mention all the economic loss of life in the transformer. TANSTAAFL is your guiding rule for real life systems.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#32

Re: Determination of Transformer Rating

07/18/2013 12:28 AM

If the transformer is built to ANSI or NEMA standards then the 11MVA would be 13.75 MVA fan cooled. Those standards state that a self cooled OA or ON transformer of that size will have a 1.25 % increase due to the addition of fans. The clinker is that the only way you can find out what fans to add and the catalog number is to go back to the manufacture of the transformer. They will charge for the fan package which will include fans and a new nameplate. If you add different fans, and quantities you will get different answers. A guess could be made that as long as you keep the same top oil temperature after fan addition and load increase, you might be all right, but you could exceed hot spot rating which is where transformers fail, the hottest spot in the winding. Since you cannot measure that unless you have an AWR guage (hot spot) installed. If you have that, go by that and make sure you don't exceed standards. If your transformer is built to other specifications, you must look up those specs. Many use the same 1.25 for fans but not all do.

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#34
In reply to #32

Re: Determination of Transformer Rating

07/18/2013 11:30 AM

I am going to correct myself. I really don't remember the cutoff point for the different levels of fan control. 10 MVA gives a 125% increase (sorry about the errant decimal) and 12 MVA gives a 133% increase. I don't have the standards in front of me right now and can't remember the cutoff for sure but I think it was 10001 KVA where the 33% increase occurs. If that is the case, the value would be 14.63 MVA. Also many manufacturers also can provide a total OA/FA/FA ratings with more fans going for a 66% increase. The nameplate should list the standards the transformer was manufactured to and you can look up those standards on the internet. The 2000 KVA unit will have only a 15% or 25% increase depending on what standards it was manufactured to. If you do not have an AWR device, which I doubt you do on the 2000 you really need to go back to the manufacter. Different types of windings have different hotspots and this is difficult to guess at. I spent a lot of years in transformer design and it is a complicated process to calculate a hot sport even when the design and build is accurately known. The hot spot is what will catch you.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#36

Re: Determination of Transformer Rating

07/19/2013 12:02 PM

Well in nothing else when this transformer burns up you will have a nice set of brand new fasn to put on your next new and properly sized transformer.

Just out of curiosity why is the old transformer not being replaced by a larger one and then re purposed to another location elsewhere that has a smaller transformer that is running at its limit?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#39

Re: Determination of Transformer Rating

07/23/2013 4:56 AM

Rather than change the transformer, wouldn't it be easier to go for modern high-efficiency lighting instead?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 41 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (2); akp (6); Alanvaderi (1); Anonymous Poster (2); Carl Pugh (1); jack of all trades (1); JCase (3); lyn (3); nick.mapun (1); pnaban (1); PWSlack (7); RAMConsult (6); tcmtech (1); TonyS (1); Tornado (3); WAWAUS (2)

Previous in Forum: Power Consumption of Geyser   Next in Forum: FCMA Soft Starter

Advertisement