03/26/2014 9:02 PM

Please share your experiences and tell me of any standard that needs to be followed: A sealed PVC cable conduit of a tank passes along the side wall of another tank's dike to the marshalling cabinet. For this to work, I would believe that the PVC cable must be fire retardant otherwise there will be big trouble if a fire were to occur in the tank dike that the cable passes through. There must be a standard somewhere that specifies these requirements but I don't know it. I want the contractor to ensure that the sealed PVC cable conduit is fire retardant. Before I do this, I want to make sure I am not making a fool of myself. Pls note I am not from I&C.

Register to Reply
Pathfinder Tags: cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Cable Conduit Requirement

03/26/2014 11:34 PM

It depends on the rating of the area.....such as mission critical shut down of equipment and fire safety requirements.....the materials being handled or processed will determine the area classification, then you need equipment that is rated for that classification....

http://en.wikipedia.org/wiki/Electrical_equipment_in_hazardous_areas

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Cable Conduit Requirement

03/27/2014 7:35 AM

As plastics go PVC has a high ignition temperature at 455°C.

May concerns would be whats in the pipe and what it feeds to. As safety equipment in the event of a fire.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Cable Conduit Requirement

03/27/2014 8:11 AM

There are pan-European and pan-North-American standards for the installation of electrical equipment in potentially explosive atmospheres. These standards are similar, though not the same, and the underlying principle behind the various techniques available is that the risks of the electrical installation causing fire or explosion are minutely low through the correct design, selection, installation and maintenance of the installation by correctly-trained persons.

If the correct training is not on board, stop work and delegate the task to someone who is correctly trained. The safety of the installation and everyone who works and lives on or near it depends upon taking this action.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#4

Re: Cable Conduit Requirement

03/27/2014 2:42 PM

Virtually all commercial wire and conduit meet a minimum fire tolerance.

This does not mean that a PVC conduit and the wiring contained inside will withstand all fires indefinitely.

You are implying that the tanks contain flammable liquids.

If true, your conduit must comply with article 500 of the NEC if you are in the USA.

This may require rigid steel conduit and explosion proof fittings, seal-offs, etc.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Active Contributor

Join Date: Mar 2014
Posts: 14
#5
In reply to #4

Re: Cable Conduit Requirement

03/27/2014 10:55 PM

Thank you. I am in North America. Thanks for leading me to NFPA 70. The tank carries flammable hydrocarbon. My concern is if there is a fire in the dike, I want the cable conduit to withstand the fire to allow for proper shutdown of the facility.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Cable Conduit Requirement

03/27/2014 11:24 PM

If you want/need the electrical installation to continue working in the event of a fire then you will be needing mineral insulated conductors eg pyrotenax.

If it is just mechanical protection that is required then steel conduit may be stipulated for hazardous areas.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#7
In reply to #5

Re: Cable Conduit Requirement

03/27/2014 11:28 PM

If the PVC conduit doesn't catch fire is certainly will be deformed, sag and perhaps even encapsulate the wires within it. Heating PVC pipe/conduit is the most frequently used method of bending it into other than straight runs. This is done at temperatures less than fire conditions.

Another concern would be the insulation of the wire within the conduit. Normally used wire THHN, THWN and others have insulation that will not withstand the heat that would be generated within the PVC conduit. As the insulation breaks down the wire within the insulation would contact each other and possibly short or break. Either way the wires would be worthless and you would have no control of the circuits.

NFPA 70 is more readily available and cheaper if you get a copy of the National Electrical Code (NEC), they are the same. NFPA 70 is part of the whole NFPA codes at about $1,500 and the NEC is about $40-50.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Active Contributor

Join Date: May 2009
Location: Western PA, US
Posts: 22
#8
In reply to #5

Re: Cable Conduit Requirement

03/30/2014 10:16 PM

The first thing you need to do is determine your area classification. If you are in (likely) a Class 1 Div 2 then you will need to follow the specifications required for the area. How "fire retardant" the conduit is really isn't the question; you need to know if it is rated for the area and materials being stored.

Your best bet is to pull the classification drawings for your area and this will define your requirements.

Rick

__________________
Very funny Scotty, now beam down my clothes!
Register to Reply
Member

Join Date: Mar 2014
Posts: 9
#9
In reply to #8

Re: Cable Conduit Requirement

03/31/2014 1:32 AM

Rick, Thank you very much for your response. The conduit is sealed so there is no flammable vapor ingress into the conduit. My understanding is that this should be sufficient from an EAC perspective. The concern is that if there is a fire in the tank dike, then I need the conduit to withstand the fire for some time to enable proper facility shutdown. Area calssification is not an issue for the problem at hand. My concern is the effect of an external fire on a PVC conduit.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #9

Re: Cable Conduit Requirement

03/31/2014 2:19 AM

refer to #6

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers: