Transformer Body Earth & Neutral Ground Earth

04/03/2014 5:20 AM

How many points of earthing needed for transformer and switchgear?
some people says 2 points for body & 2 parallel cable for neutral grounding transformer, and how about switchgear?, so we need two parallel path for PE?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Transformer Body Earth & Neutral Ground Earth

04/03/2014 10:21 AM

The transformer tank [or frame] has to be grounded [earthed] at least once but all metallic parts which could be energized in case of insulation break down have to be bonded together and connected to grounding. The neutral of transformer has to be grounded close to transformer. In the main switchgear you have to ground the neutral once again if the switchgear is located in separate building. NEC Art.250.24(A)(2).

For different transformer secondary connections see also IEEE-142/2007 ch.1.6 Location of system grounding points.

BS7430 recommends different systems to connect the neutral to earth. See fig.1 for TN system, fig.2 for TT and IT Systems.

__________________
Julius
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Transformer Body Earth & Neutral Ground Earth

04/03/2014 2:30 PM

You will have to read the appropriate standard as it depends on the standard you are working to and the application (for the minimum required earthing).

For example (from memory), the AS/NZS substation transformer and switchgear standard calls for two independent parallel runs of rated earth cable for 100% protective earthing redundancy for transformers and switchgear.

Have a look in the standards you are working to, the information should be clearly indicated. The end customer may possibly require more extreme earthing protection above what the standards say is recommended, so also consult them (as I once found out in the middle of a project).

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Transformer Body Earth & Neutral Ground Earth

04/03/2014 2:43 PM

As per usual, not enough information.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Transformer Body Earth & Neutral Ground Earth

04/03/2014 4:45 PM

It depends upon the country of installation, as that country's electrical standards would be immediately applicable to the installation and would determine the answer the Original Poster's question.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#5

Re: Transformer Body Earth & Neutral Ground Earth

04/04/2014 3:53 AM

Theoritically ONLY one idea connection to earth is sufficient for body as well as for neutral. But practically you shopuld have atleast two for a back up and earth resistance data required. In practice three pits are made in a delt form - joined together and are used for two connection fron two different pits. In many cases standards and guidelines also demand this. I am not sure which are of glob , you are talking about. SO go by standards of the area for legal/ mandatory compliances.

In all the cases while earthing body please note that the sections connected with bolts e.g. Terminal bloc covers , tank cover etc need to be bonded tegether.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Associate

Join Date: Apr 2014
Posts: 51
#6

Re: Transformer Body Earth & Neutral Ground Earth

04/04/2014 4:42 AM

We generally use 2 body earthing and 2 neutral earthings for transformer.

Register to Reply
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#7

Re: Transformer Body Earth & Neutral Ground Earth

04/09/2014 5:00 AM

common knowledge and depending the standard and the area of application. where are you installing that transformer, matters most. as for the switchgear it is as simple as ABC, unless you are assembling or manufacturing.

__________________
an error does'nt become a mistake if corrected!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Transformer Body Earth & Neutral Ground Earth

04/23/2025 4:58 AM

With two or more connections it is possible to disconnect one of them for the purposes of testing while maintaining a safe installation, from the point of view of the individual doing the testing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: