Pump and Pressure Vessel Size for 10500L/day

08/11/2014 5:14 AM

Dear All;

I am not able to calculate & decision to pump size and pressure vessels size for domestic water in Hotel upper story.

How will I calculate and choice to pump and pressure vessels size for 10500 Litre/day? I don't know the fact of depending on if calculate on this case. We need pressure output is about 3.5bar.

Please Help me.

Best regards

na

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#1

Re: vessels size for 10500L/day

08/11/2014 6:53 AM

I think you need to supply more information.

For one thing 10500 Liter/day. the usage is usually surges where the majority of water use is in the mornings with guests using it for showers, How many guests?

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#2

Re: Vessels Size For 10500L/Day

08/11/2014 9:27 AM

As Phoenix just stated, we need more info. Is there a supply water well and what yield does the well provide? Is storage based on a trucked water supply? Rain water? You will need to know peak demands and expect several peaks throughout the day. Peak demands can be guesstimated by number of rooms, number of faucets and toilets, and some history is always helpful. Is the water for a single floor? And where is the storage system located in respect to elevation from the upper story?

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Vessels Size For 10500L/Day

08/11/2014 9:41 AM

Send your requirements to a pump company, or a supplier of turn key water systems.

Either one will help you and ask the proper questions which you fail to answer here, mostly because you don't know what they are.

Do not try to do this "on-the-cheap" (yourself) as your guests will never be happy with the result.

Pay a few dollars more and do it right.

Register to Reply
2
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Vessels Size For 10500L/Day

08/11/2014 9:46 AM

Your not going to get much help here. As the question as asked is lacking all the necessary information to even begin to make any computations. Most of us are not into pulling teeth to get it either.

So I will say hire someone to do the work for you. Let them pull the teeth it's what you pay them for.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#5

Re: Vessels Size for 10500L/Day

08/11/2014 4:09 PM

Request several quotations, the suppliers will most likely want to visit the place to see your application, the rest will be a lot easier for you.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: Vessels Size for 10500L/Day

08/11/2014 5:31 PM

As others have stated, this is a specialist area that you need to pay someone for, but in addition, the pipe sizing inside the building (delivering to the rooms) may also limit the amount of water to be supplied at those peak times with associated pressure loss.

The whole system needs to be balanced and not just the pump/tank capacity.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Vessels Size for 10500L/Day

08/11/2014 6:03 PM

Have you given up on your " 2m x 2m x 2m = 8m³ volume" tank?

Did you ever arrive at an answer for the flow through the hole in the bottom?

I think all agree that you need on-site help with this project, if it is not homework.

Good Luck.

Register to Reply
Participant

Join Date: Jun 2013
Location: Lagos. Nigeria
Posts: 2
#8

Re: Vessels Size for 10500L/Day

08/11/2014 6:51 PM

Shape of pressure vessel is required. I mean whether its rectangle , cuboid or cylindrical.

this will enable determination of size.

Knowledge of the HEIGHT OF THE STOREY BUILDING is also important to select pump size based on the flow rate 'Q' and head 'H' in meters.

the pump selection should be such that its flow rate must be higher than 10.5m3/day at a head greater than the height of the storey building so that the pump can rest at certain interval of time when controlled by a float switch.

Dear friend lets know those parameters.

Regards;

__________________
Engr. Disu M. Olayiwola, Lagos; Nigeria
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#9

Re: Vessels Size for 10500L/Day

08/11/2014 8:20 PM

What would happen if the answer from here you chose was very wrong? Could you over expend money? Valuable money? Cause a big flood when guests are there? LOSE YOU JOB?

For these very simple questions you need to hire the smartest person you can get ahold of to do this. If you have to ask this question you are not that guy. Spend some good money and get a good solution from someone who specializes in this type of project design.

For example, I go to a dentist for dental work to be done. I'm not good enough at it, besides my tools are too big!

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Associate

Join Date: Sep 2012
Posts: 47
Good Answers: 3
#12
In reply to #9

Re: Vessels Size for 10500L/Day

08/12/2014 11:15 AM

Thank you. I woke up pretty grumpy, but this shook me out of it!

Register to Reply Off Topic (Score 5)
Associate

Join Date: May 2014
Posts: 30
#10

Re: Pump and Pressure Vessel Size for 10500L/day

08/11/2014 11:27 PM

-The system of my building have .basement, Ground, mezzanine, 1st to 8th & Roof. (Total 12 floor) Basement height is 10ft and other are 9ft each. (Small Hotel)

-Total water requirement is 27000L/day

-5th, 6th, 7th, 8th & roof are using by Pump feed from roof tank (10500L/day)

-other under floor of building using by Gravity feed from roof tank. (16500L/day)

-So I thought roof tank size is 27m3.

-I thought basement tank was 9m³ for transfer, complete with transfer pump (3Hp).

-Domestic water tank is built at 8th storey for the whole building. I will put out 2 line from tank, 1 for Gravity feed & 1 for Pump feed.

Now, I can't think for pump size and Pressure vessel size for (pump feed system) of upper storey.

Usually, we use pressure is 3.5bar.

If need other effect, please fill and calculate for me.

Many thank.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Pump and Pressure Vessel Size for 10500L/day

08/12/2014 4:23 AM

There is no need to share these data here as though they were some sort of afterthought to the original thread. Take them instead to specialist pump systems suppliers and discuss it with them, preferably over the telephone, as has already been suggested. On receipt of quotations, select the best, raise a purchase order, and have them do the equipment selection and installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13

Re: Pump and Pressure Vessel Size for 10500L/day

12/19/2014 5:44 AM

Can you draw graphs indicating consumption(l/m) vs hour of the day(24hrs) for each floor and submit to a pump supplier,indicating separately the capacity of sump and quantity required in overhead tank for fire protection.

__________________
pnaban
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: