Anonymous Poster #1

LV Cable Sizing

02/07/2015 7:50 PM

Hi,

I am using the formula LV Cable size = (2*K*L*I)/(voltage drop). This gives cable size in tems of mm2.

K=0.02 for copper ad 0.03 for Aluminum.

L=length of cable in metres.

I = current in amps. Normally, we use 1%, 2%, 3% and 4% voltage drop, and 5% voltage drop for motor loads. Is this okay for cable size determination?

Regs,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: LV Cable Sizing.

02/07/2015 8:12 PM

Only partly correct. The wire size must also satisfy a cross-sectional-for-ampacity requirement, with possible adjustments for ambient temperature, number and configuration of adjacent conductors, etc. See local regulations for details.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#2

Re: LV Cable Sizing.

02/07/2015 8:20 PM

I'm not fond of your formula but I cannot say if it is correct or not from the sparse information. Your formula does not take into account the cable insulation, number of conductors, cable path (residential wall, direct burial, conduit, cable tray, etc.), or any plausible indication of where this "rule of thumb" formula should be applied.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
4
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: LV Cable Sizing.

02/07/2015 8:24 PM
Reply Good Answer (Score 4)
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#4
In reply to #3

Re: LV Cable Sizing.

02/08/2015 12:29 AM

Hi,

Regarding cable distance correction factor: - is it for depth of laying or length of cables upto load centre?

The following table is not clear - what is Nil, cable diameter, 0.125m, 0.25 m, and 0.5 m? It appears 0.125m, 0.25m and 0.5m are cable diameter. Shall I understand for the blue marked cable distance correction factor that it is for 4 no of ckt (ie number of run of cable=4), and it is for a cable of diameter of 0.125 m??

Cable Distance correction Factor (K6)

No of Circuit Nil Cable diameter 0.125m 0.25m 0.5m
1 1 1 1 1 1
2 0.75 0.8 0.85 0.9 0.9
3 0.65 0.7 0.75 0.8 0.85
4 0.6 0.6 0.7 0.75 0.8
5 0.55 0.55 0.65 0.7 0.8
6 0.5 0.55 0.6 0.7 0.8

Regards,

Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: LV Cable Sizing.

02/08/2015 12:37 AM

Inspection of that table shows that no consistent formula is applied, and that the distances have very limited applicability. GIGO.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #4

Re: LV Cable Sizing.

02/08/2015 12:45 AM

You have chosen to use someone else's proprietary method(?) to do your work for you. You should contact the blog poster and ask him directly exactly when, where, why, and how you should use his "thumb rules", especially since he provides no references, standards, codes, etc.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #4

Re: LV Cable Sizing.

02/08/2015 12:51 AM

...and now I see why there are no references, it was plagiarized verbatim with no attribution to the original author, you get what you pay for, shows what you can do with your "thumb rules" and where they were before you got them.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#9
In reply to #4

Re: LV Cable Sizing.

02/08/2015 8:30 AM

There is very little anyone can tell you without knowing where this table came from. Where a table resides in a certain cabling code is often more important than the table itself. This table tells you how to identify the numerical value of K6. Clearly K6 is a variable in an unspecified formula involving cable length. If we knew what attribute the formula calculated or the actual formula with units then we might be able deduce how to use this multidimensional table.

You've presented here a classic mistake when asking for help on a blog. You've given us only the information that baffles you. This is less information than what you have. We have no chance of finding the critical missing information or understanding without added information. A citation where this table came from so somebody could look for the missing information or at the very least text information from the relevant code that you do not understand why it applies to this table.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 2)
Anonymous Poster #1
#10
In reply to #9

Re: LV Cable Sizing.

02/08/2015 9:16 AM
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#11
In reply to #10

Re: LV Cable Sizing.

02/08/2015 10:38 AM

That's better but as you correctly surmised the website does not clearly identify how to use that table. In both example cases the website demonstrates there is only one circuit making this derating factor moot. I have my suspicions what the other attributes mean but since this website does not identify which actual code this table comes from I will not post my guess. Code books are convoluted and complex for a very good reason. They attempt to handle the wide variety of real world conditions with the least amount of words. Removing any of the words will mean some scenarios will not be properly explained.

If you wish to know how to use that table, ask the one who posted it originally, not Lyn. Lyn just used a search engine, as you should have, to answer your original question.

There is also a question of relevance here. This website claims to be from an Indian electrical engineer. Presumably he uses the Indian electrical codes. They may not be relevant for your application. All of the codes used around the world are similar but they are not identical. That difference has more than once been the difference between a safe and a dangerous installation.

Take this lesson from this thread. You usually get what you pay for. You did not pay money for a universal wiring standard. This is a good thing because none exists. Your mind did pay all of us by recognizing a flaw in this website's presentation. Keep thinking clearly and you will go far.

Lastly, please come out of the shadows by using your CR4 handle instead of the anonymous posting option. You are polite and well reasoned. You will be granted more respect here by using your handle.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: LV Cable Sizing.

02/08/2015 10:48 AM

It's interesting to note that the whiners are whining about one of the 5 sites I posted. I give up.

I wonder who ties their shoes for them?

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13
In reply to #4

Re: LV Cable Sizing.

02/08/2015 11:53 AM

This table it is a copy of IEC 60346-5-52 Table A.52-18 (52-E2) - Reduction factors for more than one circuit, cables run directly in the ground .This table it is only for ampacity [current carrying capacity] calculation purpose.

No connection with voltage drop. For single core cables the reactance will increase with the distance while resistance will decrease a bit [less proximity effect].

__________________
Julius
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: LV Cable Sizing.

02/08/2015 7:06 AM

Dear Friend,

Based on the Electrical Conductivity for Electrical Grade Copper and Aluminium there is another Standard for deciding the cable/conductor size selection, which is as as follows:

1. For Copper the Current Density is 1.55 Amps. per MM^2

2. For Aluminium the Current Density is 0.968 Amps per MM^2

The above values are with out De-Rating Factor, Ambient Temp. Correction, Bunching of Conductors, Under-Ground or Over-Head laying etc., etc.

You have to apply the factors and decide the size of the .cable and add 10% margin for any variation in the assumed factor(s) and use the nearest higher size cable.

DHAYANANDHAN.S

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#14

Re: LV Cable Sizing

02/08/2015 11:12 PM

Regs,

Keep on studying and asking questions. The formula you quoted is only partially correct. First, it will give you the minimum cross-sectional area of the conductors for the specified load and length.

For a single phase circuit,

CM = (2*L*K*I)/VD

For a 3-phase balanced circuit,

CM = (√3*L*K*I)/VD

Where: L is the one-way length of the circuit, I is current in amps, VD is voltage drop as a number (not a percent), and K = 0.020 for copper... If you were using voltage drop as a percent, such as 1, 2, 3, 4, or 5, then K would be 2.0.

As others have correctly pointed out, this answer is only a portion of the answer you need. There are a number of factors that can and should increase the wire size:

  • Temperature limit for the conductor insulation,
  • Ambient temperature the circuit runs through,
  • Number of conductors in the conduit, raceway, duct, etc.,
  • Type of load (such as motor, welder, lighting, or others),
  • Whether it is continuous or not, and
  • Size of overcurrent protection ahead of the wire (or after it, if this is a short feeder and codes allow taps with overcurrent protection after the tap).

I personally would never size a motor conductor with VD=5%.

Get out the code books that are applicable for your area and study them. Get out text books and study them. Get out manufacturers' literature and study this.

When you ask questions, give us details that relate to the question, such as application, location, purpose, source of your formulae, etc.

--John M.

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15

Re: LV Cable Sizing

02/09/2015 12:49 AM

This voltage drop calculation formula it is based only on resistance shown in NEC. See:

http://ecmweb.com/code-basics/dont-let-voltage-drop-get-your-system-down

This is approximately good for small area cross section of copper conductors at a certain operation temperature. The more accurate calculation has to take into consideration skin effect and proximity effect for resistance calculation at the actual operation temperature and the reactance between conductors at the actual distance.

For still more accurate calculation you need to know the power factor also.

VD=I*R*cos(fi)+I*X*sin(fi)

For more details see:

IEEE 141 ch.3.11 Calculation of voltage drops.

__________________
Julius
Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#16

Re: LV Cable Sizing

02/09/2015 5:06 AM

There is a good source of advice on cable rating in BS 7671 (the IET Wiring Regulations). There's a link - http://electrical.theiet.org/wiring-regulations/index.cfm - but you have to buy it!.

For Volt drop specifically, the ECA sheet at http://www.eca.co.uk/filelibrary/download/?FileID=2361 will help.

As to motors, the criteria are i) starting volt drop and ii) volt drop represents wasted energy. 5% = 5% additional losses.

Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#17
In reply to #16

Re: LV Cable Sizing

02/09/2015 5:34 AM

I found a calculator also - for NEC or IEC - at http://www.cablesizer.com/iec/voltdrop/.

You could say it does what it says on the tin, but the site also computes current rating. One can be lazy!

found

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18

Re: LV Cable Sizing

02/09/2015 1:30 PM

British Standard 7671.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Reply to Forum Thread 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Anonymous Poster (1); dhayanandhan (1); Geoffrey36 (2); jmueller (1); lyn (2); PWSlack (1); RAMConsult (2); redfred (3); sauravbabu (1); Tornado (2)

Previous in Forum: Variable Speed Drive for 40W Fan   Next in Forum: NI-Cd Battery End Cell Voltage Significance

Advertisement