I'll bet there are some great stories on this topic so I thought I would start with mine and see what wisdom follows. This always seems to be a good way to share important design criteria for the people just getting into the art.
We had some motor control cabinets built by a panel builder per our request. We added fans later because we didn't specifically call them out and we trusted the vendor to know what he was doing. Ha! You get what you ask for, but it may not be what you need! Ain't it the truth!
Anyway, about 6 VFDs were installed in a cabinet about 3 feet wide, 5 feet tall, and about 12 inches deep with no ventilation. The incoming power was 480, 3 phase and the temperature rise was only "warm to the touch". But then one day about a year later, those motors were being worked pretty hard and a controller kicked out. I got called out to look at it because it wouldn't reset. (it was still too hot internally)
I noticed this oil or grease like coating on the surface of the VFD's and wondered to myself what that could be. Then it hit me that it was the re-condensed thermal grease between the VFD and its heatsink on the back. It had evaporated and settled on the front of the case. We immediately installed filtered air fans and exhaust vents in each of the cabinets. Haven't had a problem with them since.
__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle