capacity of an electrical circuit

02/22/2008 6:19 PM

I have three large freezers (1. 115V, 13A; 2. 115V, 15.7A; 3. 115V, 12.3A) running on a 120V 20A circuit. If all three are plugged in the circuit breaker trips. Is this because there are too many Watts? Can I fix this problem without running a whole new circuit?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Instrumentation Engineering - New Member Hobbies - Automotive Performance - New Member Technical Fields - Education - New Member Fans of Old Computers - TRS-80 - New Member Hobbies - Musician - New Member

Join Date: Jan 2008
Location: Tucson, AZ
Posts: 1331
Good Answers: 30
#1

Re: capacity of an electrical circuit

02/22/2008 6:29 PM

...yes. Most residential duplex (wall outlets) recpticles are circuit-breakered or fused for 20A, thus ANY combination of two of the freezers exceeds 20A...adding the third freezer is certainly WAY too much, and the circuit-breaker is "properly" tripping.

...you need to either (A) run two more separate electrical lines each with its own circuit-breaker (ideal); or, at the very least (B) run one more sepate electical line with its own circuit-breaker (not really enough).

...maybe there's some demand-timing "device" available to ensure that only ONE freezer can be "on" and a time, and when the first freezer is done running will automatically "switch" over the next (priority) freezer needing to be running?

__________________
...and the Devil said: "...yes, but it's a DRY heat..!"
Register to Reply
Active Contributor

Join Date: Jan 2008
Location: Land of many Islands
Posts: 14
#2

Re: capacity of an electrical circuit

02/22/2008 8:43 PM

Hello sallison,

Your current 20A circuit is not design to supply that heavy load, the breaker trips because of high currents(amperes).

you have two solution

1. Add new circuit 30A breaker to supply only two large freezer

2. change the whole circuit with higher amperage probably 50A

__________________
Big improvement starts with small changes
Register to Reply
Active Contributor

Join Date: Dec 2007
Location: Auburn, MA USA
Posts: 23
#13
In reply to #2

Re: capacity of an electrical circuit

02/24/2008 5:52 AM

NO NO NO

If you increase the beraker to 30 or50A you will also need to change the outlets and cord and plug on each freezer to match.

Your best bet is to run a 20A ckt to each unit you only need to run a 12/3 rx cable to get 2 more 20A ckts this will also pervent loosing all 3 units if a breaker trips melting all your goods insted of only loosing one unit

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#14
In reply to #13

Re: capacity of an electrical circuit

02/24/2008 9:24 AM

Whoa up there Lighting up USA,

The 30A/240V circuit needs to be split to 3 15A/115V circuits, is the reason I suggested using a distribution panel. I've found the work simpler this way.

No changes to existing power cords required...

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Active Contributor

Join Date: Dec 2007
Location: Auburn, MA USA
Posts: 23
#15
In reply to #14

Re: capacity of an electrical circuit

02/24/2008 9:35 AM

That was for AUTOZAM's comment.

Depending on his location to the main panel a sub panel might work out better ie: future loads?

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#16
In reply to #15

Re: capacity of an electrical circuit

02/24/2008 9:50 AM

Yes if it were a consideration then a 50A < dist panel maybe cost effective

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: capacity of an electrical circuit

02/22/2008 9:37 PM

Good thing .Cable not heated up and burnt.

Please connect each freezer in seperate outlet.do not club all the freezers in one outlet.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
4
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4

Re: capacity of an electrical circuit

02/22/2008 11:43 PM

Hello sallison

3 Freezers = 3 circuits.

If you were in New Zealand, running same compressor size at 230Volts, there would be no problem, because they could be run from a single circuit with a 30 Amp Circuit Breaker.

However, you are 115 Volt system, which means that your Compressor currents are double ours, because of your lower voltage mains supply.

Remember when a freezer compressor starts, the surge current for that motor is at least 5 times the run current of that motor.

For your own peace of mind, and to avoid an electrical fire sometime soon, get an extra two circuits run, each of the then 3 circuits fitted with a 20amp Circuit Breaker.

Then your troubles should be over, providing your Switchboard and mains cabling + supply mains can handle the increased load.

Advise your progress here, thank you.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Good Answer (Score 4)
Power-User
Hobbies - Musician - New Member Engineering Fields - Manufacturing Engineering - New Member

Join Date: Sep 2007
Location: Endless Mountains of NE Pa, USA
Posts: 298
Good Answers: 20
#30
In reply to #4

Re: capacity of an electrical circuit

02/25/2008 8:11 PM

Oh and btw Sparkstation,

I gave you and JRaef good marks for your great answers to sallison's delemma.

Jeff

__________________
Courage is not the absence of fear, but the inner resolve to rise above it....or the inane lapse in judgement brought on by copious imbibitions....Egre Flagrus
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Oct 2006
Location: East Coast, US
Posts: 94
Good Answers: 3
#5

Re: capacity of an electrical circuit

02/23/2008 11:32 PM

Do you know what your local electrical code requires for such an application? Where I'm at, it would be required to have a "home-run" - (dedicated line) - for each of those freezers.

One solution would be to put in a larger circuit breaker, assuming that the wire is the appropriate gauge to accomodate such a load.

This is a link with a chart telling you what each gauge can handle. But as Sparky said, the initial draw is much higher, and needs to be factored in.

http://www.powerstream.com/Wire_Size.htm

Register to Reply
Commentator

Join Date: Oct 2006
Location: East Coast, US
Posts: 94
Good Answers: 3
#6
In reply to #5

Re: capacity of an electrical circuit

02/23/2008 11:55 PM

It is doubtful that the wire supplying power to these freezers is even large enough, probably 10-12 gauge, but there may be another possibility...

This is a longshot. Are these freezers stand-alone units? What I mean is to find out if they're controlled by some sort of PLC. If so, you may be able to keep them from "starting" at the same time by programming the PLC to turn them on one at a time. This would help keep the load under the maximum rating.

Register to Reply
Anonymous Poster
#8
In reply to #6

Re: capacity of an electrical circuit

02/24/2008 12:22 AM

I'm not sure about this, but starting and stopping the freezer at certain times are just inefficient since it consumes a lot of current to start the freezer. At the end of the month you will be surprise about your bill.

Register to Reply
Commentator

Join Date: Oct 2006
Location: East Coast, US
Posts: 94
Good Answers: 3
#11
In reply to #8

Re: capacity of an electrical circuit

02/24/2008 2:12 AM

My proposal would assume that it would be programmed to turn on and off as needed via input from a thermostat.

Register to Reply
Anonymous Poster
#9
In reply to #5

Re: capacity of an electrical circuit

02/24/2008 1:13 AM

Don't understand the chart . Every chart I've seen and in the code book it calls for 14 ga for 15 amps , 12 ga wire for 20 amps and 10 ga wire for 30 amps . Being as that it's in the electrical code book I wouldn't say that it's just a guideline or rule of thumb . Can see going up in wire size when it's derated for a long run , but certainly not smaller than the code . The circuit breaker is sized to protect the wire , and the wire is selected to handle the load . ---- Inefficient to start and stop the freezers ?? The compressors don't run all the time . They switch on as required to maintain the temp desired . They draw max current on starting and once running , the current drops to something below full load current . Should not really change much on total current usage if you controled them so no two compressor motors started at the same instant . One compressor starts , and perhaps 4 or 5 seconds the second compressor starts after the first compressor current draw drops off . Doing it this way would probably let you run two freezers , but unlikely three . One thing for sure , is if you decide to just put in a larger breaker without large enough wire , you may build a toaster . ---- efficiency ???? Poor door gaskets , opening and closing the door unecessarily , or not keeping much in one all run up the electric bill .

Register to Reply
Anonymous Poster
#7

Re: capacity of an electrical circuit

02/24/2008 12:16 AM

The breaker you have is just right for the wire gauge. Increasing the breaker's Amps might cause you problem, if not the moment you change it, it might occur in the future. Spending time to run another line will save you from disaster.

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#10

Re: capacity of an electrical circuit

02/24/2008 1:31 AM

sallison,

No, you have to run another circuit.

I would run one three wire cable @ the gage required in your area to at least a 30A satellite distribution panel at the freezer location. In this dist panel have three 15A breakers to provide one separate 15A circuit to each freezer. The cost difference of a 50A is significant over a 30A, the 30A dist panel is sufficient for the service you described but do check local codes.

Electricity is controlled smoke...

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12

Re: capacity of an electrical circuit

02/24/2008 4:44 AM

You really should run 3 circuits (2 more) and therefore have a separate breaker for each freezer. Why? you may ask, well I assume that what is in the freezers must stay cold and if a fault occurs and blows the fuse, at least the loss of the contents will then confine itself to one freezer.

Also, as someone mentioned, the starting current of any two freezers on the same circuit, occurring exactly together, could still occasionally blow a fuse......even though the current draw is seemingly less than the fuse in question.....

Running two extra circuits will only cost marginally more than running one and you must run at least one I feel.....

Battery driven Freezer monitors with alarms are also a good idea too......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#17

Re: capacity of an electrical circuit

02/24/2008 10:58 AM

13Amp + 15.7Amp + 12.3Amps equals 41Amps. There you have it. Too much for the circuit. I don't know of a device that always keeps two of the freezers shut off, though their may be one. Doesn't seem very straightforward and simple a solution to me. Also typical house ciricuits are usually 15 amps in most rooms, and only 20 in the kitchen. The breaker rating is on the breaker in the box.

As well if you have repeatedly tripped a breaker, it may have become pitted and need to be replaced.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Anonymous Poster
#18

Re: capacity of an electrical circuit

02/24/2008 1:02 PM

FIrst you have check the total power requierment i.e each freeze -watts. Normaly you will abel to see on on freez name plate. The mathematical sum of all three freez watt ( powwr ) multiply by 1.25 time is total power requierment . That means if sum of all three freez watt comes to 1500 watt, The actual power requierment will be 1500 x 1,25 = 1875 watts divide by 115 volt = 16.30 Amp. That means you need 20 Amp MCB. You can calculate your own way & decide AMP rating of MCB

Secondly you have to check MCB you must use "B " curve for freez load , so ensure that you installe 20 AMP MCB with mark as ' C " Curve if it B curve you have replace with 20 -C.

Register to Reply
Anonymous Poster
#19

Re: capacity of an electrical circuit

02/24/2008 3:43 PM

There is a way you can probably make it all work, but you'll need additional controls to do it.

First, A freezer only needs to run to make up for heat gained from the outside or to cool contents initially placed into it. This means that on the average a normal freezer probably runs much less than 25% of the time.

Second, a 20 Amp circuit is capable of handling one 16 amp load continuosly. Since your largest freezer is 15.7 amps, the circuit is adequate for any 'ONE' of your freezers at a time.

Third, construct a control circuit that only lets one freezer run at a time. Feed 3 contactors from the 115 VAC, 20 Amp source. Connect an outlet for each freezer to the load side of one of the contactors. Put a current sensor in series with each of the freezer circuits that prevents the other two from closing if curent is flowing in the third circuit. You would need a threshold setting, say 1-2 amps, to allow for normal freezer idle current without tripping the sensing circuit.

Operation: whatever freezer turned on first would lock out the other two freezers. When the first freezer cooled down to setpoint temperature and shut off it would stop drawing current and enable all three freezer circuits. At this point if either of the other two freezers required a cooling cycle it would turn that freezer on and lock out the other two circuits until it had completed its cooling cycle. This sharing of the single circuit could continue indefinitely, and unless you loaded all three freezers with lots of warm items at the same time, it wouldn't cause any problems with any of the freezers or their contents.

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#20
In reply to #19

Re: capacity of an electrical circuit

02/24/2008 6:44 PM

Such a control system would work, but might be more complex than running 2 extra lines and installing 2 extra breakers. Also, it would make sure a qualified electrician is there to ensure the intermittent load does not exceed the panel rating.

If there was no more room on the panel, then such a control box would enable the freezers to run at their allotted time one after the other all on one circuit breaker. I don't know where you would find such a unit though. It would be pretty simple...just a switch that makes one of three outlets "live" at a time. I expect it would look like a power bar. Anybody know where to find one?

__________________
If it was easy anybody could do it.
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#28
In reply to #20

Re: capacity of an electrical circuit

02/25/2008 10:30 AM

On second thought, never mind, sure as heck some well meaning soul would replace the switching unit with a power bar. ButI knew I had run across something similar a lifetime ago, and it was legal at the time. It would likely not be legal in commercial installations, or in other countries with their own codes.

Here is the relevant section in the Canadian Electrical Code, admittedly a couple of years out of date. Its on "Appliances Exceeding 1500Watts", which these freezers do. The phrasing suggests cook tops or space heaters, but the freezers ARE an appliance, so this must apply to them as well.

26-748 Appliances exceeding 500 W.

(1) Every electrial heating and cooking appliance rated at more than 1500 W shall be supplied from a branch circuit used solely for one appliance except that more than one appliance may be connected to a sing-branch circuit providing that the following is used.

(a) A multiple throw manualy-operated device that will permit only one such appliance to be energized at one time; or

(b) If the appliance has more than one individual heating element each controlled by a switch, no main switch need be provided.

The relevant part is part (a) above...you could have each item switched one after the other, but it says it has to be a "manual" switch. So the guy running the freezer will need to power down one unit before powering up the next, and you can't use automatic equipment for that. Or, you are allowed to unplug one freezer and then plug in a second in the same receptacle, providing you turn off the freezer first. (part b)

Notwithstanding that, in commercial installations, the standards are much tighter, and will demand that three freezers will have 3 power supplies going to three breakers. Then it becomes cheaper and more effective to just install the proper wires and breakers, and more importantly, nobody will be tempted to automate, bypass, or generally do something stupid to what should be a fairly straightforward system.

__________________
If it was easy anybody could do it.
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#21

Re: capacity of an electrical circuit

02/24/2008 8:42 PM

Wow, so much foolish and dangerous advice mixed in with the good stuff...

1) Do NOT just increase the breaker size. You will likely start a fire.

2) As others have said, you CANNOT run even 2 of these freezers on one 20A breaker. Code only allows a breaker to be loaded to 80% of it's rating, so a 20A breaker can only be loaded to 16A, not 20A. Your lowest combination is 25.2A. That exceeds the rating even if you had those 2 freezers on a 30A circuit breaker and 10ga wire.

3) Forget the schemes of staging the compressors. Again as others have said previously, refrigeration equipment MUST be allowed to come on and off as the temperature control system demands. Staging them with a PLC and contactors etc. may result in damage to the food from partial thawing and refreezing. If that happens, what was the point of having a freezer?

4) Staging the freezers will also likely result in damage to the equipment because of the possibility of it being locked out when it should have defrosted the coils.

5) Forget the ideas that freezers run with less than the Full Load Amp rating; you CANNOT count on that. CONSIDERING THAT IS ILLEGAL. All sizing of conductors and their protective devices MUST be done based upon the equipment Amp ratings. NOTHING ELSE MATTERS.

6) By the way, the starting current is completely irrelevant in this situation. It may be the final factor in causing the breaker to trip, but that does not change the fact that you are overloading your system.

YOU HAVE ONLY ONE LEGAL AND SAFE COURSE OF ACTION.
You must have separate 20A circuits, each with their own breaker, installed for each freezer. In addition, each circuit will not have any meaningful head room for other devices (other than maybe a few light bulbs).

Do NOT ignore this advice. Doing so may result in death or fire.

Kudos to those who have stuck to their guns on suggesting the right actions. Shame on those who think it is acceptable to dispense potentially dangerous advice to someone who, by virtue of having to ask the question, is obviously not familiar with electrical work.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Power-User
Hobbies - Musician - New Member Engineering Fields - Manufacturing Engineering - New Member

Join Date: Sep 2007
Location: Endless Mountains of NE Pa, USA
Posts: 298
Good Answers: 20
#22
In reply to #21

Re: capacity of an electrical circuit

02/24/2008 10:02 PM

Thank you JRaef and Sparkstation for your excellent comments!

Sallison, I hope that you will Please take these comments to heart and do it the RIGHT way.

3 freezers, 3 circuits! Anything else would be a code violation and also violates COMMON SENSE!

The small amount of money and time expended is a mere pittance when weighed against the cost of replacing your home or business and its contents due to a preventable Fire.

__________________
Courage is not the absence of fear, but the inner resolve to rise above it....or the inane lapse in judgement brought on by copious imbibitions....Egre Flagrus
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#24
In reply to #21

Re: capacity of an electrical circuit

02/24/2008 11:23 PM

Hello JRaef

I have given you a Good Mark for your Post.

Cheers.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#25
In reply to #21

Re: capacity of an electrical circuit

02/24/2008 11:24 PM

3 20A breakers? Plus the cost wire 3x? That's quite a tidy sum.

Why not one 30A or 50A circuit to a sub panel and then split the 240V into 3 115V 15A or 20A circuits? He may get another large appliance someday but if not this way is cost effective.

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
2
Power-User
Hobbies - Musician - New Member Engineering Fields - Manufacturing Engineering - New Member

Join Date: Sep 2007
Location: Endless Mountains of NE Pa, USA
Posts: 298
Good Answers: 20
#27
In reply to #25

Re: capacity of an electrical circuit

02/25/2008 3:44 AM

Hi bwire,

That's still (3) 20A breakers plus a minimun 50A dbl. pole breaker plus a subpanel. It would depend on the length of the seperate runs regarding which would cost the least and whether there is room in the main panel for the breaker(s).

A Real electrician would have to go with one of the (2) scenarios. It's still (3) circuits or (4) circuits depending on which way you go. No way to get around the common sense code that's in place for a reason.

If Sallison is unable to perform the task on his/her own, or if the area they're in Requires a qualified electrician then hiring one is the best bet. Either way the cost is Still negligible compared to a fire.

I apologize if I seem single minded or unmovable on the subject of proper wiring but I've seen Way Too Many fires caused by old and even new ridiculous wiring schemes in the name of saving a few bucks.

Thanks for listening.

Jeff

__________________
Courage is not the absence of fear, but the inner resolve to rise above it....or the inane lapse in judgement brought on by copious imbibitions....Egre Flagrus
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#33
In reply to #27

Re: capacity of an electrical circuit

02/27/2008 7:57 PM

Hi snygolfgs,

You go ahead no wrong done being single minded or unmovable on this subject, you may be correct a thousand times and not get even a smile but do it wrong and you'll never be forgotten.

I tend to look to cost effectiveness while maintaining and classifying safety as paramount.

I use the sub-panel concept in these type situations where is a heavy current draw for a few safety reasons:

If a trouble occurs with a freezer; an alarm may sound or a person may run to the freezers first then if an electrical trouble; fire etc., be able to secure the energy on location. Grabbing a smoking power cord is bad news in comparison.

If you were working in the freezer area and need cycle power on then off for what ever reason a sub-panel will save steps.

Normally I use minimum 100 amp sub-panels because it just makes sense.

You're welcome,

John

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Power-User
Hobbies - Musician - New Member Engineering Fields - Manufacturing Engineering - New Member

Join Date: Sep 2007
Location: Endless Mountains of NE Pa, USA
Posts: 298
Good Answers: 20
#35
In reply to #33

Re: capacity of an electrical circuit

02/28/2008 1:31 AM

Hi John,

Sorry I haven't replied before now. I only look at this thing for a few minutes each night.

My only point was that a seperate circuit is required for each unit. How it's done doesn't really matter as long as it conforms to all local and national codes and an inspector would be happy looking at it.

Have a good evening.

Jeff

__________________
Courage is not the absence of fear, but the inner resolve to rise above it....or the inane lapse in judgement brought on by copious imbibitions....Egre Flagrus
Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#23

Re: capacity of an electrical circuit

02/24/2008 10:39 PM

Get a device that measures when power/current is flowing. on the detected signal output, use that to disable the power on the other 2 appliances.

Once number 1 gets to setpoint, number 2 is activated, then number 3, then 1 again.

Or pay someone to run a new circuit, get 3PH installed and run it to 3 points at the rear of each unit.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
2
Anonymous Poster
#26

Re: capacity of an electrical circuit

02/25/2008 1:51 AM

Most of the sollutions that are given are acceptable, good or even very good. But I guess that explaining such things to some one who apparently doesn't know ANYTHING about electricity is just dangerous.

My suggestion for Mr. or Ms. Sallison is : Have an electrician come down to your freezers and let HIM/HER check AND solve your problem. Doing this, a lot of problems, dangers will be avoided. yes ?

Register to Reply Good Answer (Score 2)
Anonymous Poster
#29

Re: capacity of an electrical circuit

02/25/2008 1:30 PM

You should have 3 circuits for the three freezers.

Some people have used timers to control the load without rewiring.

I would run two new wires here.TOO MANY WATTS

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#31

Re: capacity of an electrical circuit

02/26/2008 5:53 AM

OK. The sum of all the amps is 41.0 amps continuous, and any two continuous loads add up to more than 20A. So the 20A breaker is doing its job correctly, which is to protect the cabling between it and the downstream socket outlet(s) from overheating and the consequent risk of causing a fire. Do not under any circumstances replace the breaker with one of a higher current rating without upgrading the cabling, as that will leave the existing downstream cabling unprotected and a fire will surely follow.

Is there scope to reduce the quantity of food/drink stored so as to reduce the number of operational freezers needed, and with cascading one or two freezers out free-up some space in the building?

In addition to the good advice in the above posts, another option would be to separate the freezers by plugging them onto three separate pre-existing circuits, if present electrical distribution will allow this to take place easily.

If this is not possible, then from the nature of the wording in the posting, it would seem an appropriate course of action would be to consult a properly-qualified local electrical installer at the earliest opportunity and have additional circuit(s), for two of the freezers, to be run-in, tested, and certified.

Keep the installation test certificate filed in a safe place as it can prove a valuable valuable when the building changes ownership (in the UK, Surveyors look for these things when advising the prospective purchaser).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator
United States - Member - Les Etats Unis

Join Date: May 2007
Location: Sacramento, California
Posts: 61
#32

Re: capacity of an electrical circuit

02/27/2008 2:54 PM

Another reason (besides electrical codes and safety) to go with 3 20amp circuits, one for each freezer; If down the line you need to service/repair a freezer you will have to turn the breaker off to service it. If they are on seperate circuits you will not have to take down power for all three freezers just to service one. I guess you could just 'unplug' the freezer you needed to service but that might entail moving the freezer to get at the service disconnect which may be troublesome depending on its weight and size.

There are often many ways to accomplish a task, often doing it the 'right' (at times more expensive, initially) way in the begining can save you alot of headaches (and money) in the future, not mention the safety concerns.

__________________
No trees or ecological systems were harmed in the creation or transmission of this message. However, a large number of electrons were horribly inconvenienced.
Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#34
In reply to #32

Re: capacity of an electrical circuit

02/27/2008 8:03 PM

By right way I suppose you meant have a disconnect within easy reach?

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Register to Reply 35 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

70AARCuda (1); Andy Germany (1); Anonymous Poster (7); ArcticZone (3); autozam (1); bwire (6); Electron Oasis (1); JRaef (1); Lighting up USA (2); PWSlack (1); ramvinod (1); Snaketails (1); snygolfgs (4); Sparkstation (2); Transcendian (1); Yusef1 (2)

Previous in Forum: Transformer   Next in Forum: SPECIAL ELECTRICAL MACHINES

Advertisement