Why DC voltage?

05/17/2008 4:44 PM

Dear friends,

One easy question for you.

In hydraulics systems for solenoid valves, PLC inputs/outputs and in many other circuits, for conrol voltage, Why DC voltage(12v,24v) is used? What are problems for use of AC?

Thanks in advance..

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Why DC voltage?

05/17/2008 4:58 PM

Because most PLC's (I don't know of any which work on AC internally) have DC power supplies, and therefore have DC inputs and outputs.

If AC control is needed externally, then it's easy to connect PLC outputs to DC input/AC output solid-state relays or something of that nature.

Does that clear things up? If not, please respond.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
4
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Why DC voltage?

05/17/2008 6:17 PM

Hello Guest,

AC solenoids are not as easily controlled as DC ones, and have the potential of "chattering" at the polefaces, which sometimes requires a "shading ring = short circuited turn in the form of a heavy copper loop" around each poleface to prevent that "chattering".

DC is easily digitally controlled, in tiny increments.

DC has always been preferred for fine controls.

DC is more easily regulated.

DC control circuits have been generally standardised at mostly 24 Volts (sometimes 12 Volts), and in that way all users and manufacturers know what they specify is readily available.

That's for starters.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#25
In reply to #2

Re: Why DC voltage?

05/19/2008 8:00 AM

Good answer!

In addition:

  • 24VDC is relatively safe in the hands of the inexperienced technician compared to higher AC voltages.
  • The same power supply can be used for all the analog signals as well as the digital ones.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#3

Re: Why DC voltage?

05/17/2008 9:45 PM

In addition to SparkY's reasons, DC circuits radiate less EMI and are generally less susceptible to interference.

AC's main advantage is the ease of converting one voltage level to another via a simple passive component (transformer), not so easy with DC.

__________________
Charlie don't surf.
Reply
Power-User

Join Date: Mar 2007
Location: Newburgh, IN
Posts: 283
Good Answers: 10
#4

Re: Why DC voltage?

05/17/2008 9:56 PM

I was told many year back to use DC Solenoids on any circuit that must maintain a constant time sequence. The reason given was and AC Solenoid needs the Sine Wave at or near the peak to get enough power to move the armature that shifts the valve. I was told DC Solenoids operated the same every cycle since the power was there no matter the input timing.

It sure sounded logical to a Non-Electrial person.

The other reason I have heard is due to Electrical Shock from the normal 110VAC or the occasional 220VAC is capable of that is less prevalent with the lower voltage DC ccurrent.

Like I say, it sounded logical to a non-electrical person.

__________________
Bud Trinkel
Reply
Power-User

Join Date: Oct 2007
Location: Hartwell Georgia N34* 56.770 / W83* 35.431
Posts: 222
Good Answers: 1
#5

Re: Why DC voltage?

05/17/2008 10:31 PM

Safe and simple.

James

__________________
" adapt, improvise, overcome "
Reply Score 1 for Good Answer
Power-User
Technical Fields - Technical Writing - Validation Specialist-Medical Devices United States - Member - From the Big Apple! Hobbies - Model Rocketry - Rockets should go nuclear! Fans of Old Computers - PDP 11 - Studied computers at W.H.Taft H.S., Bronx, NY. Popular Science - Cosmology - Radio Science Observing

Join Date: Dec 2007
Location: Miami, FL.
Posts: 303
#15
In reply to #5

Re: Why DC voltage?

05/18/2008 10:03 AM

...and cheaper and safer, easy to maintian!!!!!!!!!!

__________________
WARNING! All suggestions are informative only. It is the prerogative of the user to implement under his sole responsibility. This commentator will not be liable for any damages or injuries incurred.
Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Australia - Member - New Member

Join Date: Aug 2007
Location: Childers, Queensland
Posts: 412
Good Answers: 5
#6

Re: Why DC voltage?

05/17/2008 11:21 PM

Also:- Many hydraulic components were originally devised for the mobile/automotive industry. It's mainly 12 and 24vdc there!

I would agree with all other contributers as to the ease of control on dc as, if we have a 240 ac input to a solenoid coil, we frequently need to convert to 207 dc with a rectifier plug so that we can 'adjust' the operating properties of the coil.

__________________
"A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools!" Douglas Adams 1952-2001. E&OE!
Reply
Power-User

Join Date: Mar 2008
Location: London England
Posts: 288
Good Answers: 3
#7

Re: Why DC voltage?

05/17/2008 11:47 PM

Hello there,

I am by no means an 'expert' but, bare in mind you are using power around water.......Using a DC power supply I would think is safer. If water gets into the DC power system the amount of damage will be isolated to the DC supply motor and relatively small area around it. If it is AC all kinds of precautions have to be taken in case water 'shorts out' any connection. It could go as far as starting a fire down the line away from the immediate power trip.

Of course I could be well off target with this answer but, I am sure a more expert person will answer your question.

Take care

jfmfit

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#8
In reply to #7

Re: Why DC voltage?

05/18/2008 12:25 AM

Hello jfmfit

The electrical "leakage" problem are equal, whether AC or DC.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2008
Location: London England
Posts: 288
Good Answers: 3
#9
In reply to #8

Re: Why DC voltage?

05/18/2008 3:04 AM

Hello Sparkstation,

I think...........I KNOW you are far more expert on this because I can barely wire up a three pin plug! So you have me there. If as I at first thought the electrics was around a possible source that could short them out, would not it be simple first, to have an all in one DC supply right where the power is needed, and, with a DC supply it could be say down to 12 or 24 volts and so everything is more manageable, including may be smaller motors if there is any and finite control, which is sometimes more necessary?

I am really interested in this as I can wire stuff 'parrot fashion', as long as there is an expert to check it before anything is plugged in.

I think people tend to take electricity for granted sometimes and do not give it the respect it deserves, with often dangerous consequences.think it should be like any gas installation where, you must have a qualified Electrician to do any final connections.

I know of people going from a 240v AC power supply to a home and, working on a 440 (I think it is in the UK) power supply in a factory. They are entirely different beasts!

I learned the hard way, though there was no damage to me, I got one, of I think six wires wrong in an industrial cast iron plug which weighed about a pound. I plugged it in and with the explosion the plug vaporised. I said my machine need re-wiring to my boss, but it was only a small work force of six and, he said have a go. needless to say I did not have a go after that. I copied what I was doing from another plug. Thought after 'double checking' I had it right. But I didn't. Don't take risks.

jfmfit

Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#10
In reply to #8

Re: Why DC voltage?

05/18/2008 3:14 AM

You should also consider the fact that almost all "old" car fires are caused by some electrical fault. DC currents are just as dangerous as AC currents at the same levels.

An aquaintance of mine had his car go up in flames while he was driving it around the welsh mountains. He said it was the most scary thing he ever had happen to him, sudden flames from the dash board.

Reply
Power-User

Join Date: Mar 2008
Location: London England
Posts: 288
Good Answers: 3
#11
In reply to #10

Re: Why DC voltage?

05/18/2008 3:38 AM

Hello case491,

I did not mention I bought a car. It was a mini whose battery was behind the drivers seat. Problem was every time I brakes the battery would short circuit on the metal frame of the original mini seat! My seat was on fire twice before I realised what was the problem. The second time the battery totally discharged and welded my seat to the angle frame and battery terminal, which was part of a shelf going the full width of the cab.

jfmfit

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#12

Re: Why DC voltage?

05/18/2008 3:55 AM

Control supply has to be reliable.A supply from battery is the most reliable and hence most control supply is dc and voltage varies depending upon the application 24v DC, In high voltage substation 110V dc is used.Now we can also use ac by use of inverters with battery . But again reliability is compromised as if anything goes wrong with inverter control supply is off.The battery that is supplying will sufficient capacity and is on charge .Even for this reason railways prefer DC supply for signal and point machine operations .

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Anonymous Poster
#13

Re: Why DC voltage?

05/18/2008 8:18 AM

Hey All,

Let me start by stating that I'm a licensed Journeyman Electrician.

The reasoning for D.C. controls is multi-faceted:

  1. Safety( lesss chance of injury/fatality)
  2. stability
  3. readily available( in most cases)

PLC's (from the old TI 120's through A/B RS Logix500's have the capability of both D.C. and A.C. I/O's. As Sparky stated about "chatter" the most common solution is a capacitor across the line and neutral terminals. I have never used a "shadow ring" nor have I ever ran across one.

Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#14
In reply to #13

Re: Why DC voltage?

05/18/2008 8:45 AM

It all depends on the voltage. But AC is held to be more likely to stop your heart and DC is held to give a stronger "can't let go" factor. Under the wrong circumstances, either will ruin your whole day and can ruin the rest of your life.

Please don't delude yourself with wrong facts about AC or DC being safer. Safety of either depends on your attitude and procedures.

At 12 or 24V neither are very harmfull so no sweats about it but over 40Volts any can kill. Injury can happen at any Voltage simply by burning.

Reply
Power-User
Technical Fields - Technical Writing - Validation Specialist-Medical Devices United States - Member - From the Big Apple! Hobbies - Model Rocketry - Rockets should go nuclear! Fans of Old Computers - PDP 11 - Studied computers at W.H.Taft H.S., Bronx, NY. Popular Science - Cosmology - Radio Science Observing

Join Date: Dec 2007
Location: Miami, FL.
Posts: 303
#17
In reply to #14

Re: Why DC voltage?

05/18/2008 10:11 AM

Sir, stick to the topic, we all know what it is. We started at 12-24 volts and all of a sudden you're at 40 thousand! How far do you have to go? Be objective for GOD sakes!

A little anecdote...If you've never been schocked, pinched, or cut; you've never been there!

I was working on a Lumonics Laser at a major Pharmaceutical; an Engineer had left the discharge electrode disconnected and sticking outside the operator door. I barely brushed my elbow across it when a spark jumped 6 inches and shocked me. I was in heaven for about 6 seconds propelled by 25Kvolts DC. And I'm still here! So tell me about DC voltage!

__________________
WARNING! All suggestions are informative only. It is the prerogative of the user to implement under his sole responsibility. This commentator will not be liable for any damages or injuries incurred.
Reply
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#18
In reply to #17

Re: Why DC voltage?

05/18/2008 10:20 AM

Read properly and than comment. Nobody mentions 40 thousand volts except you

Reply
Power-User
Technical Fields - Technical Writing - Validation Specialist-Medical Devices United States - Member - From the Big Apple! Hobbies - Model Rocketry - Rockets should go nuclear! Fans of Old Computers - PDP 11 - Studied computers at W.H.Taft H.S., Bronx, NY. Popular Science - Cosmology - Radio Science Observing

Join Date: Dec 2007
Location: Miami, FL.
Posts: 303
#16
In reply to #13

Re: Why DC voltage?

05/18/2008 10:07 AM

Whatever he calls it; it does exist and is used widely. Look-it-up...(Google it)!

__________________
WARNING! All suggestions are informative only. It is the prerogative of the user to implement under his sole responsibility. This commentator will not be liable for any damages or injuries incurred.
Reply
3
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#19

Re: Why DC voltage?

05/18/2008 11:26 AM

As far as electrical controls are concerned, here are the main supplies used and why they are chosen. Note that explosive areas require a totally different treatment of the electric distribution and is not covered here.

5-12VDC: Only used on control boards for electronics circuits. Not enough drive for most control applications. Even the car industry is trying to use higher voltages.

24VAC: Simple to produce from a small transformer when the system is line powered. It is the first choice in HVAC and some simple control circuits. The low voltage makes it relatively safe in most applications. It can only drive small actuators. Switching with mechanical contacts produce very little sparking and leads to long contact life even with cheap switches.

24VDC: Need a DC power supply to produce when the system is line powered or is easily obtained from batteries. The system can easily be "battery backed up". It is the first choice in complex control circuits including analog signal sensing especially 4-20mA loops. It is easier to handle by total electronic controllers than 24VAC. The low voltage makes it relatively safe in most applications. It can only drive small actuators. Switching with mechanical contacts produce a little more sparking than 24VAC but still give long contact life even with cheap switches.

48VDC: Generally just below the limit of electrical code increased safety requirements. Need a DC power supply to produce when the system is line powered or is easily obtained from batteries. It is a popular choice in telecommunication because of its high drive capacity for long distance and the simple battery back up. The higher DC voltage requires some safety awareness because 48DC can produce some medium size arcs. Switching with mechanical contacts produce some sparking especially for larger loads. Long contact life requires expensive switches often equipped with mercury whetted contacts to continually renew the and increase the reliability. It is difficult to control with electronics switches.

120/240VAC: Simple to produce when the system is line powered. It is a very popular choice in industrial control systems because of its high drive capacity for large actuators. The high voltage requires more safety awareness in most applications. Switching with mechanical contacts produce some sparking especially for larger loads. Long contact life requires good quality switches. It is more difficult to control with electronics switches than 24VDC but it is done when needed.

125VDC: Need a DC power supply to produce when the system is line powered. It is a popular choice in specialized industrial control systems such as power plants because of its high drive capacity for large actuators and the simple battery back up. With modern UPS available, this will eventually disappear for the following reasons: The high DC voltage requires more safety awareness because 125DC can produce long and destructive arcs. Switching with mechanical contacts produce a lot of sparking especially for larger loads. Long contact life requires expensive switches often equipped with magnets to blow the arc out. It is very difficult to control with electronics switches. Just this last point makes it a dying breed.

Comments on the above posts:

Stevem: "In addition to SparkY's reasons, DC circuits radiate less EMI and are generally less susceptible to interference."

Not usually true. Switching DC especially with mechanical contacts produce more arcing than AC therefore producing more EMI. The susceptibility to EMI usually depends on circuit impedance. You can certainly affect a small electronic switch (DC or AC) with EMI but unless you have a monstrous Tesla coil, you will not switch on a small relay (DC or AC).

Case491: "You should also consider the fact that almost all "old" car fires are caused by some electrical fault. DC currents are just as dangerous as AC currents at the same levels."

For the same voltage level, DC produces longer arcs with higher energy. It also creeps on surfaces more easily. The only thing safer about DC is that when it goes through your heart, it simply stops it. As long as the damages are minimal, the heart will usually re-start correctly once disconnected. AC has a different effect. It produces fibrillations in the heart which continue in this lethal mode even after the power sources is disconnected. You often need to apply DC to "reset" it. But as you said after, both can injure or kill you. All you need is enough voltage to pierce through the skin and then the current easily flows through you wet and conductive internals. This produces all kind of damages including cell wall destruction which will eventually die. Enough current will also boil your blood.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply Good Answer (Score 3)
Guru

Join Date: Sep 2007
Posts: 1817
Good Answers: 7
#20
In reply to #19

Re: Why DC voltage?

05/18/2008 11:33 AM

Thank you for your exceptionally clear write up, no more posts needed I think.

Reply
Anonymous Poster
#23
In reply to #19

Re: Why DC voltage?

05/18/2008 8:43 PM

Excellent answer Marco could have written it myself ;-)

Sorry to disappoint other commentators but there is one more thing - power factor.

Most actuators, relays etc are highly inductive (coils of wire). This can produce large current flows in AC systems which can overload the transformer. Control systems have a habit of growing, so very common to hear the overloaded power trasnformer in the control panel humming away. There is no reactive power in a DC system.

By the by, car manufacturers are introducing 48volt car batteries to try and cut down on the cabling in modern cars.

Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#24
In reply to #23

Re: Why DC voltage?

05/18/2008 10:36 PM

That would be the size of cabling - not the footage?

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#27
In reply to #23

Re: Why DC voltage?

05/19/2008 10:31 AM

You are right that most AC actuators have a very bad power factor but DC power supplies do generate a lot of harmonics. In most system the load from actuators and control is negligible on the main supply but could force you to upgrade the small control transformers. As far as the main transformer is concerned, one 10HP motor draws much more power than most complex control panel.

At the end you have to choose between to evils but if your control load is small with respect to the plant power feeder, it doesn't matter which one you choose. Take the control voltage that is more convenient. Usually it is the one you already use for other components in the plant.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#21

Re: Why DC voltage?

05/18/2008 11:50 AM

AC current through a coil has a continuous waring EMF and capacitate coupling. There is also some chatter.

Most AC relays have a bridge rectifier and use a DC coil.

DC coils don't run as hot as an AC coil.

True there is an inrush current spike as well as a counter EMF when activating and deactivating a DC coil. This one time and not 60 or 50 times a second.

Reply
Anonymous Poster
#22

Re: Why DC voltage?

05/18/2008 4:38 PM

Also, AC neutral is usually grounded to protect against shock. DC does not need to be. This means that either the + or the - can short to ground (conduit or frame ground) without affecting the operation of the circuit.

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#28
In reply to #22

Re: Why DC voltage?

05/19/2008 10:55 AM

Below 48V, you can usually have either AC or DC floating. You are right that floating supplies usually allow you to operate with one line grounded but this can be more of a curse than a blessing. By delaying the time when you figure out that you have a line shorted, it is more difficult to figure out what caused it. The shorted line can also generate unwanted ground loops giving you strange "noise" problems.

I prefer to ground the neutral of all my supplies even at 24VDC. Using a properly sized fuse you will know immediately when something goes wrong. Usually is it while you are modifying the system. You might as well fix it while you have your hands in it.

An even more compelling reason to avoid floating control supplies is that it could short to a 480V line. Now you have a safety issue. Assuming that the control circuits have enough insulation to take it (50% of the case), you will have a 24VDC supply floating at 277V with respect to ground (480V LL = 277V LN). Since you don't expect this, you might approach it carelessly and get zapped badly. If you had grounded the return, some fuses would have burned when the short occurred and you would have found and fixed the cause right away. I prefer having a machine stop because of a blown fuse than sending somebody to the hospital for electrical burns or simply falling off the ladder.

Grounded supplies are normally safer than floating supplies. The only exception are in explosive areas (oil refineries, various mills...) where the consequences of generating a spark are worst than the danger of getting shocked. Anyway, their people are trained accordingly and they have monitors that indicate if one line has been grounded.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Anonymous Poster
#26

Re: Why DC voltage?

05/19/2008 10:14 AM

Electrical Inspectors in the US and Canada typically spend more time reviewing voltages above 24vdc.

Reply
Anonymous Poster
#29

Re: Why DC voltage?

05/19/2008 3:23 PM

AC goes in two directions. DC goes in only one.

AC is net EMF. DC is total EMF.

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#31
In reply to #29

Re: Why DC voltage?

05/19/2008 10:40 PM

We often complain that people posting questions are unclear. We should also abstain to answer if we don't intend to make it understandable. While your first sentence "AC goes in two directions. DC goes in only one." is a simple fact learned at high school, the second sentence "AC is net EMF. DC is total EMF" is beyond me. Please explain the wisdom of your claim.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#30

Re: Why DC voltage?

05/19/2008 10:26 PM

Dear Sirs/ Madams.

My reply to:

Sparkstation #2

<< sometimes requires a "shading ring = short circuited turn in the form of a heavy copper loop" around each poleface to prevent that "chattering". >>

Dear Sir not " sometimes " but always & Not "poleface " but part of poleface; almost less than 1/2 the area to produce a 2nd leading phase.

It is in all AC shaded-pole motors; Relays; contactors.

It works as the 2nd winding + Series-Capacitor works in Capacitor-Start / Run AC motors.

Of cource it is to stop Chattering.

A well put reply.

Regards.

To: stevem #3

A good addition to Sparkstation #2

--------

Quote in Beej50's post:

<<"A common mistake people make when trying to design something completely foolproof is to underestimate the ingenuity of complete fools!" Douglas Adams 1952-2001. E&OE! >>

My Boss always suggested us to make products " FOOL-PROOF " but NOT "Bloody-Fool-Proof " You can't.

--------

Repl;y to: case491 #20 & #19

Really an exceptional write up.

< no more posts needed I think.>

but there is always a good addition to a good writing.

Let's say some-thing toi add, even if it is not as good as the original idea

Kind regards

Reply Score 1 for Good Answer
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#32
In reply to #30

Re: Why DC voltage?

05/23/2008 10:07 PM

Hello Haajee

<"....My reply to:

Sparkstation #2

<< sometimes requires a "shading ring = short circuited turn in the form of a heavy copper loop" around each poleface to prevent that "chattering". >>

Dear Sir not " sometimes " but always & Not "poleface " but part of poleface; almost less than 1/2 the area to produce a 2nd leading phase.

It is in all AC shaded-pole motors; Relays; contactors.

It works as the 2nd winding + Series-Capacitor works in Capacitor-Start / Run AC motors.

Of cource it is to stop Chattering.

A well put reply.

Regards.....">.

In your: <"....Dear Sir not " sometimes " but always & Not "poleface " but part of poleface; almost less than 1/2 the area to produce a 2nd leading phase.....">

You are absolutely correct with that statement, for AC Contactors.

In DC Relays and Contactors, there can be a short-circuited heavy current turn, in the form of a short-circuiting copper ring or slug, around the poleface end, to make the relay/contactor a "slow to operate" version.

Likewise, In DC Relays and Contactors, there can be a short-circuited heavy current turn, in the form of a copper ring, around the rear end of the coil, far from the poleface, to make the relay/contactor a "slow to release" version.

Again, in DC Relays and Contactors, there can be a short-circuited heavy current turn, in the form of a copper ring, around the rear end of the coil, far from the poleface, to make the relay/contactor a "slow to release" version, along with a short-circuiting copper ring or slug, around the poleface end, to make the relay/contactor a "slow to operate", both at the same time......

There were many variations on the position/s and dimensions of the copper "slug".

In older telephone systems which used electromagnetic relays, the use of copper short-circuiting "slugs" at various places on a relay armature, gave the needed timing, once installed, no maintenance of that "timing unit" was needed.

Refer: BPO3000 types of relay: http://www.britishtelephones.com/autorel.htm

Have a GA point from me.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#33
In reply to #32

Re: Why DC voltage?

05/23/2008 10:19 PM

Regards & thanks for informative reply.

Thanks again.

Have a good day !!!!!!!

Reply Off Topic (Score 5)
Reply to Forum Thread 33 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); Beej50 (1); Bill (1); BudT (1); case491 (4); Haajee (2); hastingselectric (1); jfmfit (3); jmart23 (2); marcot (4); nesubra (1); PWSlack (1); ronald (3); Sparkstation (3); stevem (1)

Previous in Forum: lux calculation   Next in Forum: POWER FACTOR.

Advertisement