Flow Meters in Parallel

01/22/2009 2:05 AM

Hello ,

What is then purpose of having two Corilois flow meter in parallel, If one meter is able to give the required flow

Service is Cude oil with the following

80000 BPD From Pump data ( total flow at the header prior to meter )

84000 BPD from Instrument data sheet for one meter

Apart from Redundancy is there any other reason

Regards

jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#1

Re: Flow Meter In Parallel

01/22/2009 4:28 AM

The spinning of the water in the chamber is used to divert a small portion of the fluid past the meter. (It is not known why it is called a Coriolis meter ). The accuracy of the split may be less at higher flows.

Using 2 I identical meters may result in better accuracy and in addition a difference in measurement may indicate other problems.

Different sizes can also be required to handle varying flows.

In water metering to buildings a big and small meter are often used in parallel. (big for bulk and small for the trickle flow)

Note that 2 identical looking meters may in fact have a different split ratio in the "Coriolis" chamber.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5
In reply to #1

Re: Flow Meter In Parallel

01/23/2009 7:56 AM

A Coriolis meter is called that because it uses the Coriolis effect, and actually measures that apparent force. G. Coriolis first described this psuedo force that is used to describe objects motion in a rotating reference frame. That is why the first coriolis flow meters had the liquid travel in huge circular paths. Some of the first ones, for just a 2" tubing run, were about 3' tall. now they suffice with just a small bow in them.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Score 1 for Off Topic
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#9
In reply to #5

Re: Flow Meter In Parallel

01/24/2009 4:57 AM

The direction of spin is caused by the construction and not by the Coriolis "force". If it was the meter won't work on or below the equator.

It should not be called a Coriolis meter.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#10
In reply to #9

Re: Flow Meter In Parallel

01/24/2009 6:58 AM

Beg to disagree, the coriolis flow meter does work by coriolis effect. The coriolis effect unforturnately got linked to earth's rotation, but the application is beyond this.

Th coriolis effect is the apparant deflection of an moving object when viewed from a rotating frame.

The coriolis force is the force perpendicular to the velocity of body when the newtons laws are converted to polar (rotating) reference frame.

In coriolis flow meters, an ultrasonic vibration is passed throug the fluid (and in general case , the pipe/tube being circular, the vibration provides the circular reference frame. The changes in the frequency, phase etc of the signal are afunction of the flow rate.

This is from the literature of the coriolis flow meters we procure/

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Score 1 for Good Answer
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: Flow Meter In Parallel

01/22/2009 6:59 AM

The only applications where I've seen two flowmeters in parallel were for those where continuous operation is necessary. If one flowmeter goes bad or needs to be calibrated (requiring physical removal), the operation may continue using the remaining one.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2009
Posts: 15
Good Answers: 1
#12
In reply to #2

Re: Flow Meter In Parallel

01/26/2009 3:51 AM

I disagree with your "the only applications ... were for those where continuous operation is necessary.

You can have several meters in parallel to cover a large flowrange.

You normally size a metering system this way :

2 times 100% of max flow

3 times 50%

4 times 33%, etc..

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#14
In reply to #12

Re: Flow Meter In Parallel

01/26/2009 7:01 AM

I didn't say that it can't be done.

Okay, the application says that the pumps have a capacity of 80,000 bpd. This means that the flow is usually below this point, maybe even half. Each flowmeter is rated at 84,000 bpd so one is more than enough to handle the flow.

If the flowrate is more than the biggest flowmeter available on the market, then, yes, you might be forced to use more than one. This is not the case here.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
2
Active Contributor

Join Date: Jan 2009
Posts: 15
Good Answers: 1
#3

Re: Flow Meters in Parallel

01/23/2009 5:21 AM

In normal operation, you can expect to have approx 50% of the flow going in each line if the skid is trully symetrical.

the assembly must have been sized to 2 times 100% of max flow. Basically, you could run the total flow in one line occasionally. Reading the data you sent, that seems right.

Designing this way allows you to :

1) run the meters on the middle of their flow range which is where they are the most linear and thus accuracy is best.

2) Ensure full redundancy should your Scada/flowprocess system handles this

3) Detect changes in the performances of the meters. After the meters are commissioned, you will notice a slight difference in the indicated flow. This slight difference is normally proportionally stable. If the total flow increases, you should normally see proportional increases in each line. You determine a line flow coefficient. This coefficient is normally steady. If this moves out of certain tolerances, there could be a performance issue (material build up, mud, water, gas, piece of foreign particules (steel, gloves, bolts, nuts, etc), whatever can be stuck in there)

4) Recalibrate the meters without disruption of crude oil supply.

5) Isolate one meter for repair without disruption of crude oil supply.

6) get a better accuracy at low flow.

7) Get an extended flowrange. The min flow is lower on a 2" meter than on a 6" meter.

Beside the above operating advantages, there could have been cost considerations as well :

1) I have no idea of the cost of one coriolis meter but would think that larger size coriliolis meter are not proportionally as cheap as the smaller size ones. In other words, it may be cheaper to buy two times 2 inches coriolis meters than one time a larger sized one to achieve same max flow. Two times 2 inches doesn't equal to one time 4 inches in term of flowcapacity.

2) Because of 1) above you may also make savings on the valves although the piping may cost you a bit more.

As a conclusion: if this metering is critical, it is very good practice to design it with full redundancy.

Register to Reply Good Answer (Score 2)
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#6
In reply to #3

Re: Flow Meters in Parallel

01/23/2009 11:20 AM

Welcome to Cr4.

GA from me,

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#4

Re: Flow Meters in Parallel

01/23/2009 6:20 AM

It is simply to use one meter to do the job and the other as a spare, and as you notice from P&ID there are an isolating valves to fulfill that requirement.

Note: Refer to your P&ID drawing, the arrows of fluid flow downstream of meters must be reversed.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#7

Re: Flow Meters in Parallel

01/23/2009 11:29 AM

Vulcan is correct as far as I know, the only real way to calibrate these things is to take them out and send them to a flow lab. Therefore, you need two if you can't take your line down to fix a meter. Otherwise, all they can do is zero them by blocking them in (note if your block valves leak you will have issues).

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#8

Re: Flow Meters in Parallel

01/23/2009 9:33 PM

If the intention is to detect if a meter is going bad, two meters connected in series is better for comparison than parallel meters. When connected in series, you know that the flow through them is exactly the same. In a parallel connection, the installation will have to be precise in order to assure exact same flow through the two flowmeters.

From your figures, the individual flowmeters have about the same flowrate as the pumps. Halving the flow between two meters will put the flow into the lower half of the meter's range. The upper half will never be reached, much less exceeded. That puts the majority of your flow in the less-accurate low-flow region of the meters.

So, no, I don't think the purpose of having two meters in parallel is anything other than redundancy.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 15
Good Answers: 1
#13
In reply to #8

Re: Flow Meters in Parallel

01/26/2009 4:39 AM

I agree with your point "two meters in series" provides a better failure detection.

But if one meter is down, you must stop the flow to remove it unless you have a bypass line, which bypass flow will not be metered.

So meters in parallel provides a good compromise.

Best engineering is to have a Z config or a master meter.

Basically the Z config consists in having both meters in parallel most of the time. You can run a periodic control of your meters by rearranging the open/closed valves to set the two meters in series. In term of piping, you will need a bypass line with an isolation valve between the downstream side of the upstream meter and the upstream side of the downstream meter.

Master meter is used when recalibrating on the field the meters. It is a stand-by line. It allows you to move one meter for recalibration instead of two or three. Basically you run the same flow of fluid in the proved meter and the master meter, both running in series. You determine the new meter factor and reset it at the flowcomputer. Metering flowcomputers offer this feature.

In the present case, the piping arrangement doesn't plan for both Z and master meter config anyway.

Register to Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#11

Re: Flow Meters in Parallel

01/24/2009 12:10 PM

Thanks for all the Inputs

Regards

Jose

Register to Reply
Participant

Join Date: Feb 2009
Posts: 4
#15

Re: Flow Meters in Parallel

02/02/2009 2:23 PM

hello my friend

maybe one flowmeter is for the control (fic) and the other one for the protection of the unit (trip). This situation is very common lately because of the safety.

__________________
Panathinaikos
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#16

Re: Flow Meters in Parallel

02/05/2009 12:53 AM

I agree with Mr.Abdel Halem. Both meters have isolation Valves so anything goes wrong with one the other takes over to ensure constant & continuous flow data. In furnace oil pumps we install 2 strainers in parallel so that we switch over while cleaning one.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (1); betomachine (1); ducon (1); gsuhas (1); HELLINAS (1); Hendrik (2); josej (1); Phys (1); Reivax (3); sb (1); Vulcan (3)