Flowmeter

05/16/2009 4:10 AM

While selecting flowmeter (say magnetic), we look whether line remains full or not.

What is the idea behind this?

Thanks

__________________
Be simple and specific for a great success in Life
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Flowmeter

05/16/2009 4:17 AM

Not certain what you mean, but you certainly can't measure fluid velocity if the fluid isn't there! So by definition the line needs to be full.
Flow meters are usually positioned so that air can't into the line and the flow is relatively laminar, e.g a straight pipe run for (say) a length of at least 5 times the pipe diameter, either side of the meter.
Sorry if I'm off target here...(now where's my banjo and that cow?)

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2
In reply to #1

Re: Flowmeter

05/16/2009 7:25 AM

You're not off target but spot on.

A magnetic flowmeter operates by using the fluid passing through a magnetic field to generate an AC or DC voltage. If the fluid is not there, there will be no generated voltage. If there are bubbles in the fluid, you'll get a very noisy signal.

The banjo and the cow are at the town hall performing at a concert.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#3

Re: Flowmeter

05/16/2009 7:31 AM

The velocity in a pipe is not uniform it will be faster at the centre and slower against the wand. The uneven distribution will have an effect on the result.

The friction in a pipe will be less if the pipe is not flowing full (the ratio of wet perimeter vs area changes fastest just below full) Therefore a pipe almost flowing full may deliver more water for the same measured velocity.

At any flow not fill the reduced wet area need to be considered.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#6
In reply to #3

Re: Flowmeter

05/17/2009 11:12 AM

Hendrik

No, what you explained is not the reason.

What Andrew Ward explains is the real and only reason for requirement of full flow for flowmeters.

Also What Andrew tells about Krohne meters is also true.

(I am in design and production of Magnetic Flowmeters)

My GA to Andrew Ward

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#7
In reply to #6

Re: Flowmeter

05/18/2009 1:27 AM

Hi gsuhas

My last sentence is about the same as his. Therefore not false.

The problem with flowmeters is that it measures avarage velocities. If not full the level may be anywhere but I think it will mostly be close to full because what is after the meter..

With almost full the area stays almost at 100% and can therefore not have a big influence but the changing velocity distribution pattern will have an influeance on the avarage and therefore on the calculated flow.

I havent tested this on meters but on tunnels and I can assure you that the flow on a 95% full tunnel is more than on a full (submerged) tunnel with the same slope.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#8
In reply to #7

Re: Flowmeter

05/18/2009 1:40 AM

As you say, magnetic flow meter measures average velocity. This is not a problem, but it is advantage. As it measures average velocity, to find out flow rate we can use the multiplication of meter measured velcity and the cross sectional area.

Beside, there is no assurance that the pipe is full if the installation is not proper. In that case, if line is not full the meter with built in multiplier assumes that the line is full and give multiplication of average velocity and the full cross sectioanl area of the line (which is not really full of liquid. This gives higher reading than actual flow rate as Andrew say.

Besides, when we are talking of accuracies of the order of 0.1 to 0.3%, 95% filled line will give big error, which is not acceptable by industries.

If flow meter which measures local velocity instead of average velocity (type insertion flowmeter), we can not infer what will be the flow rate unless it is mounted at a point where velocity is average velocity.

Register to Reply
3
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#4

Re: Flowmeter

05/17/2009 2:41 AM

Another point that hasn't been made yet is that a magnetic flowmeter measures velocity. You want volume. The meter calculates volume using this velocity and multiplying by the cross sectional area. If the meter is not full, the cross sectional area of the fluid is less than the cross sectional area of the meter. This will cause the meter to report a larger volumetric flow than you really have. I have seen mags advertised that work with less-than-full pipes (Krohne I think) where there is a level sensor in the meter as well as the electrodes for measuring velocity.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply Good Answer (Score 3)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #4

Re: Flowmeter

05/17/2009 9:21 AM

GA. You figured out the simplest and most important reason to keep the pipe full all the time you want to measure flow.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Commentator

Join Date: Aug 2008
Posts: 56
#12
In reply to #4

Re: Flowmeter

11/02/2010 3:05 PM

Dear Andrew,

There is a situation in our plant where there is gravity flow throuth a line of 4''. and the process does not allow to provide any bend on this line as the process may get checked (in this condition mechanical will have to cut the line as steam fushing doesnt work in this process). I have enquired krohne for the partial flow mag flow meters for 4'' line but they said that krohne manufacture partial flow type magflowmeters on 8'' and larger dia flowmeters. do you any suggestion on this?

Register to Reply
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#13
In reply to #12

Re: Flowmeter

11/02/2010 3:44 PM

Raj,

One suggestion I have is to fabricate a Palmer-Bowles flume (some people spell them Palmer-Bowlus) into your pipe. It may be difficult to do depending on if your pipe can be open to atmosphere or not. If not, you would probably need a tee flange above the measurement point to mount an ultrasonic level sensor. Flumes generate a velocity head into the flow that is proportional to flow. I've used these flumes in wastewater applications where solids plugging the pipe would be an issue. Something that small might be a problem to calibrate accurately, but it may be good enough if you have nothing now and the flow stays relatively constant.

I'm not a mechanical guy and can't really suggest where to get a flume that will fit, but I hope this is enough information to get you started.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#9

Re: Flowmeter

05/18/2009 1:55 AM

A flowmeter on a rising main should always be full. Air trapped in there will cause problems. All needed to do is to get rid of air some distance before the meter.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#10
In reply to #9

Re: Flowmeter

05/18/2009 2:14 AM

You are right, if the flow meter is in rising mains.

But, it is not true if flowmeter is in horizontal line. If it is in horizontal line, it is recommended that line be raised by 1 D after flowmeter to assure full line condition.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Flowmeter

05/18/2009 3:43 AM

If the two electro-devices (two electrodes) aren't wetted all the time, the magnetic-devices won't operate correctly, and therefore the electro-magnetic flowmeter won't work.

If all else fails, read the manufacturer's installation instructions supplied with the equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments