Mysterious Shock Received When Operating Fire Extinguisher...

11/25/2010 12:28 PM

Hi, all,

We are scratching our head over an incident that happened at one our our sawmills the other day. A worker noticed a small fire on a 50 hp blower motor that was failing and grabbed an ABC dry chemical, handheld fire extinguisher. He gave the fire a short blast of dry chem from about 6 feet away and felt a tingle in his hands. He gave a second, longer blast of dry chem and was knocked over by the shock he received. He was checked over in hospital and wasn't hurt.

He was standing on dry concrete, with CSA approved workboots and was not touching any other metals.

The blower is a lobe-type blower, V-belt driven, that provides the motive power to blow wood chips down a metal pipeline.

The weather was very cold, about -30C, and clear.

We checked the grounding in the area and found that everything was properly grounded. There was an existing ground fault in another motor about 100 yards away that had been existing for some time.

Since dry chemical powder is supposed to be nonconductive I'm curious about the possibility that we had a static electricity situation. I have heard that V-belts can build up tremendous static charges under the right circumstances. I also mention the weather because the cold would point to the air being very dry, conducive to static buildup.

I checked with our supplier who maintains and recharges our fire extinguishers--they repressurize the extinguisher with dry nitrogen so there wouldn't have been any moisture in the extinguisher to lessen the conductivity of the dry chemical stream.

Even if the dry chem spray touched electrically "hot" parts in the failing motor it should not have transmitted a shock. However, I'm not so sure that a static charge behaves the same way, since static charge is conducted off of automobiles with a rubber strip, which is essentially an insulator.

Does anyone have any suggestions on what might have happened?

Thanks,

Jon.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#101
In reply to #99
Find in discussion

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 5:40 PM

see post #55

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#102
In reply to #101

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 5:51 PM

My apologies 34point5... you had it, I apparently didn't pay enough attention when reading. Thanks.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#103
In reply to #102

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 6:29 PM

Not a problem CI, well, actually, it's a common enough 'problem' all over.

& I do think it is good that Guest brought up Navy training as a possible source of "known problems", behind what I always just took as "proper extinguisher & smoke technique".

I am very interested to find out if this is a "reason behind", that has been "lost", prior to my training, so now absent from my instructing, and obviously that of other instructors on the thread, so the OP's training program.

It would be great if someone could post the relevant part of the Navy instructors manual.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#104

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 6:38 PM

As you expected, still no reply from NFPA. Will keep you informed or even resend the email to a specific address.

I did find these esp shoes. They may be something that people could wear during dry seasons to dissipate the static. It is kind of like wearing the tin foil on your feet instead of your head. FYI

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#105
In reply to #104

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 7:24 PM

Hey, they even have them for some of the more fashion-conscious among us .

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#106
In reply to #105

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 7:37 PM

If you wear these you are even protected from lightning. It would increase the chance of being hit by something else though

__________________
The Twain Has Met
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#107
In reply to #106

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 7:45 PM

FEREVENSAKE don't let sue see - she'll be on the next plane!

.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#109
In reply to #107

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 9:39 PM

She's seen them. In the BBT department I think it was. I wonder what would happen if one of the mill workers would wear them on the job .

Sorry OP, it gets this way sometimes.

__________________
The Twain Has Met
Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#110
In reply to #109

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 10:41 PM

Well it's sort of on topic as to the severity of the shock.

You will note the 'shoe earth straps' are a megohm - which acts as a earth in the static buildup sense, but acts as a current limiter, keeping a person fairly safe, in terms of not being 'fully earthed', so far as, say contact with mains power.

It is one of the interesting things about rubber and rubber alloys, that they become conductive at high voltages.

Or gumboots are not protection against lighting. And wearing earth straps would be a good way the get the best shock possible from a big static source.

I.e. 'rubber soled' work boots are no protection if it's static, but possibly quite good protection if it was 'mains leakage' - (depending on their condition and composition and structure and moisture and/or sweat. The latter two, possibly high if She is about.)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#108
In reply to #106

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/29/2010 8:06 PM

John and Ky

I thought "esp" stood for electrostatic protection but I put a pair on and found that I could sense things. Now what I sense are fetishes that we can't discuss. So I guess esp means something else. Wonderful stylish shoes but you are right about the hit.

Cheers

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#112
In reply to #106

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/30/2010 4:09 AM

Did you mean? "Hit-on by other men?"

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#114
In reply to #112

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/30/2010 4:31 PM

Yep, sorta. If this goes on I'll never be shown around the plant by the mill operator. Either way I mean.

BTW Andy, I have it under control nowadays, sorta. I could be a wondering party trick if I chose to wear a certain combination of fabrics. It's not really painful (the shock sensation, not the boots) but very unpleasant, for both parties involved.

I'm over it, so to say. Besides, wearing my tin foil hat has helped too. Gosh this is a fun place to be while still not being off topic. Or am I?

Gotta go check my tire pressure.

Have one on me, Ky.

__________________
The Twain Has Met
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#115
In reply to #114

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 3:59 AM

LOL!!!!

You have lost your "shocking" personality, how sad!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#111
In reply to #104

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/30/2010 4:07 AM

I am not sure that they will help or not. They may even make the problem worse for all I know.

It really depends on how the discharge took place. If it was a "flash-over" over the shoes, then they would probably help.....

Is this the source of the saying "I wouldn't want to be in your shoes!"

When I pointed out the special anti static shoe tapes it was for Ky, who has a problem with static buildup on his person for no apparent reason. Which was why I placed it as being Off Topic....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member United States - Member - New Member

Join Date: Apr 2007
Location: Wichita, Kansas USA
Posts: 653
Good Answers: 30
#113

Re: Mysterious Shock Received When Operating Fire Extinguisher...

11/30/2010 12:59 PM

I know it's been mentioned, but in a quick scroll through the posts, I didn't see this detail/theory thrown out: if the worker did indeed have on gloves, he was insulated from the fire extinguisher, and if a charge was building up on in, it would have to exceed the insulation threshold of the gloves to discharge. Perhaps this is part of the reason there was a large enough discharge event on his second, longer blast, to knock him over? Bare hands on the extinguisher would be a completely different scenario, and I don't see any real discussion about that part of the setup. My $.02 worth.

Tom D.

Register to Reply
Power-User

Join Date: Apr 2008
Posts: 365
#116

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 9:17 AM

Hello Jon,

I dont know the answer but am taking a guess.

Any substance leaving containment under pressure cools to a certain degree. Perhaps such cooling was great enougth to allow a moisture build up along the stream path to allow electricity to pass back to the operator.

Cheers

Peter

Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#117

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 11:57 AM

This just came in from the NFPA:

Kevin,

It is my understanding that ABC extinguishers typically do not create a sufficient static charge for this to be a concern. Typically, static discharge is a problem only with carbon dioxide extinguishers. It is more likely that the "shock" was generated by another source of energy.

I recommend that you contact an extinguisher manufacturer for further clarification.

I hope this satisfies your inquiry. If you need additional assistance, please do not hesitate to contact NFPA's Technical Advisory Service.

Sincerely,

Barry D. Chase

Fire Protection Engineer

NFPA

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#118
In reply to #117

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 12:13 PM

I guess that's in line with my searches (#67), but it's not a result I expected.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#119
In reply to #118

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 1:37 PM

It's not the response I expected either. I reread the OP with this information in mind and thought about this...

He gave the fire a short blast of dry chem from about 6 feet away and felt a tingle in his hands.

Come to think of it... I can't remember any single time I would describe a static electricity discharge as a tingle. It's always sharp and quick. Wouldn't tingling be more of a sustained current?

We checked the grounding in the area and found that everything was properly grounded. There was an existing ground fault in another motor about 100 yards away that had been existing for some time.

Given a known ground fault (and in light of the NFPA info), I would move that to the top of my suspect list.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#120

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 2:01 PM

Well, All,

As is maybe normal with mysteries, there is a real simple answer. It is called getting the facts straight right off the get-go.

Bottom line: The fire extinguisher used was NOT a dry chem; it was a CO2 unit.

The water was muddied by the fact that someone hit the motor (after the first response from the CO2 extinguisher) with a dry chem extinguisher. It took quite a bit of talking to find that little tidbit out!

The CO2 unit was hand-held, off the ground while being discharged, so the user experienced the static charge buildup and discharge while using the extinguisher.

I found some research papers on the web from the 1980's that discussed the voltage buildup; it can go as high as 50kV within about two seconds or so after the CO2 discharge is started. The energy is not high, so the static discharge is not dangerous to the operator unless their involuntary motions cause potential injury.

The funny thing is that the researcher tried various ways to reduce the static buildup and came up with a couple of ways to knock it down to almost nothing. But the extinguisher we used, which is a "Flag" trade name, doesn't look like it has any of the static mitigation measures. And when I phoned the outfit that owns the "Flag" name, I got someone who must have been a boot camp Sergeant: "You modern pussies who can't stand some static electricity! @#%$^&%$. " No a lot of interest from this guy.

So, we know how the shock happened. We are looking at reviewing our fire extinguisher training to accommodate this issue.

Thanks, All, for your interest and input! It has been an interesting thread!

Jon.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#121
In reply to #120

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 2:06 PM

Good luck.

I'd be "reflagging" my extinguishers with another brand from the sound of their response.

Happy Holidays!

Register to Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#122
In reply to #120

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 2:06 PM

Just to say it again... (see 34point5's post #55 for more)... the extinguishers should always be placed on the ground prior to discharge (for your training purposes).

Glad to see the mystery solved. It has been interesting.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#123
In reply to #122

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 2:13 PM

I asked Mr. Flag about that, pointing out that the US Military trains both CO2 and Dry Chem to be set down before using. His response was "I was in the military, too, and I wasn't trained that way. After all, they are portable, use them as portable! And thats how I train people, blah, blah." A perfect example of a human 1-way valve. All out, no in.

Jon.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#128
In reply to #123

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 5:15 PM

Well I'm glad that sorted it self out to a "known issue"- though not to you or your guys, unfortunately.

I'm mightily Disappointed that your suppliers "trainer" is such an ignorant A-hole (classic case of "loss of passing on WHY" in training)

What you might like to do is contact the local fire service and ask them if they will run a short course, or let your guys attend their next extinguisher training day.

Mostly this comes under fire awareness education/PR and is part of the service (free) - not to sure about 'all parts of all countries' though.

Meanwhile - come in 'under the smoke', and as you said above, should not see anyone flung into anything.

And thanks for being concerned enough to bring this here - and staying through the "process"

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#129
In reply to #128

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 5:37 PM

Bringing in the local volunteer fire department to help with this training is certainly on our agenda.

I'll also suggest that we modify our purchasing of CO2 extinguishers by asking the suppliers come up with static electricity data, now that we know that the static generation is controllable.

By the way, for those that are interested, the research report is:

"Electrostatic Effects with Portable CO2 Fire Extinguishers"

By G.J. Butterworth and P.D. Dowling,

Published in the Journal of Electrostatics, 11 (1981) pp 43-55.

It is available for purchase off the 'net at about $40 US. It makes for interesting reading and, like I mentioned before, offers a solution to bring the electrostatic production down to nearly nothing when operating a fire extinguisher. And as they are not patented solutions, they are fair game to anyone. There are some fascinating photos in the report of electrostatic discharges taking place in a specially-made clear plastic CO2 horn. Looks like a mini electrical storm.

That is why I am floored that the one supplier I contacted was so weird about static discharges. The extinguisher in question was built 18 YEARS AFTER this technical report was published, so it should have been mainstream in the extinguisher industry by then. But then, why should I be surprised? I'm sure military people were still buying swords 18 years after the machine gun was developed... :>(

Jon.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#130
In reply to #129

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 5:52 PM

, check on who trains who - as you might find the 'townies' train the volunteers in such as extinguishers and BA (breathing apparatus).

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#131
In reply to #130

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 6:01 PM

Good Point! There is a "paid", real live fire department not far away and they will likely have the training HP that we need. And probably to the level of detail we need.

Jon.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#132
In reply to #131

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 10:37 PM

It's probably 'free' either way - but 'good form' is to make a donation - these guys are always scratching for new equipment. Often just the 'small bean' stuff.

Also - I don't know about Canada - but a lot of places have a "fire warden" or "fire marshal" qualification, for corporate employees.

They learn basic response skills, OH&S, evacuation, and first aid, etcetera. This then gives you someone on hand to keep the training/awareness current with the other guys, and train new guys.

Generally they get all the updates rattling around the fire fighting organizations. And they see to things like dates, position of types, proper signage, that hoses, hydrants whatever works. And obviously the right person will bring some order to response if something happens - despite the 'preventive measures' they've produce.

Picking such a person is something generally done during some sort of live fire training. As you can never 'guess' how people react to a real fire. Whichever organisation you pick to train your guys, have a quiet word up front with them, on who they might pick.

Otherwise you are generally looking for a 'floating shop floor' person, with some leadership experience or potential. Not necessarily an existing gang leader or shift boss.

You want one per shift minimum. It might cost you a bit in time off and maybe course fees, but that will possibly come off your insurance premium.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member United States - Member - New Member

Join Date: Apr 2007
Location: Wichita, Kansas USA
Posts: 653
Good Answers: 30
#124
In reply to #120

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 2:19 PM

I would still like to know; has it be determined if the shocked party was or was not wearing gloves? Seems like it would be good to know which would cause the least operator "discomfort" when using a CO2 extinguisher, should the situation arise again.

Tom D.

Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#125
In reply to #124

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 3:01 PM

Tom,

Yes, they were wearing gloves. It was too cold out to do anything "ungloved".

I think the least operator discomfort would be to do what you can to ground the extinguisher out before actually pulling the trigger. This would be putting it on the ground, against a piece of wood or metal that is connected to the ground or similiar. Anything to give the static charge an easy way off the fire extinguisher. Since the charge can get to a significantly high voltage, unless one was wearing electricians gloves rated to 50kV, you WILL eventually get a static electricity shock off of the extinguisher unless it is grounded.

Jon.

Register to Reply
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#126
In reply to #125

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 3:19 PM

Thanks for letting us know. Interesting, Ky.

__________________
The Twain Has Met
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#127
In reply to #120

Re: Mysterious Shock Received When Operating Fire Extinguisher...

12/01/2010 3:58 PM

I don't know about pussies but I remember getting shock (rooster) and then I learned to swear like a boot camp sergeant.

Good detective work and it is nice to see a resolution.

Cheers

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Register to Reply Page 2 of 2: « First < Prev 1 2 Last »

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (14); Andy Germany (18); Anonymous Poster (4); BruceFlorida (1); ChaoticIntellect (4); corelite (1); DaS Energy (1); Doorman (1); Iris (1); JohnDG (4); kevinm (10); kramarat (9); ky (9); Lehman57 (2); lyn (13); mjb1962853 (1); Mohamed Wahab (1); mountk2 (4); North of 60 (1); old salt (11); Phaddy (1); phoenix911 (2); RHABE (1); sawmilleng (16); tdesmit (2)